You need to add a fuse to prevent overload.
You need to configure a manually manipulated molded case circuit breaker (MCCB) between the AC power supply and VFD. The breaker must be locked in the open state to facilitate installation and inspection. The capacity of the breaker needs to be 1.5 to 2 times the rated current of the VFD.
According to the working principle and structure   of breakers, if the manufacturer's regulation is not followed, hot ionized   gases may escape from the breaker enclosure when a short-circuit occurs. To   ensure safe use, exercise extra caution when installing and placing the   breaker. Follow the manufacturer's instructions.
To ensure safety, you can configure an electromagnetic contactor on the input side to control the switch-on and switch-off of the main circuit power, so that the input power supply of the VFD can be effectively cut off when a system fault occurs.
D.5.1 AC 3PH 380 V (-15%)–440 V (+10%)
Model
Breaker    (A)
Fuse (A)
The    rated working current of the contactor (A)
GD35-1R5G-4-C1/D1/H1
15
16
10
GD35-2R2G-4-C1/D1/H1
17.4
16
10
GD35-004G-4-C1/D1/H1/H2
30
25
16
GD35-5R5G-4-C1/D1/H1/H2
45
25
16
GD35-7R5G-4- C1/D1/H1/H2
60
40
25
GD35-011G-4- C1/D1/H1/H2
78
63
32
GD35-015G-4-C1/D1/H1/H2
105
63
50
GD35-018G-4-C1/D1/H1/H2
114
100
63
GD35-022G-4-C1/D1/H1/H2
138
100
80
GD35-030G-4-C1/D1/H1/H2
186
125
95
GD35-037G-4-C1/D1/H1
228
160
120
GD35-045G-4-C1/D1/H1
270
200
135
GD35-055G-4-C1/D1/H1
315
200
170
GD35-075G-4-C1/D1/H1
420
250
230
GD35-090G-4-C1/D1/H1
480
315
280
GD35-110G-4-C1/D1/H1
630
400
315
GD35-132G-4-C1/D1/H1
720
400
380
GD35-160G-4-C1/D1/H1
870
630
450
GD35-185G-4-C1/D1/H1
630
1110
580
GD35-200G-4-C1/D1/H1
1110
630
580
GD35-220G-4-C1/D1/H1
1230
800
630
GD35-250G-4-C1/D1/H1
1380
800
700
GD35-280G-4-C1/D1/H1
1500
1000
780
GD35-315G-4-C1/D1/H1
1740
1200
900
Note: The accessory specifications described in the preceding table are ideal values. You can select accessories based on the actual market conditions, but try not to use those with lower values.
D.5.2 AC 3PH 520 V (-15%)–690 V (+10%)
Model
Breaker    (A)
Fuse (A)
GD35-022G-6-C1/D1/H1
105
63
50
GD35-030G-6-C1/D1/H1
105
63
50
GD35-037G-6-C1/D1/H1
114
100
63
GD35-045G-6-C1/D1/H1
138
100
80
GD35-055G-6-C1/D1/H1
186
125
95
GD35-075G-6-C1/D1/H1
270
200
135
GD35-090G-6-C1/D1/H1
270
200
135
GD35-110G-6-C1/D1/H1
315
200
170
GD35-132G-6-C1/D1/H1
420
250
230
GD35-160G-6-C1/D1/H1
480
315
280
GD35-185G-6-C1/D1/H1
480
315
280
GD35-200G-6-C1/D1/H1
630
400
315
GD35-220G-6-C1/D1/H1
720
400
380
GD35-250G-6-C1/D1/H1
720
400
380
GD35-280G-6-C1/D1/H1
870
630
450
GD35-315G-6-C1/D1/H1
1110
630
580
GD35-350G-6-C1/D1/H1
1110
630
580
GD35-400G-6-C1/D1/H1
1230
800
630
GD35-500G-6-C1/D1/H1
1500
1000
780
GD35-560G-6-C1/D1/H1
1740
1200
900
GD35-630G-6-C1/D1/H1
2010
1380
1035