When fault occurred, process the fault as shown below.
1.    When VFD fault occurred, confirm whether keypad display is improper? If yes, contact INVT;
2.    If keypad works properly, check the function codes in P07 group to confirm the corresponding fault record parameters, and determine the real state when current fault occurred through parameters;
3.    Check the table below to see whether corresponding exception states exist based on the corresponding corrective measures;
4.    Rule out the faults or ask for help from professionals;
5.    After confirming faults are removed, reset the fault and start running.
7.5.1 Details of faults and solutions
Fault code
Fault type
Possible cause
Corrective measures
OUt1
Inverter unit Phase-U protection
Acceleration is too fast;
IGBT module is damaged;
Misacts caused by interference; drive wires are poorly connected   ;
To-ground short circuit occurs
Increase acceleration time;
Replace the power unit;
Check drive wires;
Check whether there is strong interference surrounds the   peripheral equipment
OUt2
Inverter unit Phase-V protection
OUt3
Inverter unit Phase-W protection
OV1
Over-voltage during acceleration
Deceleration time is too short;
Exception occurred to input voltage;
Large energy feedback;
Lack of brake units;
Dynamic brake is not enabled, and the deceleration   time is too short.
Check input power;
Check whether load deceleration time is too short;   or the motor starts during rotating;
Install dynamic brake units;
Check the setup of related function codes
OV2
Over-voltage during deceleration
OV3
Over-voltage during constant speed running
OC1
Over-current during acceleration
Grid voltage is too low;
VFD power is too small;
Load transient or exception occurred;
To-ground short circuit or output phase loss occur;
Strong external interference sources;
Overvoltage stall protection is not enabled
Increase acceleration /deceleration   time;
  Check input power;
  Select the VFD with larger power;
Check if the load is short circuited   (to-ground short circuit or line-to-line short circuit) or the rotation is   not smooth;
Check the output wiring;
Check if there is strong interference;
Check the setup of related function   codes.
OC2
Over-current during deceleration
OC3
Over-current during constant speed running
UV
Bus undervoltage fault
Check grid input power;
OL1
Motor overload
Rated motor current is set improperly;
Motor stall or load jumps violently
Check   grid voltage;
Reset   rated motor current;
Check the   load and adjust torque boost
OL2
VFD overload
The motor   in rotating is restarted;
Load is too   large;
Power is   too small;
Avoid   restart after stop;
Check   grid voltage;
Select   proper motor
SPI
Phase loss on input side
Phase loss or violent fluctuation occurred   to R, S and T input
Check the input power;
Check installation wiring
SPO
Phase loss on output side
Phase loss occurred to U, V, W output (or   the three phases of motor is asymmetrical)
Check the motor and cable
OH1
Overheat of rectifier module
Air duct is blocked or fan is damaged;
Ambient temperature is too high;
Long-time overload running
Ventilate   the air duct or replace the fan;
Lower the   ambient temperature
OH2
Overheat of inverter module
EF
External fault
SI external fault input terminal acts
Check external device input
CE
485 communication fault
Baud rate is set improperly;
Communication   line fault;
Communication   address error;
Communication   suffers from strong interference
Set   proper baud rate;
Check the   wiring of communication interfaces;
Set   proper communication address;
Replace   or change the wiring to enhance anti-interference capacity
ItE
Current detection fault
Poor contact of the connector of control   board;
Hall component is damaged;
Exception   occurred to amplification circuit
Check the   connector and re-plug;
Replace   the hall component;
Replace   the main control board
tE
Motor autotuning fault
Motor capacity does not match with the VFD   capacity, this fault may occur easily if the difference between them is   exceeds five power classes;
Motor parameter is set improperly;
The parameters gained from autotuning   deviate sharply from the standard parameters;
Autotuning   timeout
Change   the VFD model, or adopt V/F mode for control;
Set   proper motor type and nameplate parameters;
Empty the   motor load and carry out autotuning again;
Check   motor wiring and parameter setup;
Check   whether upper limit frequency is larger than 2/3 of the rated frequency
EEP
EEPROM fault
R/W error occurred to the control   parameters;
EEPROM is   damaged
Press STOP/RST   to reset;
PIDE
PID feedback offline fault
PID feedback offline;
PID feedback   source disappears;
Check PID feedback signal wires;
Check PID   feedback source
bCE
Brake unit fault
Brake circuit fault or brake tube is   damaged;
The   resistance of external brake resistor is too small
Check the brake unit, replace with new   brake tubes;
Increase brake resistance
END
Running time is up
The actual running time of the VFD is larger than   the set running time
Ask help from the supplier, adjust the set running   time
OL3
Electronic overload fault
The VFD releases overload pre-alarm based on the   set value
Check the load and overload pre-alarm threshold
PCE
Keypad communication fault
The keypad wire is poorly contacted or   disconnected;
