Check before powering on
Please check according to the installation list in Chapter 2.
Original powering operation
Check to ensure there is no mistake in wiring and power supply, switch on the air switch of the AC power supply on the input side of the VFD to power on the VFD. 8.8.8.8.8. will be displayed on the keypad, and the contactor closes normally. When the character on the nixie tubs changes to the set frequency, the VFD has finished the initialization and it is in the stand-by state.
Below diagram shows the first operation: (take motor 1 as the example)
Note: If fault occurs, please do as the "Fault Tracking". Estimate the fault reason and settle the issue.
Besides P00.01 and P00.02, terminal command setting can also be used to set running command channel.
Current running    command channel
P00.01
Multi-function    terminal 36
Switch to keypad
Multi-function    terminal 37
Switch    to terminal
Multi-function    terminal 38
Switch    to communication
Keypad running command channel
Terminal running command channel
Communication running command channel
Note: "/" means the multi-function terminal is invalid on the current given channel.
Relative parameters table:
Function code
Default value
P00.00
Speed control mode
0: Sensorless vector control mode 0 (apply to AM and   SM)
1: Sensorless vector control mode 1 (applying to AM)
2: SVPWM   control
P00.01
Run command channel
0: Keypad   running command
1: Terminal   running command channel ("LOCAL/REMOT" flickering)
2: Communication   running command channel ("LOCAL/REMOT" on);
P00.02
Communication running commands
0: Modbus communication channel
1: PROFIBUS\CANopen communication channel
2: Ethernet communication channel
3: Reserved
P00.18
Function
restore parameter
0: No operation
1: Restore the default value
2: Cancel   the fault record
P00.15
Motor parameter autotuning
0: No operation
1: Rotation autotuning
2: Static autotuning 1 (autotune totally)
3: Static   autotuning 2 (autotune part parameters)
P02.00
Motor type 1
0: Asynchronous motor
1: Synchronous   motor
P02.01
Rated power of asynchronous motor 1
0.1–3000.0   kW
Depend on model
P02.02
Rated frequency of asynchronous motor 1
0.01 Hz–P00.03   (max. output frequency)
50.00 Hz
P02.03
Rated speed of asynchronous motor 1
1–36000 rpm
Depend on model
P02.04
Rated voltage of asynchronous motor 1
0–1200 V
Depend on model
P02.05
Rated current of asynchronous motor 1
0.8–6000.0   A
Depend on model
P02.15
Rated power of synchronous motor 1
0.1–3000.0   kW
Depend on model
P02.16
Rated frequency of synchronous motor 1
50.00 Hz
P02.17
Number of poles pairs for synchronous motor   1
1–128
P02.18
Rated voltage of synchronous motor 1
0–1200 V
Depend on model
P02.19
Rated current of synchronous motor 1
0.8–6000.0   A
Depend on model
P05.01–P05.09
Multi-function digital input terminals
 (S1–S8,HDI)   function selection
36: Shift   the command to keypad
37: Shift   the command to terminals
38: Shift   the command to communication
P07.01
Parameter copy
The function code determines the manner of   parameters copy.
0: No operation
1: Upload the local function parameter to   the keypad
2: Download the keypad function parameter   to local address (including the motor parameters)
3: Download the keypad function parameter   to local address (excluding the motor parameter of P02 and P12 group)
4: Download the keypad function parameters   to local address (only for the motor parameter of P02 and P12 group)
P07.02
QUICK/JOG function selection
0: No function
1: Jogging. Press QUICK/JOG to begin the   jogging running.
2: Shift the display state by the shifting   key. Press QUICK/JOG to shift the displayed   function code from right to left.
3: Shift between forward rotations and   reverse rotations. Press QUICK/JOG to shift the   direction of the frequency commands. This function is only valid in the   keypad commands channels.
4: Clear UP/DOWN settings. Press QUICK/JOG   to clear the set value of UP/DOWN.
5: Coast to stop. Press QUICK/JOG   to coast to stop.
6: Shift the given manner of running   commands. Press QUICK/JOG to shift the given manner of   running commands.
7: Quick commission mode (commission   according to the non-factory parameter)