9.4.1 Command code 03H, reading N words (continuously up to 16 words)
The command code 03H is used by the master to read data from the VFD. The count of data to be read depends on the "data count" in the command. A maximum of 16 pieces of data can be read. The addresses of the read parameters must be contiguous. Each piece of data occupies 2 bytes, that is, one word. The command format is presented using the hexadecimal system (a number followed by "H" indicates a hexadecimal value). One hexadecimal value occupies one byte.
For example, starting from the data address of 0004H, to read two contiguous pieces of data (that is, to read content from the data addresses 0004H and 0005H) of the VFD whose address is 01H, the frame structures are described in the following.
RTU master command (sent from the master to the VFD):
START
T1-T2-T3-T4 (time gap with a min. length   of 3.5 bytes)
ADDR (address)
01H
CMD (command code)
03H
Start address high-order   bit
00H
Start address low-order   bit
04H
Data count high-order   bit
00H
Data count low-order   bit
02H
CRC low-order bit
85H
CRC high-order   bit
CAH
END
"START" and "END" are "T1-T2-T3-T4 (time gap with a min. length of 3.5 bytes)", indicating that a time gap with a minimum length of 3.5 bytes must be kept before RS485 communication is executed. The time gap is used to distinguish one message from another so that the two messages are not regarded as one message.
"ADDR" is "01H", indicating that the command is sent to the VFD whose address is 01H. The ADDR information occupies one byte.
"CMD" is "03H", indicating that the command is used to read data from the VFD. The CMD information occupies one byte.
"Start address" indicates that data reading is started from this address. It occupies two bytes, with the high-order bit on the left and low-order bit on the right.
"Data count" indicates the count of data to be read (unit: word). "Start address" is "0004H" and "Data count" is 0002H, indicating that data is to be read from the data addresses of 0004H and 0005H.
CRC check occupies two bytes, with the low-order bit on the left and high-order bit on the right.
RTU slave response (sent from the VFD to the master):
START
ADDR
01H
CMD
03H
High-order bit of data in 0004H
04H
Low-order bit of data in 0004H
13H
High-order bit of data in 0005H
88H
Low-order bit of data in 0005H
00H
CRC low-order bits
00H
CRC high-order   bits
7EH
9DH
END
The definition of the response information is described as follows:
"ADDR" is "01H", indicating that the message is sent from the VFD whose address is 01H. The ADDR information occupies one byte.
"CMD" is "03H", indicating that the message is a VFD response to the 03H command from the master for reading data. The CMD information occupies one byte.
"Number of bytes" indicates the number of bytes between a byte (not included) and the CRC byte (not included). The value "04" indicates that there are four bytes of data between "Number of bytes" and "CRC low-order bit", that is, "High-order bit of data in 0004H", "Low-order bit of data in 0004H", "High-order bit of data in 0005H", and "Low-order of data in 0005H".
A piece of data is two bytes, with the high-order bits on the left and low-order bit on the right. From the response, the data in 0004H is 1388H, and that in 0005H is 0000H.
9.4.2 Command word 06H, writing a word
This command is used by the master to write data to the VFD. One command can be used to write only one piece of data. It is used to modify the parameters and running mode of the VFD. For example, to write 5000 (1388H) to 0004H of the VFD whose address is 02H, the frame structures are described in the following.
START
ADDR
02H
CMD
06H
High-order bit of data writing address
00H
Low-order bit of data writing address
04H
Data content high-order bit
13H
Data content low-order bit
88H
CRC low-order bit
C5H
CRC high-order bit
6EH
END
START
ADDR
02H
CMD
06H
00H
04H
13H
88H
CRC low-order bit
C5H
CRC high-order bit
6EH
END
Note: Sections 9.4.1 and 9.4.2 mainly describe the command formats. For the detailed application, see section 9.4.8.
9.4.3 Command code 08H, diagnosis
Sub-function code description:
Sub-function code
Description
0000
Return   data based on query requests
For example, to query about the circuit detection information about the VFD whose address is 01H, the query and return strings are the same, and the formats are described in the following tables.
RTU master command:
START
ADDR
01H
CMD
08H
Sub-function code high-order bit
00H
Sub-function code low-order bit
00H
12H
ABH
CRC CHK   low-order bit
ADH
CRC CHK   high-order bit
14H
END
RTU slave response:
START
ADDR
01H
CMD
08H
00H
00H
12H
ABH
ADH
14H
END
9.4.4 Command code 10H, continuous writing
The command code 10H is used by the master to write data to the VFD. The quantity of data to be written is determined by "Data count", and a maximum of 16 pieces of data can be written.
