10.4.1 Command code: 03H
03H (correspond to binary 0000 0011), read N words (Word)(Max. continuous reading is 16 words)
Command code 03H means that if the master read data form the VFD, the reading number depends on the "data number" in the command code. The Max. continuous reading number is 16 and the parameter address should be continuous. The byte length of every data is 2 (one word). The following command format is illustrated by hex (a number with "H" means hex) and one hex occupies one byte.
The command code is used to read the working stage of the VFD.
For example, read continuous 2 data content from0004H from the VFD with the address of 01H (read the content of data address of 0004H and 0005H), the frame structure is as below:
RTU master command message (from the master to the VFD)
START
T1-T2-T3-T4   (transmission time of 3.5 bytes)
ADDR
01H
CMD
03H
High bit of the   start bit
00H
Low bit of the   start bit
04H
High bit of data   number
00H
Low bit of data   number
02H
Low bit of CRC
85H
High bit of CRC
CAH
END
T1-T2-T3-T4 between START and END is to provide at least the time of 3.5 bytes as the leisure time and distinguish two messages for the avoidance of taking two messages as one message.
ADDR = 01H means the command message is sent to the VFD with the address of 01H and ADDR occupies one byte
CMD=03H means the command message is sent to read data form the VFD and CMD occupies one byte
"Start address" means reading data form the address and it occupies 2 bytes with the fact that the high bit is in the front and the low bit is in the behind.
"Data number" means the reading data number with the unit of word. If the "start address’ is 0004H and the "data number" is 0002H, the data of 0004H and 0005H will be read.
CRC occupies 2 bytes with the fact that the high bit is in the front and the low bit is in the behind.
RTU slave response message (from the VFD to the master)
START
ADDR
01H
CMD
03H
Byte number
04H
Data high bit of   address 0004H
13H
Data low bit of   address 0004H
88H
Data high bit of   address 0005H
00H
Data low bit of   address 0005H
00H
Low bit of CRC
7EH
High bit of CRC
9DH
END
The meaning of the response is that:
CMD=03H means the message is receiced from the VFD to the master for the response of reading command and CMD occupies one byte
"Byte number" means all byte number from the byte (excluding the byte) to CRC byte (excluding the byte). 04 means there are 4 byte of data from the "byte number" to "CRC CHK low bit", which are "digital address 0004H high bit", "digital address 0004H low bit", "digital address 0005H high bit" and "digital address 0005H low bit".
There are 2 bytes stored in one data with the fact that the high bit is in the front and the low bit is in the behind of the message, the data of data address 0004H is 1388H,and the data of data address 0005H is 0000H.
10.4.2  Command code: 06H
06H (correspond to binary 0000 0110), write one word (Word)
The command means that the master write data to the VFD and one command can write one data other than multiple dates. The effect is to change the working mode of the VFD.
For example, write 5000 (1388H) to 0004H from the VFD with the address of 02H, the frame structure is as below:
START
ADDR
02H
CMD
06H
High bit of writing data address
00H
Low bit of writing data address
04H
Data content
13H
Data content
88H
Low bit of CRC
C5H
High bit of CRC
6EH
END
START
ADDR
02H
CMD
06H
00H
04H
High bit of data content
13H
Low bit of data content
88H
Low bit of CRC
C5H
High bit of CRC
6EH
END
Note: section 10.2 and 10.3 mainly describe the command format, and the detailed application will be mentioned in 10.8 with examples.
10.4.3 Command code 08H for diagnosis
Meaning of sub-function codes
Sub-function Code
Description
0000
Return to   inquire information data
For example: The inquiry information string is same as the response information string when the loop detection to address 01H of driver is carried out.
The RTU request command is:
START
ADDR
01H
CMD
08H
High bit of sub-function code
00H
Low bit of sub-function code
00H
12H
ABH
Low bit of CRC
ADH
High bit of CRC
14H
END
The RTU response command is:
START
ADDR
01H
CMD
08H
00H
00H
12H
ABH
Low bit of CRC
ADH
High bit of CRC
14H
END
10.4.4  Command code: 10H, continuous writing
Command code 10H means that if the master writes data to the VFD, the data number depends on the "data number" in the command code. The Max. continuous reading number is 16.
For example, write 5000(1388H) to 0004H of the VFD whose slave address is 02H and 50(0032H) to 0005H, the frame structure is as below:
START
ADDR
02H
CMD
10H
High bit of write data
00H
Low bit of write data
04H
00H
02H
Byte number
04H
High bit of data 0004H
13H
Low bit of data 0004H
88H
High bit of data 0005H
00H
Low bit of data 0005H
32H
Low bit of CRC
C5H
High bit of CRC
6EH
END
START
ADDR
02H
CMD
10H
00H
04H
00H
02H
Low bit of CRC
C5H
High bit of CRC
6EH
END
10.4.5  The definition of data address
The address definition of the communication data in this part is to control the running of the VFD and get the state information and related function parameters of the VFD.
