Do as the following after the VFD fault:
1. Check to ensure there is nothing wrong with the kepad. If not, please contact with the local INVT office.
2. If there is nothing wrong, please check P07 and ensure the corresponding recorded fault parameters to confirm the real state when the current fault occurs by all parameters.
3. See the following table for detailed solution and check the corresponding abnormal state.
4. Eliminate the fault and ask for relative help.
5. Check to eliminate the fault and carry out fault reset to run the VFD.
8.5.1 VFD faults and troubleshooting resolutions
Code
Fault
Cause
Solution
OUt1
Inverter
unit U
phase
protection
The   acceleration is too fast
There is   damage to the internal to IGBT of the phase
lMisoperation   is caused by interference.
The   connection of the driving wires is not good
Short-to-ground   occurs.
Increase the   ACC time
Change   the power unit
Check the   driving wires
Check if   there is strong interference to the external equipment
OUt2
Inverter
unit V
phase
protection
OUt3
Inverter
unit W
phase
protection
OV1
Accelerating overvoltage
The input   voltage is abnormal
There is   large energy feedback
No   braking components
Braking   energy is not open
Check the   input power
Check if   the DEC time of the load is too short or the VFD starts during the rotation   of the motor or it needs to increase the energy consumption components
Install   the dynamic braking components
Check the   setting of related function codes
OV2
Decelerating overvoltage
OV3
Constant overvoltage
OC1
Accelerating overcurrent
The   acceleration or deceleration is too fast
The   voltage of the grid is too low
The power   of the VFD is too low
The load transients   or is abnormal
The   grounding is short circuited or the output is phase loss
There is   strong external interference
The   overvoltage stall protection is not open
Increase   the ACC/DEC time
lCheck the   input power
Select   the VFD with a larger power
Check if   the load is short circuited (the grounding short circuited or the wire short   circuited) or the rotation is not smooth
Check the   output configuration.
OC2
Decelerating overcurrent
OC3
Constant overcurrent
UV
Bus
under-
voltage
fault
Check the   input power of the grid
OL1
Motor
overload
The rated   current of the motor is not correctly set
The motor   stall or load transients is too strong
Check the   power of the grid
Reset the   rated current of the motor
Check the   load and adjust the torque lift
OL2
VFD
overload
Reset the   rotating motor
The   voltage of the grid is too low.
The load   is too heavy.
The motor   power is too small
Avoid the   restarting after stopping.
Select a VFD   with bigger power.
Select a   proper motor.
SPI
Input
phase
loss
Phase   loss or fluctuation of input R,S,T
Check   input power
Check   installation distribution
SPO
Output
phase loss
U,V,W   phase loss input (or serious asymmetrical three phase of the load)
Check the   output distribution
Check the motor and cable
OH1
Rectifier module overheated
Air duct   jam or fan damage
Ambient   temperature is too high.
The time   of overload running is too long.
Dredge   the vent duct or replace the fan
Lower the   ambient temperature
OH2
Inverter module overheated
EF
External
fault
SI   external fault input terminals action
Check the   external device input
CE
485
commun-
ication
fault
The baud   rate setting is incorrect.
Fault   occurs to the communication wiring.
The   communication address is wrong.
There is   strong interference to the communication.
Set   proper baud rate
Check the   communication connection distribution
Set   proper communication address.
Change or   replace the connection distribution or improve the anti-interference   capability.
ItE
Current-
detecting
 fault
The connection   of the control board is not good
Hall components   are broken
The   modifying circuit is abnormal.
Check the   connector and repatch
Change   the Hall
Change   the main control panel
tE
Motor-autotuning fault
The motor   capacity does not comply with the VFD capability
The rated   parameter of the motor does not set correctly.
The   offset between the parameters from autotune and the standard parameter is   huge
Autotune   overtime
Change   the VFD mode
lSet the ratedparameter   according to the motor name plate
Empty the   motor load and reindentify
Check the   motor connection and set the parameter.
Check if   the upper limit frequency is above 2/3 of the rated frequency.
EEP
EEPROM
operation
 fault
Error of   controlling the write and read of the parameters
Damage to   EEPROM
Press STOP/RST   to reset
PIDE
PID
feedback
 outline
fault
PID   feedback offline
PID   feedback source disappear
Check the   PID feedback signal
Check the   PID feedback source
bCE
Braking
unit fault
Braking   circuit fault or damage to the braking pipes
The external   braking resistor is not sufficient
Check the   braking unit and change new braking pipe
Increase   the braking resistor
END
Running
 time arrival
The   actual running time of the VFD is above the internal setting running time.
Ask for   the supplier and adjust the setting running time.
OL3
Electrical overload
The VFD   will report overload pre-alarm according to the set value.
Check the   load and the overload pre-alarm point.
PCE
Keypad
commun-
ication
fault
The   connection of the keypad wires is not good or broken.
The   keypad wire is too long and affected by strong interference.
There is   circuit fault on the communication of the keypad and main board.
Check the   keypad wires and ensure whether there is mistake.
Check the   environment and avoid the interference source.
Change   the hardware and ask for service.
UPE
Parameters uploading fault
DNE
Parameters downloading fault
There is   mistake on the data storage of the keypad.
Repack-up   the data in the keypad.
E-DP
PROFIBUS communication fault
Communication   address is not correct.
Corresponding   resistor is not dialed
The files   of main stop GSD does not set sound
The   peripheral interference is too large.
Check   related setting
Check the   surrounding environment, and eliminate interference effects.
E-NET
Ethernet communication fault
The   Ethernet address is not set right.
The   Ethernet communication is not selected to right.
Check the   related setting.
Check the   communication method selection.
E-CAN
CANopen communication fault
The   connection is not sound
The   communication baud rate is not matched
Check the   connection
Draw out   the correspond resistor
Set the   same baud rate
ETH1
Grounding shortcut fault 1
The   output of the VFD is short circuited with the ground.
There is   fault in the current detection circuit.
The   actual motor power sharply differs from the VFD power.
Check if   the connection of the motor is normal or not
Change   the hall
Set motor   parameters correctly.
ETH2
Grounding shortcut fault 2
Change   the Hall
dEu
Speed deviation fault
The load   is too heavy or stalled.
Check the   load and ensure it is normal.
Increase   the detection time.
Check   whether the control parameters are normal.
STo
Maladjustment fault
The   control parameters of the synchronous motors not set properly.
The   autoturn parameter is not right.
The VFD   is not connected to the motor.
Check   whether the control parameter is set properly or not.
Increase   the maladjustment detection time.
LL
Electronic underload fault
The VFD   will report the underload pre-alarm according to the set value.
Check the   load and the underload pre-alarm point.
8.5.2 Other status
Code
State
Cause
Solution
PoFF
System power failure
The system is powered off or the bus   voltage is too low.
Check the grid conditions.
Failure of communication betweem the keypad   and main control panel
The keypad is not properly connected.
Check the installation environment of the   keypad.