When a fault occurred, handle the fault as follows.
1. When a VFD fault occurred, confirm whether keypad display is improper? If yes, contact INVT;
2. If keypad works properly, check the function codes in P07 group to confirm the corresponding fault record parameters, and determine the real state when current fault occurred through parameters;
3. Check the table below to see whether corresponding exception states exist based on the corresponding corrective measures;
4. Rule out the faults or ask for help from professionals;
5. After confirming faults are removed, reset the fault and start running.
Fault code | Fault type | Possible cause | Solution |
OUt1 | Inverter unit Phase-U protection | Acceleration is too fast; IGBT module is damaged; Misacts caused by interference; drive wires are poorly connected ; To-ground short circuit occurs | Increase acceleration time; Replace the power unit; Check drive wires; Check whether there is strong interference surrounds the peripheral equipment |
OUt2 | Inverter unit Phase-V protection | ||
OUt3 | Inverter unit Phase-W protection | ||
OV1 | Over-voltage during acceleration | Exception occurred to input voltage; Large energy feedback; Lack of braking units; Dynamic brake is not enabled | Check input power; Check whether load deceleration time is too short; or the motor starts during rotating; Install dynamic braking units; Check the setup of related function codes |
OV2 | Over-voltage during deceleration | ||
OV3 | Over-voltage during constant speed running | ||
OC1 | Over-current during acceleration | Acceleration is too fast; Grid voltage is too low; Inverter power is too small; Load transient or exception occurred; To-ground short circuit or output phase loss occur; Strong external interference sources; Overvoltage stall protection is not enabled | Increase acceleration /deceleration time; Check if the load is short circuited (to-ground short circuit or line-to-line short circuit) or the rotation is not smooth; Check the output wiring; Check if there is strong interference; Check the setup of related function codes. |
OC2 | Over-current during deceleration | ||
OC3 | Over-current during constant speed running | ||
UV | Bus undervoltage fault | Grid voltage is too low; Overvoltage stall protection is not enabled | Check grid input power; Check the setup of related function codes |
OL1 | Motor overload | Grid voltage is too low; Rated motor current is set improperly; Motor stall or load jumps violently | Check grid voltage; Reset rated motor current; Check the load and adjust torque boost |
OL2 | Inverter overload | Acceleration is too fast; The motor in rotating is restarted; Grid voltage is too low; Load is too large; Power is too small; | Increase acceleration time; Avoid restart after stop; Check grid voltage; Select the VFD with larger power; Select proper motor |
SPI | Phase loss on input side | Phase loss or violent fluctuation occurred to R, S and T input | Check the input power; Check installation wiring |
SPO | Phase loss on output side | Phase loss occurred to U, V, W output (or the three phases of motor is asymmetrical) | Check the output wiring; Check the motor and cable |
OH1 | Overheat of rectifier module | Air duct is blocked or fan is damaged; Ambient temperature is too high; Long-time overload running | Ventilate the air duct or replace the fan; Lower the ambient temperature |
OH2 | Overheat of VFD module | ||
EF | External fault | SI external fault input terminal acts | Check external device input |
CE | Modbus/Modbus TCP communication fault | Baud rate is set improperly; Communication line fault; Communication address error; Communication suffers from strong interference | Set proper baud rate; Check the wiring of communication interfaces; Set proper communication address; Replace or change the wiring to enhance anti-interference capacity |
ItE | Current detection fault | Poor contact of the connector of control board; Hall component is damaged; Exception occurred to amplification circuit | Check the connector and re-plug; Replace the hall component; Replace the main control board |
tE | Motor autotuning fault | Motor capacity does not match with the VFD capacity, this fault may occur easily if the difference between them is exceeds five power classes; Motor parameter is set improperly; The parameters gained from autotuning deviate sharply from the standard parameters; Autotuning timeout | Change the VFD model, or adopt V/F mode for control; Set proper motor type and nameplate parameters; Empty the motor load and carry out autotuning again; Check motor wiring and parameter setup; Check whether upper limit frequency is larger than 2/3 of the rated frequency |
EEP | EEPROM fault | R/W error occurred to the control parameters; EEPROM is damaged | Press STOP/RST to reset; Replace the main control board |
PIDE | PID feedback offline fault | PID feedback offline; PID feedback source disappears; | Check PID feedback signal wires; Check PID feedback source |