The keypad wire is too long and suffers strong   interference;
Circuit fault occurred to the keypad or   communication part of the main board
Check the keypad wires to confirm whether fault   exists;
Check the surroundings to rule out interference   source;
Replace the hardware and ask for maintenance   service
UPE
Parameter upload error
Replace the hardware and ask for maintenance   service;
DNE
Parameter download error
Data storage error occurred to the keypad
Re-backup keypad data
ETH1
To-ground short circuit fault 1
VFD   output is short connected to the ground;
Current   detection circuit is faulty;
Actual   motor power setup deviates sharply from the VFD power
Check   whether motor wiring is proper;
Replace the   main control board;
Reset the   motor parameters properly
ETH2
VFD output   is short connected to ground;
dEu
Speed deviation fault
Load is   too heavy, or stall occurred
Check the   load to ensure it is proper, increase the detection time;
Check   whether control parameters are set properly
STo
Maladjustment fault
Control   parameters of synchronous motor is set improperly;
The   parameter gained from autotuning is inaccurate;
The VFD   is not connected to motor
Check   whether load is proper;
Check   whether control parameters are set correctly;
Increase   maladjustment detection time
LL
Electronic underload fault
The VFD performs underload pre-alarm based on the   set value
ENC1O
Encoder offline fault
Encoder line sequence is wrong, or signal wires are   poorly connected
Check the encoder wiring
ENC1D
Encoder reversal fault
The encoder speed signal is contrary to the motor   running direction
Reset encoder direction
ENC1Z
Encoder Z pulse offline fault
Z signal wires are disconnected
Check the wiring of Z signal
OT
Motor over-temperature fault
Motor   over-temperature input terminal is valid;
Exception   occurred to t temperature detection Exception occurred to resistor;
Long-time   overload running or exception occurred
Check the   wiring of motor over-temperature input terminal (terminal function 57);
Check   whether temperature sensor is proper;
Check the   motor and perform maintenance on the motor
STO
Safe torque off
Safe   torque off function is enabled by external forces
STL1
Exception occurred to safe circuit of channel   H1
The   wiring of STO is improper;
Fault   occurred to external switch of STO;
Hardware   fault occurred to safety circuit of channel H1
Check   whether terminal wiring of STO is proper and firm enough;
Check   whether external switch of STO can work properly;
Replace   the control board
STL2
Exception occurred to channel H2 safe   circuit
Hardware   fault occurred to safety circuit of channel H2
STL3
Exception occurred to channel H1 and   channel H2
Hardware   fault occurred to STO circuit
CrCE
Safety code FLASH CRC check fault
Control   board is faulty
E-Err
Repetitive extension card type
The two   inserted extension cards are of the same type
Users   should not insert two cards with the same type; check the type of extension   card, and remove one card after power down
ENCUV
Encoder UVW loss fault
No   electric level variation occurred to UVW signal
Check the   wiring of UVW;
Encoder   is damaged
F1-Er
Failed to identify the extension card in   card slot 1
There is   data transmission in interfaces of card slot 1, however, it cannot read the   card type
Confirm   whether the extension card inserted can be supported;
Stabilize   the extension card interfaces after power down, and confirm whether fault   still occurs at next power-on;
Check   whether the insertion port is damaged, if yes, replace the insertion port   after power down
F2-Er
Failed to identify the extension card in   card slot 2
There is   data transmission in interfaces of card slot 2, however, it cannot read the   card type
F3-Er
Failed to identify the the extension card   in card slot 3
There is   data transmission in  interfaces of   card slot 3, however, it cannot read the card type
C1-Er
Communication timeout occurred to the extension   card in card slot 1
There is   no data transmission in interfaces of card slot 1
C2-Er
Communication timeout occurred to the extension   card in card slot 2
There is   no data transmission in interfaces of card slot 2
C3-Er
Communication timeout occurred to the extension   card in card slot 3
There is   no data transmission in interfaces of card slot 3
E-DP
PROFIBUS card communication timeout fault
There is   no data transmission between the communication card and the host computer (or   PLC)
Check   whether the communication card wiring is loose or dropped
E-NET
Ethernet card communication timeout fault
E-CAN
CANopen card communication timeout fault
E-PN
PROFINET card communication timeout fault
E-CAT
EtherCAT card communication timeout fault
E-BAC
BACNet card communication timeout fault
E-DEV
DeviceNet card communication timeout fault
ESCAN
Can master/slave communication card communication   timeout fault
There is   no data transmission between the CAN master and slave communication cards
S-Err
Master-slave synchronous CAN slave fault
Fault   occurred to one of the CAN slave VFDs
Detect   the CAN slave VFD and analyze the corresponding fault cause of the VFD
7.5.2 Other state
Displayed    code
State    type
Possible    cause
Solution
PoFF
System power failure
The   system is powered off or the bus voltage is too low.
Check the   grid conditions.