8.4.1 Capacitor reforming

If the VFD has been left unused for a long time, you need to follow the instructions to reform the DC bus capacitor before using it. The storage time is calculated from the date the VFD is delivered.

Storage time

Operation    instruction

Less than 1 year

No charging operation   is required.

1 to 2 years

The VFD needs to be   powered on for 1 hour before the first running command.

2 to 3 years

Use a voltage   controlled power supply to charge the VFD:

Charge the VFD at 25%   of the rated voltage for 30 minutes, and then charge it at 50% of the rated   voltage for 30 minutes, at 75% for another 30 minutes, and finally charge it   at 100% of the rated voltage for 30 minutes.

More than 3 years

Use a voltage   controlled power supply to charge the VFD:

Charge the VFD at 25%   of the rated voltage for 2 hours, and then charge it at 50% of the rated   voltage for 2 hours, at 75% for another 2 hours, and finally charge it at   100% of the rated voltage for 2 hours.

 

The method for using a voltage controlled power supply to charge the VFD is described as follows:

The selection of a voltage controlled power supply depends on the power supply of the VFD. For VFDs with an incoming voltage of 1PH/3PH 230 V AC, you can use a 230 V AC/2 A voltage regulator. Both 1PH and 3PH VFDs can be charged with a 1PH voltage controlled power supply (connect L+ to R, and N to S or T). All the DC bus capacitors share one rectifier, and therefore they are all charged.

For VFDs of a high voltage class, ensure that the voltage requirement (for example, 380 V) is met during charging. Capacitor changing requires little current, and therefore you can use a small-capacity power supply (2 A is sufficient).

The method for using a resistor (incandescent lamp) to charge the drive is described as follows:

If you directly connect the drive device to a power supply to charge the DC bus capacitor, it needs to be charged for a minimum of 60 minutes. The charging operation must be performed at a normal indoor temperature without load, and you must connect a resistor in series mode in the 3PH circuit of the power supply.

For a 380 V drive device, use a resistor of 1 kΩ/100W. If the voltage of the power supply is no higher than 380 V, you can also use an incandescent lamp of 100W. If an incandescent lamp is used, it may go off or the light may become very weak.

image.png


8.4.2 Electrolytic capacitor replacement

image.png

² Read the safety precautions carefully and   follow the instructions to perform operations. Otherwise, physical injuries   or damage to the device may be caused.

The electrolytic capacitor of the VFD must be replaced if it has been used for more than 35,000 hours. For details about the replacement, contact the local INVT office.