bCE | Braking unit fault | Brake circuit fault or brake tube is damaged; The resistance of external braking resistor is too small | Check the braking unit, replace with new brake tubes; Increase brake resistance |
END | Running time is up | The actual running time of the VFD is larger than the set running time | Ask help from the supplier, adjust the set running time |
OL3 | Electronic overload fault | The VFD releases overload pre-alarm based on the set value | Check the load and overload pre-alarm threshold |
PCE | Keypad communication fault | The keypad wire is poorly contacted or disconnected; The keypad wire is too long and suffers strong interference; Circuit fault occurred to the keypad or communication part of the main board | Check the keypad wires to confirm whether fault exists; Check the surroundings to rule out interference source; Replace the hardware and ask for maintenance service |
UPE | Parameter upload error | The keypad wire is poorly contacted or disconnected; The keypad wire is too long and suffers strong interference; Circuit fault occurred to the keypad or communication part of the main board | Check the surroundings to rule out interference source; Replace the hardware and ask for maintenance service; Replace the hardware and ask for maintenance service |
DNE | Parameter download error | The keypad wire is poorly contacted or disconnected; The keypad wire is too long and suffers strong interference; Data storage error occurred to the keypad | Check the surroundings to rule out interference source; Replace the hardware and ask for maintenance service; Re-backup keypad data |
ETH1 | To-ground short circuit fault 1 | Inverter output is short connected to the ground; Current detection circuit is faulty; Actual motor power setup deviates sharply from the VFD power | Check whether motor wiring is proper; Replace the hall component; Replace the main control board; Reset the motor parameters properly |
ETH2 | To-ground short circuit fault 1 | Inverter output is short connected to ground; Current detection circuit is faulty; Actual motor power setup deviates sharply from the VFD power | Check whether motor wiring is proper; Replace the hall component; Replace the main control board; Reset the motor parameters properly |
dEu | Speed deviation fault | Load is too heavy, or stall occurred | Check the load to ensure it is proper, increase the detection time; Check whether control parameters are set properly |
STo | Maladjustment fault | Control parameters of synchronous motor is set improperly; The parameter gained from autotuning is inaccurate; The VFD is not connected to motor | Check the load to ensure it is proper, Check whether load is proper; Check whether control parameters are set correctly; Increase maladjustment detection time |
LL | Electronic underload fault | The VFD performs underload pre-alarm based on the set value | Check the load and overload pre-alarm threshold |
ENC1O | Encoder offline fault | Encoder line sequence is wrong, or signal wires are poorly connected | Check the encoder wiring |
ENC1D | Encoder reversal fault | The encoder speed signal is contrary to the motor running direction | Reset encoder direction |
ENC1Z | Encoder Z pulse offline fault | Z signal wires are disconnected | Check the wiring of Z signal |
OT | Motor over-temperature fault | Motor over-temperature input terminal is valid; Exception occurred to t temperature detection Exception occurred to resistor; Long-time overload running or exception occurred | Check the wiring of motor over-temperature input terminal (terminal function 57); Check whether temperature sensor is proper; Check the motor and perform maintenance on the motor |
STO | Safe torque off | Safe torque off function is enabled by external forces | / |
STL1 | Exception occurred to safe circuit of channel H1 | The wiring of STO is improper; Fault occurred to external switch of STO; Hardware fault occurred to safety circuit of channel H1 | Check whether terminal wiring of STO is proper and firm enough; Check whether external switch of STO can work properly; Replace the control board |
STL2 | Exception occurred to channel H2 safe circuit | The wiring of STO is improper; Fault occurred to external switch of STO; Hardware fault occurred to safety circuit of channel H2 | Check whether terminal wiring of STO is proper and firm enough; Check whether external switch of STO can work properly; Replace the control board |
STL3 | Exception occurred to channel H1 and channel H2 | Hardware fault occurred to STO circuit | Replace the control board |
CrCE | Safety code FLASH CRC check fault | Control board is faulty | Replace the control board |
E-Err | Repetitive expansion card type | The two inserted expansion cards are of the same type | Users should not insert two cards with the same type; check the type of expansion card, and remove one card after power down |