10.4.5.1 Function code address representation rules
The parameter address occupies 2 bytes with the fact that the high bit is in the front and the low bit is in the behind. The range of high and low byte are: high byte—00–ffH; low byte—00–ffH. The high byte is the group number before the radix point of the function code and the low byte is the number after the radix point. But both the high byte and the low byte should be changed into hex. For example P05.06, the group number before the radix point of the function code is 05, then the high bit of the parameter is 05, the number after the radix point 06, then the low bit of the parameter is 06, then t he function code address is 0506H and the parameter address of P10.01 is 0A01H.
Note: P29 group is the factory parameter which cannot be read or changed. Some parameters cannot be changed when the VFD is in the running state and some parameters cannot be changed in any state. The setting range, unit and related instructions should be paid attention to when modifying the function code parameters.
Besides, EEPROM is stocked frequently, which may shorten the usage time of EEPROM. For users, some functions are not necessary to be stocked on the communication mode. The needs can be met on by changing the value in RAM. Changing the high bit of the function code form 0 to 1 can also realize the function. For example, the function code P00.07 is not stocked into EEPROM. Only by changing the value in RAM can set the address to 8007H. This address can only be used in writing RAM other than reading. If it is used to read, it is an invalid address.
10.4.5.2 The address instruction of other function in Modbus
The master can operate on the parameters of the VFD as well as control the VFD, such as running or stopping and monitoring the working state of the VFD.
Below is the parameter list of other functions:
Function instruction
Address definition
Data meaning instruction
R/W characteristics
Communication  control command
2000H
0001H:forward   running
R/W
0002H:reverse   running
0003H:forward   jogging
0004H:reverse jogging
0005H:stop
0006H:coast to   stop (emergency stop)
0007H:fault reset
0008H:jogging   stop
The address of communication   setting
2001H
Communication   setting frequency(0–Fmax(unit: 0.01Hz))
R/W
2002H
PID given, range   (0–1000, 1000 corresponds to100.0% )
2003H
PID feedback,   range (0–1000, 1000 corresponds to100.0% )
R/W
2004H
Torque setting   value (-3000–3000, 1000 corresponds to the 100.0% of the rated current of the   motor)
R/W
2005H
The upper limit   frequency setting during forward rotation(0–Fmax(unit: 0.01Hz))
R/W
2006H
The upper limit   frequency setting during reverse rotation(0–Fmax(unit: 0.01Hz))
R/W
2007H
The upper limit   torque of electromotion torque  (0–3000,   1000 corresponds to the 100.0% of the rated current of the motor)
R/W
2008H
The upper limit   torque of braking torque  (0–3000, 1000   corresponds to the 100.0% of the rated current of the motor)
R/W
2009H
Special control command   word
Bit0–1:=00: motor 1     =01: motor   2
        =10: motor   3   =11: motor 4
Bit2:=1 torque control prohibit
=0: torque control prohibit invalid
Bit3:=1 power consumption clear
=0:no power consumption clear
Bit4:=1 pre-exciting enabling
 =0: pre-exciting   disabling
Bit5:=1   DC braking enabling
    =0: DC braking disabling
R/W
200AH
Virtual input   terminal command , range: 0x000–0x1FF
R/W
200BH
Virtual output   terminal command , range: 0x00–0x0F
R/W
200CH
Voltage setting   value (special for V/F separation)
(0–1000, 1000   corresponds to the 100.0%)
R/W
200DH
AO output setting   1
(-1000–1000, 1000   corresponds to 100.0%)
R/W
200EH
AO output setting   2
R/W
SW 1 of the VFD
2100H
R
0002H:forward   running
0003H:stop
0004H:fault
0005H: POFF state
0006H: pre-exciting state
SW 2 of the VFD
2101H
Bit0: =0: not ready   for operation  =1: ready for operation
Bi1–2:=00:motor 1   =01:motor 2
       =10:motor 3   =11:motor 4
Bit3:  =0:asynchronous   motor  =1:synchronous motor
Bit4:  =0:pre-alarm   without overload =1:overload pre-alarm
Bit5– Bit6: =00:   keypad control
=01: terminal contorl
=10: communication control
R
Fault code of the   VFD
2102H
See the fault   type instruction
R
Identifying code   of the VFD
2103H
GD300-----0x010a
R
Operation   frequency
3000H
R
Setting   freqency
3001H
R
Bus   voltage
3002H
0.0–2000.0V (unit: 0.1V)
R
Output   voltage
3003H
0–1200V (unit: 1V)
R
Output   current
3004H
0.0–3000.0A (unit: 0.1A)
R
Rotation   speed
3005H
0–65535 (unit: 1RPM)
R
Output   power
3006H
-300.0–300.0% (unit: 0.1%)
R
Output   torque
3007H
-250.0–250.0% (unit: 0.1%)
R
Close   loop setting
3008H
-100.0–100.0% (unit: 0.1%)
R
Close   loop feedback
3009H
R
Input   IO state
300AH
000–1FF
R
Output   IO state
300BH
000–1FF
R
Analog   input 1
300CH
0.00–10.00V (unit: 0.01V)
R
Analog   input 2
300DH
R
Analog   input 3
300EH
R
Analog   input 4
300FH
R
Read   input of high-speed pulse 1
3010H
0.00–50.00kHz (unit: 0.01Hz)
R
Read   input of high-speed pulse 2
3011H
R
Read   the current stage of multi-step speed
3012H
0–15
R
External   length
3013H
0–65535
R
External   counting
3014H
0–65535
R
Torque   setting
3015H
R
3016H
R
Fault   code
5000H
R
R/W characteristics means the function is with read and write characteristics. For example, "communication control command" is writing chrematistics and control the VFD with writing command (06H). R characteristic can only read other than write and W characteristic can only write other than read.
