3.3.1 Main circuit connection diagram

image.png

Figure 3‑6 Main circuit connection diagram of 380V VFDs

Note:

  • The fuse, input reactor, input filter, output reactor, output filter are optional parts. Please refer to Appendix D and Appendix E for detailed information.

3.3.2 Main circuit terminals diagram

image.png

Figure 3‑7 Main circuit terminals diagram of VFDs of 380V (7.5–15kW)

image.png

Figure 3‑8 Main circuit terminals diagram of VFDs of 380V (18.5–30kW)

image.png

Figure 3‑9 Main circuit terminals diagram of VFDs of 380V (37–55kW)

Terminal

Description

R, S, T

Three-phase power input terminals

(+) , (-)

Anode and cathode of the DC bus

U, V, W

Three-phase AC output terminals

PE,

Grounding terminals

 

3.3.3 Main circuit terminal wiring

1.    Connect the ground line of input power cable to the ground terminal of VFD (PE) directly, and connect 3PH input cable to R, S and T and fasten up.

2.    Connect the ground line of motor cable to the ground terminal of the VFD, and connect the 3PH motor cable to U, V, W and fasten up.

3.    Connect the brake resistor which carries cables to the designated position.

4.    Fasten up all the cables on the outside of the VFD if allowed.

image.png

Figure 3‑10 Correct installation of the screw

3.3.4 Control circuit wiring and terminals

3.3.4.1 Control circuit wiring diagram of rectifier

image.png

Figure 3‑11 Control circuit wiring diagram of rectifier

3.3.4.2 Control circuit terminal of rectifier

image.png

Figure 3‑12 Rectifier control circuit terminal


Table 3‑1 Terminals in rectification control circuit

Type

Identifier

Name

Description


Input phase detection

R

Input phase R

Three-phase mains input terminals, detecting mains phases RS and ST

Detection voltage range: AC 0–690V

Note: Pay attention to the wiring sequence.


S

Input phase S


T

Input phase T


Output phase detection

U

Reserved



V


W


Power

+10V

10V reference power supply

10V reference power supply

Max. output current: 50mA

As the adjusting power supply of the external potentiometer

Potentiometer resistance: above 5 kΩ


+24V

24V power supply

To provide 24V±10% power supply externally, with the max. output current of 200mA

Generally serving as the power supply of digital input and output or the power supply of the external sensor


COM


Common terminal of 10V


GND


Common terminal of 24V


Analog input and output

AI1

Analog input 1

1. Input range: 0–10V or 0–20mA for AI1

2. Input impedance: 20kΩ for voltage input and 500Ω for current input

3. The input type (voltage or current) is set through the jumper.

4. Resolution: When 10V corresponds to 50Hz, the min. resolution is 5mV.

5. Deviation: ±1%, 25°C


AO1

Analog output 1

1. Output range: 0–10V or 0–20mA

2. The output type (voltage or current) is set through the jumper.

3. Resolution: 12 bits; accuracy: 1%

4. Deviation: ±1%, 25°C



Digital input and output

S1

Digital input 1

1. Internal impedance: 3.3kΩ
  2. Max. input frequency: 1kHz


S2

Digital input 2


S3

Digital input 3


S4

Digital input 4


S5

Digital input 5


S6

AC buffer contactor actuation feedback signal input


Communication

485+

RS485 communication

RS485 communication terminals, using the Modbus protocol


485-


Relay output

RO1A

Relay 1 NO contactor

1. Contactor capacity: 3A/AC250V, 1A/DC30V
  2. Not able to function as high-frequency digital output


RO1B

Relay 1 NC contactor


RO1C

Relay 1 common contactor


RO2A

Relay 2 NO contactor


RO2B

Relay 2 NC contactor


RO2C

Relay 2 common contactor


 

3.3.4.3 Converting control circuit wiring

image.png

Figure 3‑13 Converting control circuit wiring

3.3.4.4 Terminals in converting control circuit

image.png

Figure 3‑14 Terminals in converting control circuit


Table 3‑2 Terminals in converting control circuit

Type

Identifier

Name

Description

Power

+10V

+10V reference power supply

GND as the reference

Setpoint 10.5V

Max. output current: 100mA

With output short-circuit protection

Accuracy: 1%

+24V

24V power supply

COM as the reference

With output short-circuit protection

Max. current provided externally: 100mA

Accuracy: 10%

Generally serving as the digital input and output working power supply or the power supply of the external sensor

PW

External power

COM as the reference, providing the working power for digital input and output from the external to the internal

Input voltage range: DC12–30V

Analog input

AI1

Analog input 1

GND as the reference

1. Input range: 0–10V or 0–20mA

2. The input type (voltage or current) is set through the jumper J3.

3. Resolution: 12 bits

4. Deviation: ±1%, 25°C

AI2

Analog input 2

GND as the reference

1. Input range: 0–10V or 0–20mA

2. The input type (voltage or current) is set through the jumper J4.

3. Resolution: 12 bits

4. Deviation: ±1%, 25°C

AI3

Analog input 3

GND as the reference

1. Input range: -10–10V

3. The voltage input is selected through the function code.

4. Resolution: 12 bits

5. Deviation:±1%, 25°C

Analog output

AO1

Analog output 1

GND as the reference

1. Output range: -10V–10V or -20mA–20mA

2. The input type (voltage or current) is set through the jumpers J1 and J2.

3. Deviation:±1%, 25°C

AO2

Analog output 2

Digital input and output

S1

Digital input 1

COM as the reference

1. Internal impedance: 3.3kΩ

2. Acceptable input voltage: 12–30V

3. Dual-directional input terminals, supporting NPN and PNP

4. Max input frequency: 1kHz

5: For HDI, max. input frequency: 50kHz

S2

Digital input 2

S3

Digital input 3

S4

Digital input 4

S5

Digital input 5

S6

Digital input 6

S7

Digital input 7

S8

Digital input 8

HDI

High speed pulse input

Y1

Open collector output

COM as the reference

1. Contact capacity: 200mA/30V

2. Output frequency range: 0–1kHz, OC output

3. Input power: DC12–30V

HDO

Open collector output or open collector high speed pulse output

COM as the reference

1. Output voltage amplitude: 24V

2. Output frequency: 50kHz

Relay output

RO1A

Relay 1 NO contactor

1. Contactor capacity: AC250V/3A, DC30V/1A

2. Not able to function as high-frequency digital output

RO1B

Relay 1 NC contactor

RO1C

Relay 1 common contactor

RO2A

Relay 2 NO contactor

RO2B

Relay 2 NC contactor

RO2C

Relay 2 common contactor

Communication

485+

485-

RS485 communication

RS485 communication terminals, using the Modbus protocol

Others

PE

Shield ground

Used for grounding the shield layer in terminal wiring, such as the shield layers of the analog signal cable, RS485 communication cable, and motor cable

COM

Common terminal

Common terminal of +24V

CME

Common terminal

Common terminal of open collector output

 

3.3.5 Input /Output signal connection figure

Use U-shaped short-circuit connectors to set NPN mode or PNP mode and the internal or external power supply. The default setting is NPN internal mode.

image.png

Figure 3‑15 U-shaped short-circuit positions

If the signal is from NPN transistor, set the U-shaped short-circuit connector between +24V and PW as follows according to the used power supply.

image.png

Figure 3‑16 NPN modes

If the signal is from PNP transistor, set the U-shaped short-circuit connector as follows according to the used power supply.

image.png

Figure 3‑17 PNP modes


上一章节 下一章节