You need to add a fuse to prevent overload.
You need to configure a manually manipulated molded case circuit breaker (MCCB) between the AC power supply and VFD. The breaker must be locked in the open state to facilitate installation and inspection. The capacity of the breaker needs to be 1.5 to 2 times the rated current of the VFD.
² According to the working principle and structure   of breakers, if the manufacturer's regulation is not followed, hot ionized   gases may escape from the breaker enclosure when a short-circuit occurs. To   ensure safe use, exercise extra caution when installing and placing the   breaker. Follow the manufacturer's instructions.
To ensure safety, you can configure an electromagnetic contactor on the input side to control the switch-on and switch-off of the main circuit power, so that the input power supply of the VFD can be effectively cut off when a system fault occurs.
Table D.2 AC 3PH 380V(-15%)–440V(+10%)
VFD model
Breaker    rated current (A)
Quick    fuse (A)
Contactor rated current (A)
GD350A-1R5G/2R2P-4
6/10
10/10
9/9
GD350A-2R2G/003P-4
10/20
10/20
9/18
GD350A-004G/5R5P-4
20/25
20/35
18/25
GD350A-5R5G/7R5P-4
25/32
35/40
25/32
GD350A-7R5G/011P-4
32/50
40/50
32/38
GD350A-011G/015P-4
50/63
50/60
38/50
GD350A-015G/018P-4
63/63
60/70
50/65
GD350A-018G/022P-4
63/80
70/90
65/80
GD350A-022G/030P-4
80/100
90/125
80/80
GD350A-030G/037P-4
100/125
125/125
80/98
GD350A-037G/045P-4
125/140
125/150
98/115
GD350A-045G/055P-4
140/180
150/200
115/150
GD350A-055G/075P-4
180/225
200/250
150/185
GD350A-075G-/090P4
225/250
250/300
185/225
GD350A-090G/110P-4
250/315
300/350
225/265
GD350A-110G/132P-4
315/400
350/400
265/330
GD350A-132G/160P-4
400/500
400/500
330/400
GD350A-160G/185P-4
500/500
500/600
400/400
GD350A-185G/200P-4
500/630
600/600
400/500
GD350A-200G/220P-4
630/630
600/700
500/500
GD350A-220G/250P-4
630/700
700/800
500/630
GD350A-250G/280P-4
700/800
800/1000
630/630
GD350A-280G/315P-4
800/1000
1000/1000
630/800
GD350A-315G/355P-4
1000/1000
1000/1000
800/800
GD350A-355G/400P-4
1000/1000
1000/1200
800/1000
GD350A-400G/450P-4
1000/1250
1200/1200
1000/1000
GD350A-450G/500P-4
1250/1250
1200/1400
1000/1000
GD350-500G-4
1250
1400
1000
Note: The accessory specifications described in the preceding table are ideal values. You can select accessories based on the actual market conditions, but try not to use those with lower values.