Note:when operate on the VFD with the table above, it is necessary to enable some parameters. For example, the operation of running and stopping, it is necessary to set P00.01 to communication running command channel and set P00.02 to Modbus communication channel. And when operate on "PID given", it is necessary to set P09.00 to "Modbus communication setting".
The encoding rules for device codes (corresponds to identifying code 2103H of the VFD)
High 8 bit
Meaning
Low 8 bit
Meaning
01
GD
0x08
GD35 vector VFD
0x09
GD35-H1 vector VFD
0x0a
GD300 vector VFD
0x0b
GD100 simple   vector VFD
0x0c
GD200 universal VFD
0x0d
GD10 mini VFD
10.4.6  Fieldbus ratio values
The communication data is expressed by hex in actual application and there is no radix point in hex. For example, 50.12Hz cannot be expressed by hex so 50.12 can be magnified by 100 times into 5012, so hex 1394H can be used to express 50.12.
A non-integer can be timed by a multiple to get an integer and the integer can be called fieldbus ratio values.
The fieldbus ratio values are refered to the radix point of the setting range or default value in the function parameter list. If there are figures behind the radix point (n=1), then the fieldbus ratio value m is 10n. Take the table as the example:
If there is one figure behind the radix point in the setting range or the default value, then the fieldbus ratio value is 10. if the data received by the upper monitor is 50, then the "hibernation restore delay time" is 5.0 (5.0=50÷10).
If Modbus communication is used to control the hibernation restore delay time as 5.0s. Firstly, 5.0 can be magnified by 10 times to integer 50 (32H) and then this data can be sent.
After the VFD receives the command, it will change 50 into 5 according to the fieldbus ratio value and then set the hibernation restore delay time as 5s.
Another example, after the upper monitor sends the command of reading the parameter of hibernation restore delay time ,if the response message of the VFD is as following:
Because the parameter data is 0032H (50) and 50 divided by 10 is 5, then the hibernation restore delay time is 5s.
10.4.7  Fault message response
There may be fault in the communication control. For example, some parameter can only be read. If a writing message is sent, the VFD will return a fault response message.
The fault message is from the VFD to the master, its code and meaning is as below:
Code
Meaning
01H
Illegal command
The command from master cannot be   executed. The reason maybe:
1. This command is only for new device;
2. Slave is in fault state and cannot execute it.
02H
Illegal data address.
Some of the operation addresses are invalid or not   allowed to access. Especially the combination of the register and the transmitting   bytes are invalid.
03H
Illegal value
When there are invalid data in the   message framed received by slave.
Note:This error   code does not indicate the data value to write exceed the range, but indicate   the message frame is an illegal frame.
04H
Operation failed
The parameter setting in parameter writing is   invalid. For example, the function input terminal cannot be set repeatedly.
05H
Password error
The password written to the password check address is not same as the   password set by P7.00.
06H
Data frame error
In the frame message sent by the upper monitor,   the length of the digital frame is incorrect or the counting of CRC check bit   in RTU is different from the lower monitor.
07H
Parameters only for reaf
It only happen in write command
08H
Parameters cannot be changed during running
The modified parameter in the writing of the upper   monitor cannot be modified during running.
09H
Password protection
When the upper monitor is writing or reading and   the user password is set without password unlocking, it will report that the   system is locked.
The slave uses functional code fields and fault addresses to indicate it is a normal response or some error occurs (named as objection response). For normal responses, the slave shows corresponding function codes, digital address or sub-function codes as the response. For objection responses, the slave returns a code which equals the normal code, but the first byte is logic 1.
