Function code
Default    value
Modify
P10.00
Simple PLC
0: Stop after running once. The VFD has to   be commanded again after finishing a cycle.
1: Run at the final value after running   once. After finish a signal, the VFD will keep the running frequency and   direction of the last run.
2: Cycle running. The VFD keeps running until   receiving a stop command, then system will stop.
P10.01
 Simple PLC memory
0: Power loss without memory
1: Power loss with memory; PLC record the   running stage and frequency when power loss.
P10.02
Multi-step speed 0
The frequency setting range of stage 0–15: -100.0–100.0%,   100.0% of the frequency setting corresponds to max. output frequency P00.03.
The operation time setting of stage 0–15: the time   unit is determined by P10.37..
When selecting simple PLC running, set P10.02–P10.33   to define the running frequency and time of all stages.
Note: The symbol of multi-step determines the running   direction of simple PLC. The negative value means reverse rotation.
image.png If multi-step speed operation is selected,   multi-step speeds are in the range of --fmax–fmax and   it can be set continuously. The start/stop of multi-step running is   also determined by P00.01.
Goodrive35 series VFDs can set 16 stages speed,   selected by the combination of multi-step terminals 1–4 (select the setting   by S terminals, the corresponding function codes are P05.01–P05.09),   corresponding to the speed 1 to speed 15.
When terminal 1, 2, 3, 4=OFF, the frequency input   mode is selected via P00.06 or P00.07. When terminal 1, 2, 3, and 4 are not   off, they run at multi-step which takes precedence of keypad, analog value,   high-speed pulse, PLC, and communication frequency input.
The relation between terminal 1, 2, 3, 4 and   multi-step speed is as following:
0.0%
P10.03
Running time of step 0
0.0 s
P10.04
Multi-step speed 1
0.0%
P10.05
The running time of step 1
0.0 s
P10.06
Multi-step speed 2
0.0%
P10.07
The running time of step 2
0.0 s
P10.08
Multi-step speed 3
0.0%
P10.09
The running time of step 3
0.0 s
P10.10
Multi-step speed 4
0.0%
P10.11
The running time of step 4
0.0 s
P10.12
Multi-step speed 5
0.0%
P10.13
The running time of step 5
0.0 s
P10.14
Multi-step speed 6
0.0%
P10.15
The running time of step 6
0.0 s
P10.16
Multi-step speed 7
0.0%
P10.17
The running time of step 7
0.0 s
P10.18
Multi-step speed 8
0.0%
P10.19
The running time of step 8
0.0 s
P10.20
Multi-step speed 9
0.0%
P10.21
The running time of step 9
0.0 s
P10.22
Multi-step speed 10
0.0%
P10.23
The running time of step 10
0.0 s
P10.24
Multi-step speed 11
0.0%
P10.25
The running time of step 11
0.0 s
P10.26
Multi-step speed 12
0.0%
P10.27
The running time of step 12
0.0 s
P10.28
Multi-step speed 13
0.0%
P10.29
Running time of step 13
0.0 s
P10.30
Multi-step speed 14
0.0%
P10.31
Running time of step 14
0.0 s
P10.32
Multi-step speed 15
0.0%
P10.33
Running time of step 15
0.0 s
P10.34
Simple PLC 0–7 step ACC/DEC time
Below is the detailed instruction:
After users select the corresponding ACC/DEC   time, the combining 16 binary bit can   be changed into hexadecimal bit, and then set the corresponding function   codes.
ACC/DEC time 1 is set by P00.11 and P00.12;   ACC/DEC time 2 is set by P08.00 and P08.01; ACC/DEC time 3 is set by P08.02   and P08.03; ACC/DEC time 4 is set by P08.04 and P08.05.
Setting range: 0x0000–0xFFFF
0x0000
P10.35
Simple PLC 8–15 step ACC/DEC time
0x0000
P10.36
PLC restart
0: Restart from the first step; stop during   running (cause by the stop command, fault or power loss), run from the first   stage after restart.
1: Continue to run from the stop frequency;   stop during running (cause by stop command and fault), the VFD will record   the running time automatically, enter into the stage after restart and keep   the remaining running at the setting frequency.
P10.37
Multi-step time unit
0: Seconds; the running time of all steps   is counted by second
1: Minutes; the running time of all steps   is counted by minute