For example, to write 5000 (1388H) and 50 (0032H) respectively to 0004H and 0005H of the VFD whose slave address is 02H, the frame structures are described in the following.
START
ADDR
02H
CMD
10H
00H
04H
00H
02H
Number of bytes
04H
Content high-order bit of 0004H
13H
Content low-order bit of 0004H
88H
Content high-order bit of 0005H
00H
Content low-order bit of 0005H
32H
CRC low-order bit
C5H
CRC high-order bit
6EH
END
START
ADDR
02H
CMD
10H
00H
04H
00H
02H
CRC low-order bit
C5H
CRC high-order bit
6EH
END
9.4.5 Data address definition
This section describes the address definition of communication data. The addresses are used for controlling the running, obtaining the status information, and setting function parameters of the VFD.
9.4.5.1 Function code address format rules
The address of a function code consists of two bytes, with the high-order bit on the left and low-order bit on the right. The high-order bit ranges from 00 to ffH, and the low-order bit also ranges from 00 to ffH. The high-order bit is the hexadecimal form of the group number before the dot mark, and low-order bit is that of the number behind the dot mark. Take P05.06 as an example: The group number is 05, that is, the high-order bit of the parameter address is the hexadecimal form of 05; and the number behind the dot mark is 06, that is, the low-order bit is the hexadecimal form of 06. Therefore, the function code address is 0506H in the hexadecimal form. For example, the parameter address ofP10.01 is 0A01H.
Function code
Description
Setting   range
Default
Modify
P10.00
Simple PLC mode
0: Stop after running once
1: Keep running with the final value after   running once
2: Cyclic running
0–2
P10.01
Simple PLC memory   selection
0: Without memory after power-off
1: With memory after power-off
0–1
The parameters in the P99 group are set by the manufacturer and cannot be read or modified. Some parameters cannot be modified when the VFD is running; some cannot be modified regardless of the VFD status. Pay attention to the setting range, unit, and description of a parameter when modifying it.
The service life of the Electrically Erasable Programmable Read-Only Memory (EEPROM) may be reduced if it is frequently used for storage. Some function codes do not need to be stored during communication. The application requirements can be met by modifying the value of the on-chip RAM, that is, modifying the MSB of the corresponding function code address from 0 to 1. For example, if P00.07 is not to be stored in the EEPROM, you need only to modify the value in the RAM, that is, set the address to 8007H. The address can be used only for writing data to the on-chip RAM, and it is invalid when used for reading data.
9.4.5.2 Description of other function addresses
In addition to modifying the parameters of the VFD, the master can also control the VFD, such as starting and stopping it, and monitoring the operation status of the VFD. The following table describes other function parameters.
Function
Address
Data description
R/W
Communication-based control command
2000H
0001H: Forward running
R/W
0002H: Reverse running
0003H: Forward jogging
0004H: Reverse jogging
0005H: Stop
0006H: Coast to stop   (emergency stop)
0007H: Fault reset
0008H: Jogging to stop
Communication-based value   setting
2001H
Communication-based   frequency setting (0–Fmax, unit: 0.01 Hz)
R/W
2002H
PID setting, range (0–1000, 1000 corresponding to 100.0%)
2003H
PID feedback,   range (0–1000, 1000 corresponding to 100.0%)
R/W
2004H
Torque setting   (-3000 – +3000, 1000 corresponding to 100.0% of the motor rated current)
R/W
2005H
Setting of the upper limit of the forward running frequency (0–Fmax,   unit: 0.01 Hz)
R/W
2006H
Setting of the upper limit of the reverse running frequency (0–Fmax,   unit: 0.01 Hz)
R/W
2007H
Upper limit of the electromotion torque (0–3000, 1000 corresponding to   100.0% of the motor rated current)
R/W
2008H
Upper limit of the brake torque (0–3000, 1000 corresponding to 100.0%   of the motor rated current)
R/W
2009H
Special control command word:
Bit0–1: =00: Motor 1   =01: Motor 2