For example: when the master sends a message to the slave, requiring it to read a group of address data of the VFD function codes, there will be following function codes:
0 0 0 0 0 0 1 1 (Hex 03H)
For normal responses, the slave responds the same codes, while for objection responses, it will return:
1 0 0 0 0 0 1 1 (Hex 83H)
Besides the function codes modification for the objection fault, the slave will respond a byte of abnormal code which defines the error reason.
When the master receives the response for the objection, in a typical processing, it will send the message again or modify the corresponding order.
For example, set the "running command channel" of the VFD (P00.01, parameter address is 0001H) with the address of 01H to 03, the command is as following:
But the setting range of "running command channel" is 0–2, if it is set to 3, because the number is beyond the range, the VFD will return fault response message as below:
Abnormal response code 86H means the abnormal response to writing command 06H; the fault code is 04H. In the table above, its name is operation failed and its meaning is that the parameter setting in parameter writing is invalid. For example, the function input terminal cannot be set repeatedly.
10.4.8  Example of writing and reading
Refer to 10.4.1 and 10.4.2 for the command format.
10.4.8.1 Example of reading command 03H
Read the state word 1 of the VFD with the address of 01H (refer to table 1). From the table 1, the parameter address of the state word 1 of the VFD is 2100H.
The command sent to the VFD:
If the response message is as below:
The data content is 0003H. From the table 1, the VFD stops.
Watch "the current fault type" to "the previous 5 times fault type" of the VFD through commands, the corresponding function code is P07.27–P07.32 and corresponding parameter address is 071BH–0720H(there are 6 from 071BH).
See from the returned data, all fault types are 0023H (decimal 35) with the meaning of maladjustment (STo).
10.4.8.2 Example of writing command 06H
Make the VFD with the address of 03H to run forward. See table 1, the address of "communication control command" is 2000H and forward running is 0001. See the table below.
The command sent by the master:
If the operation is success, the response may be as below (the same with the command sent by the master):
Set the Max. Output frequency of the VFD with the address of 03H as100Hz.
Function code
Detailed instruction   of parameters
Setting range
Default value
Modify
P00.03
Max. output frequency
P00.04~600.00H (400.00Hz)
100.00~600.00
50.00Hz
See the figures behind the radix point, the fieldbus ratio value of the Max. output frequency (P00.03) is 100. 100Hz timed by 100 is 10000 and the corresponding hex is 2710H.
If the operation is successful, the response may be as below (the same with the command sent by the master):
Note: the blank in the above command is for illustration. The blank cannot be added in the actual application unless the upper monitor can remove the blank by themselves.
10.4.8.3 Example of continous writing command 10H
Example 1: make the VFD whose address is 01H run forward at 10Hz. Refer to the instruction of 2000H and 0001. Set the address of "communication setting frequency" is 2001H and 10Hz corresponds to 03E8H. See the table below.
Address definition
R/W characteristics
2000H
R/W
0005H:stop
0007H:fault reset
0008H:jogging stop
2001H
R/W
2002H
Set P00.01 to 2 and P00.06 to 8.
Example 2: set the ACC time of 01H VFD as 10s and the DEC time as 20s
P00.11
ACC time 1
ACC time means the time needed if the VFD speeds   up from 0Hz to the Max. One (P00.03).
DEC time means the time needed if the VFD   speeds down from the Max. Output frequency to 0Hz (P00.03).
Goodrive300 series VFDs define four groups   of ACC/DEC time which can be selected by P05. The factory default ACC/DEC   time of the VFD is the first group.
Setting range of P00.11 and P00.12:0.0–3600.0s
Depend on model
P00.12
DEC time 1
Depend on model
The corresponding address of P00.11 is 000B, the ACC time of 10s corresponds to 0064H, and the DEC time of 20s corresponds to 00C8H.
Note: The space between above commands is for instruction and there is no space between the commands during actual applications.
10.4.8.4 Modbus communication debugging instance
A PC is used as the host, an RS232-RS485 converter is used for signal conversion, and the PC serial port used by the converter is COM1 (a RS232 port). The upper computer commissioning software is the serial port commissioning assistant Commix, which can be downloaded from the Internet. Download a version that can automatically execute the CRC check function. The following figure shows the interface of Commix.
First, select COM1 for "serial port" and the baud rate should be set to the same value with P14.01. The data bit, check bit and stop bit must be consistent with the setup in P14.02. As RTU mode is used here, "HEX" should be selected. Check image.pngto make the software add CRC automatically, and select CRC16 (ModbusRTU) with the starting byte being 1. Once enabled, CRC check will be added automatically, which removes the need to fill in CRC manually.
The commissioning command to set the VFD whose address is 03H to be forward running is as follows:
1.  Set the address (P14.00) of the VFD to 03.
2.  Set "Channel of running commands" (P00.01) to "Communication", and set "Communication channel of running commands" (P00.02) to the Modbus communication channel.
3. Click Send. If the line configuration and settings are correct, a response transmitted by the VFD will be received.