ENCUV | Encoder UVW loss fault | No electric level variation occurred to UVW signal | Check the wiring of UVW; Encoder is damaged |
F1-Er | Failed to identify the expansion card in card slot 1 | There is data transmission in interfaces of card slot 1, however, it cannot read the card type | Confirm whether the expansion card inserted can be supported; Stabilize the expansion card interfaces after power down, and confirm whether fault still occurs at next power-on; Check whether the insertion port is damaged, if yes, replace the insertion port after power down |
F2-Er | Failed to identify the expansion card in card slot 2 | There is data transmission in interfaces of card slot 2, however, it cannot read the card type | Confirm whether the expansion card inserted can be supported; Stabilize the expansion card interfaces after power down, and confirm whether fault still occurs at next power-on; Check whether the insertion port is damaged, if yes, replace the insertion port after power down |
F3-Er | Failed to identify the expansion card in card slot 3 | There is data transmission in interfaces of card slot 3, however, it cannot read the card type | Confirm whether the expansion card inserted can be supported; Stabilize the expansion card interfaces after power down, and confirm whether fault still occurs at next power-on; Check whether the insertion port is damaged, if yes, replace the insertion port after power down |
C1-Er | Communication timeout occurred to the expansion card in card slot 1 | There is no data transmission in interfaces of card slot 1 | Confirm whether the expansion card inserted can be supported; Stabilize the expansion card interfaces after power down, and confirm whether fault still occurs at next power-on; Check whether the insertion port is damaged, if yes, replace the insertion port after power down |
C2-Er | Communication timeout occurred to the expansion card in card slot 2 | There is no data transmission in interfaces of card slot 2 | Confirm whether the expansion card inserted can be supported; Stabilize the expansion card interfaces after power down, and confirm whether fault still occurs at next power-on; Check whether the insertion port is damaged, if yes, replace the insertion port after power down |
C3-Er | Communication timeout occurred to the expansion card in card slot 3 | There is no data transmission in interfaces of card slot 3 | Confirm whether the expansion card inserted can be supported; Stabilize the expansion card interfaces after power down, and confirm whether fault still occurs at next power-on; Check whether the insertion port is damaged, if yes, replace the insertion port after power down |
E-DP | Profibus card communication timeout fault | There is no data transmission between the communication card and the host computer (or PLC) | Check whether the communication card wiring is loose or dropped |
E-NET | Ethernet card communication timeout fault | There is no data transmission between the communication card and the host computer | Check whether the communication card wiring is loose or dropped |
E-CAN | CANopen card communication timeout fault | There is no data transmission between the communication card and the host computer (or PLC) | Check whether the communication card wiring is loose or dropped |
E-PN | Profinet card communication timeout fault | There is no data transmission between the communication card and the host computer (or PLC) | Check whether the communication card wiring is loose or dropped |
E-CAT | EtherCat card communication timeout fault | There is no data transmission between the communication card and the host computer (or PLC) | Check whether the communication card wiring is loose or dropped |
E-BAC | BACNet card communication timeout fault | There is no data transmission between the communication card and the host computer (or PLC) | Check whether the communication card wiring is loose or dropped |
E-DEV | DeviceNET card communication timeout fault | There is no data transmission between the communication card and the host computer (or PLC) | Check whether the communication card wiring is loose or dropped |
ESCAN | Can master/slave communication card communication timeout fault | There is no data transmission between the CAN master and slave communication cards | Check whether the communication card wiring is loose or dropped |
S-Err | Master-slave synchronous CAN slave fault | Fault occurred to one of the CAN slave VFDs | Detect the CAN slave VFD and analyze the corresponding fault cause of the VFD |
E-EIP | EtherNetIP card communication timeout | No data transferred between the communication card and upper computer (or PLC) | Check whether the communication card cable is loosen or disconnected. |
Displayed code | State type | Possible cause | Solution |
PoFF | System power failure | The system is powered off or the bus voltage is too low. | Check the grid conditions. |