Bit2: =1 Enable speed/torque control switchover
=0:   Disable speed/torque control switchover
Bit3: =1 Clear electricity consumption
=0:   Not clear electricity consumption
Bit4: =1 Pre-excitation; =0: Disable   pre-excitation
Bit5: =1 DC   brake  =0: Disable DC brake
R/W
200AH
Virtual input   terminal command, range: 0x000–0x3FF
Corresponding to   S8/S7/S6/S5/HDIB/HDIA/S4/ S3/ S2/S1
R/W
200BH
Virtual output   terminal command, range: 0x00–0x0F
Corresponding to   local RO2/RO1/HDO/Y1
R/W
200CH
Voltage setting   (used for V/F separation)
(0–1000, 1000   corresponding to 100.0% of the motor rated voltage)
R/W
200DH
AO output setting   1 (-1000–+1000, 1000 corresponding to   100.0%)
R/W
200EH
AO output setting   2 (-1000–+1000, 1000 corresponding to   100.0%)
R/W
VFD status word 1
2100H
R
0003H: Stopped
0004H: Faulty
0005H: POFF
0006H: Pre-excited
VFD status word 2
2101H
Bit0:  =0: Not ready to run =1: Ready to run
Bi1–2: =00: Motor 1   =01: Motor 2
Bit3: =0: Asynchronous   motor  =1: Synchronous motor
Bit4: =0: No overload   alarm =1: Overload alarm
Bit5–Bit6: =00: Keypad-based   control   =01: Terminal-based control
=10: Communication-based   control
Bit7: Reserved
Bit8: =0: Speed   control  =1: Torque control
Bit9: =0: Non   position control
=1: Position control
Bit11–Bit10:   =0: Vector 0  =1: Vector 1
=2: Closed-loop vector
=3: Space voltage vector
R
VFD fault code
2102H
See the   description of fault types.
R
VFD identification code
2103H
GD350A-----0x01A2
R
Running frequency
3000H
0–Fmax (Unit: 0.01Hz)
Compatible with   CHF100A and CHV100 communication addresses
R
Set frequency
3001H
R
Bus voltage
3002H
0.0–2000.0V (Unit: 0.1V)
R
Output voltage
3003H
0–1200V (Unit: 1V)
R
Output current
3004H
0.0–3000.0A (Unit: 0.1A)
R
Rotating speed
3005H
0–65535 (Unit: 1RPM)
R
Output power
3006H
-300.0–300.0% (Unit: 0.1%)
R
Output torque
3007H
-250.0–250.0% (Unit: 0.1%)
R
Closed-loop setting
3008H
-100.0–100.0% (Unit: 0.1%)
R
Closed-loop feedback
3009H
R
Input state
300AH
000–3F
Corresponding   to the local HDIB/ HDIA/S4/S3/S2/S1
R
Output state
300BH
000–0F
Corresponding   to the local RO2/RO1/HDO/Y1
R
Analog input 1
300CH
0.00–10.00V (Unit: 0.01V)
R
Analog input 2
300DH
R
Analog input 3
300EH
-10.00–10.00V (Unit: 0.01V)
R
Analog input 4
300FH
R
Read input of HDIA high-speed pulse
3010H
0.00–50.00kHz (Unit: 0.01Hz)
R
Read input of HDIB high-speed pulse
3011H
R
Read current step of multi-step speed
3012H
0–15
R
External length
3013H
0–65535
R
External count value
3014H
0–65535
R
Torque setting
3015H
R
Identification code
3016H
R
Fault code
5000H
R
The Read/Write (R/W) characteristics indicate whether a function can be read and written. For example, "Communication-based control command" can be written, and therefore the command code 6H is used to control the VFD. The R characteristic indicates that a function can only be read, and W indicates that a function can only be written.
Note: Some parameters in the preceding table are valid only after they are enabled. Take the running and stop operations as examples, you need to set "Running command channel" (P00.01) to "Communication", and set "Communication running command channel" (P00.02) to the Modbus communication channel. For another example, when modifying "PID setting", you need to set "PID reference source" (P09.00) to Modbus communication.
The following table describes the encoding rules of device codes (corresponding to the identification code 2103H of the VFD).
Eight high-order bits of code
Meaning
Eight low-order bits of code
Meaning
01
GD
0x08
GD35 vector VFD
0x09
GD35-H1 vector VFD
0x0a
GD300 vector VFD
0xa0
GD350 vector VFD
0xa1
GD350-UL vector VFD
0xa2
GD350A vector VFD
9.4.6 Fieldbus scale
In practical applications, communication data is represented in the hexadecimal form, but hexadecimal values cannot represent decimals. For example, 50.12 Hz cannot be represented in the hexadecimal form. In such cases, we can multiply 50.12 by 100 to obtain an integer 5012, and then 50.12 can be represented as 1394H (5012 in the decimal form) in the hexadecimal form.
In the process of multiplying a non-integer by a multiple to obtain an integer, the multiple is referred to as a fieldbus scale.
The fieldbus scale depends on the number of decimals in the value specified in "Detailed parameter description" or "Default value". If there are n decimals in the value, the fieldbus scale m is the nth-power of 10. Take the following table as an example, m is 10.
Function code
Description
Setting range
Default
Modify
P01.20
Wake-up-from-sleep   delay
0.0–3600.0s (valid   when P01.19 is 2)
0.00–3600.0
0.0s
P01.21
Restart after   power failure
0:   Disable
1:   Enable
0–1
The value specified in "Setting range" or "Default" contains one decimal, so the fieldbus scale is 10. If the value received by the upper computer is 50, the value of "Wake-up-from-sleep delay" of the VFD is 5.0 (5.0=50/10).
To set the "Wake-up-from-sleep delay" to 5.0s through Modbus communication, you need first to multiply 5.0 by 10 according to the scale to obtain an integer 50, that is, 32H in the hexadecimal form, and then transmit the following write command:
After receiving the command, the VFD converts 50 into 5.0 based on the fieldbus scale, and then sets "Wake-up-from-sleep delay" to 5.0s.
For another example, after the upper computer transmits the "Wake-up-from-sleep delay" parameter read command, the master receives the following response from the VFD:
The parameter data is 0032H, that is, 50, so 5.0 is obtained based on the fieldbus scale (50/10=5.0). In this case, the master identifies that the "Wake-up-from-sleep delay" is 5.0s.
9.4.7 Error message response
Operation errors may occur in communication-based control. For example, some parameters can only be read, but a write command is transmitted. In this case, the VFD returns an error message response.
Error message responses are sent from the VFD to the master. The following table describes the codes and definitions of the error message responses.
Code
Description
01H
Invalid command
The command code   received by the upper computer is not allowed to be executed. The possible   causes are as follows:
• The function code is   applicable only on new devices and is not implemented on this device.
• The slave is in the   faulty state when processing this request.
02H
Invalid data address
For the VFD, the data   address in the request of the upper computer is not allowed. In particular, the   combination of the register address and the number of the to-be-transmitted   bytes is invalid.
03H
Invalid data value
The received data   domain contains a value that is not allowed. The value indicates the error of   the remaining structure in the combined request.
Note: It does not mean that the data item submitted for storage in the   register includes a value unexpected by the program.
04H
Operation failure
The parameter is set to an invalid value in the write operation. For   example, a function input terminal cannot be set repeatedly.
05H
Password error
The password entered in the password verification address is different   from that set in P07.00.
06H
Data frame error
The length of the data frame transmitted by the upper computer is   incorrect, or in the RTU format, the value of the CRC check bit is   inconsistent with the CRC value calculated by the lower computer.
07H
Parameter read-only
The parameter to be modified in the write operation of the upper   computer is a read-only parameter.
08H
Parameter cannot be modified in running
The parameter to be modified in the write operation of the upper   computer cannot be modified during the running of the VFD.
09H
Password protection
A user password is set, and the upper computer does not provide the   password to unlock the system when performing a read or write operation. The   error of "system locked" is reported.
When returning a response, the slave device uses a function code domain and fault address to indicate whether it is a normal response (no error) or exception response (some errors occur). In a normal response, the device returns the corresponding function code and data address or sub-function code. In an exception response, the device returns a code that is equal to a normal code, but the first bit is logic 1.
For example, if the master device transmits a request message to a slave device for reading a group of function code address data, the code is generated as follows:
0 0 0 0 0 0 1 1  (03H in the hexadecimal form)
For an exception response, the following code is returned:
1 0 0 0 0 0 1 1 (83H in the hexadecimal form)
In addition to the modification of the code, the slave device returns a byte of exception code that describes the cause of the exception. After receiving the exception response, the typical processing of the master device is to transmit the request message again or modify the command based on the fault information.
For example, to set the "Channel of running commands" (P00.01, the parameter address is 0001H) of the VFD whose address is 01H to 03, the command is as follows:
However, the setting range of the "Running command channel" is 0 to 2. The value 3 exceeds the setting range. In this case, the VFD returns an error message response as shown in the following:
The exception response code 86H (generated based on the highest-order bit "1" of the write command 06H) indicates that it is an exception response to the write command (06H). The error code is 04H. From the preceding table, we can see that it indicates the error "Operation failure", which means "The parameter is set to an invalid value in the write operation".
9.4.8 Read/Write operation example
For details about the formats of the read and write commands, see sections 9.4.1 and 9.4.2.
9.4.8.1 Examples of read command 03H
Example 1: Read status word 1 of the VFD whose address is 01H. According to the table of other function addresses, the parameter address of status word 1 of the VFD is 2100H.
The read command transmitted to the VFD is as follows:
Assume that the following response is returned:
The data content returned by the VFD is 0003H, which indicates that the VFD is in the stopped state.
Example 2: View information about the VFD whose address is 03H, including "Present fault type" (P07.27) to "5th-last fault type" (P07.32) of which the parameter addresses are 071BH to 0720H (contiguous 6 parameter addresses starting from 071BH).
The command transmitted to the VFD is as follows:
According to the returned data, all the fault types are 0023H, that is, 35 in the decimal form, which means the maladjustment fault (STo)
9.4.8.2 Examples of write command 06H
Example 1: Set the VFD whose address is 03H to be forward running. Refer to the table of other function parameters, the address of "Communication-based control command" is 2000H, and 0001H indicates forward running.
Function
Address
Data description
R/W
2000H
R/W
0005H: Stop
0007H: Fault reset
The command transmitted by the master is as follows:
If the operation is successful, the following response is returned (same as the command transmitted by the master):
Example 2: Set the "Max. output frequency" of the VFD whose address is 03H to 100 Hz.
Function code
Description
Setting range
Default
Modify
P00.03
P00.04–600.00H (400.00Hz)
100.00–600.00
50.00Hz
According to the number of decimals, the fieldbus scale of the "Max. output frequency" (P00.03) is 100. Multiply 100 Hz by 100. The value 10000 is obtained, and it is 2710H in the hexadecimal form.
Note: In the preceding command description, spaces are added to a command just for explanatory purposes. In practical applications, no space is required in the commands.
9.4.8.3 Examples of continuously write command 10H
Example 1: Set the VFD whose address is 01H to be forward running at the frequency of 10 Hz. Refer to the table of other function parameters, the address of "Communication-based control command" is 2000H, 0001H indicates forward running, and the address of "Communication-based value setting" is 2001H, as shown in the following figure. 10 Hz is 03E8H in the hexadecimal form.
Function
Address
Data description
R/W
2000H
R/W
0005H: Stop
0007H: Fault reset
2001H
R/W
2002H
In the actual operation, set P00.01 to 2 and P00.06 to 8.
If the operation is successful, the following response is returned:
Example 2: Set "ACC time" of the VFD whose address is 01H to 10s, and "DEC time" to 20s.
P00.11
ACC time 1
Setting   range of P00.11 and P00.12: 0.0–3600.0s
Model depended
P00.12
DEC time 1
Model depended
The address of P00.11 is 000B, 10s is 0064H in the hexadecimal form, and 20s is 00C8H in the hexadecimal form.
9.4.8.4 Modbus communication commissioning example
A PC is used as the host, an RS232-RS485 converter is used for signal conversion, and the PC serial port used by the converter is COM1 (an RS232 port). The upper computer commissioning software is the serial port commissioning assistant Commix, which can be downloaded from the Internet. Download a version that can automatically execute the CRC check function. The following figure shows the interface of Commix.
First, set the serial port to COM1. Then, set the baud rate consistently with P14.01. The data bits, check bits, and end bits must be set consistently with P14.02. If the RTU mode is selected, you need to select the hexadecimal form Input HEX. To set the software to automatically execute the CRC function, you need to select ModbusRTU, select CRC16 (MODBU SRTU), and set the start byte to 1. After the auto CRC check function is enabled, do not enter CRC information in commands. Otherwise, command errors may occur due to repeated CRC check.
The commissioning command to set the VFD whose address is 03H to be forward running is as follows:
Set the address (P14.00) of the VFD to 03.
Set "Channel of running commands" (P00.01) to "Communication", and set "Communication channel of running commands" (P00.02) to the Modbus communication channel.
Click Send. If the line configuration and settings are correct, a response transmitted by the VFD is received as follows: