Do as the following after the VFD fault:
1. Check to ensure there is nothing wrong with the keypad. If not, contact the local INVT office.
2. If there is nothing wrong, please check P07 and ensure the corresponding recorded fault parameters to confirm the real state when the current fault occurs by all parameters.
3. See the following table for detailed solution and check the corresponding abnormal state.
4. Eliminate the fault and ask for relative help.
5. Check to eliminate the fault and carry out fault reset to run the VFD.
8.5.1 VFD faults and solutions
Code
Fault
Cause
Solution
OUt1
Inverter unit U phase protection
lThe   acceleration is too fast
lThere is   damage to the internal to IGBT of the phase
lMisoperation   is caused by interference.
lThe   connection of the driving wires is not good
lShort-to-ground   occurs.
l Increase acceleration   time
l Change   the power unit
l Check the   driving wires
l Check if   there is strong interference to the external equipment
OUt2
Inverter unit V phase protection
OUt3
Inverter unit W phase protection
OV1
ACC overvoltage
lThe input   voltage is abnormal
lThere is   large energy feedback
lNo brake   components
lBrake   energy is not open
lCheck the   input power
lCheck if   the DEC time of the load is too short, or the motor is started when it is   rotating.
lInstall a   dynamic brake components
lCheck the   setting of relative function codes
OV2
DEC overvoltage
OV3
Constant-speed overvoltage
OC1
ACC overcurrent
lThe   acceleration or deceleration is too fast
lThe   voltage of the grid is too low
lThe power   of VFD is too low
lThe load   transients or is abnormal
lThe   grounding is short circuited or the output is phase loss
lThere is   strong external interference
lThe   overvoltage stall protection is not open
lIncrease   the ACC time
lSelect   the VFD with a larger power
lCheck if   the load is short circuited (the grounding short circuited or the wire short   circuited) or the rotation is not smooth
lCheck the   output configuration.
lCheck if   there is strong interference
OC2
DEC overcurrent
OC3
Constant-speed overcurrent
UV
Bus undervoltage
lCheck the   input power of the grid;
OL1
Motor overload
lThe rated   current of the motor is not correctly set
lThe motor   stall or load transients is too strong
lCheck the   power of the grid
lReset the   rated current of the motor
lCheck the   load and adjust the torque lift
OL2
VFD overload
lRestart   the rotating motor
lThe   voltage of the grid is too low.
lThe load   is too heavy.
lThe motor   power is too small.
lAvoid the   restarting after stopping.
lSelect a VFD   with bigger power.
lSelect a   proper motor.
SPI
Input side phase loss
lPhase   loss or fluctuation of input R,S,T
lCheck   input power
lCheck   installation distribution
SPO
Output side phase loss
lU, V,W   phase loss input (or serious asymmetrical three phase of the load)
lCheck the   output distribution
lCheck the motor and cable
OH1
Rectifying module overheated
lAir duct   jam or fan damage
lAmbient   temperature is too high.
lThe time   of overload running is too long.
lDredge   the vent duct or replace the fan
lLower the   ambient temperature
OH2
Inverter module overheated
EF
External fault
lSI external   fault input terminals act
lCheck the   external device input
CE
485 communication fault
lThe baud   rate setting is incorrect.
lFault   occurs to the communication wiring.
lCommunication   address is wrong.
lThere is   strong interference to the communication.
lSet   proper baud rate
lCheck the   communication connection distribution
lSet   proper communication address.
lChange or   replace the connection distribution or improve the anti-interference   capability.
ItE
Current-detecting fault
lThe   connection of the control board is not good
lHall components   are broken
lThe   modifying circuit is abnormal.
lCheck the   connector and re-plug
lChange   the Hall
lChange   the main control panel
tE
Motor-autotuning fault
lThe motor   capacity does not comply with VFD capability
lThe rated   parameter of the motor does not set correctly.
lThe   offset between the parameters from autotune and the standard parameter is   huge
lAutotune   overtime
lChange   the VFD mode
lSet the rated   parameter according to the motor name plate
lEmpty the   motor load and re-identify
lCheck the   motor connection and set the parameter.
lCheck if   the upper limit frequency is above 2/3 of the rated frequency.
EEP
EEPROM operation fault
lError of   controlling the write and read of the parameters
lDamage to   EEPROM
lPress STOP/RST   to reset
PIDE
PID feedback outline fault
lPID   feedback offline
lPID   feedback source disappear
lCheck the   PID feedback signal
lCheck the   PID feedback source
bCE
Brake unit fault
lBrake   circuit fault or damage to the brake pipes
lExternal brake   resistor is insufficient
lCheck the   brake unit, and change new brake pipe
lIncrease   the brake resistor
END
Running time arrival
lThe   actual running time of the VFD is above the internal setting running time.
lAsk for   the supplier and adjust the setting running time.
OL3
Electrical overload
lVFD   will report overload pre-alarm based on the set value.
lCheck the   load and the overload pre-alarm threshold.
PCE
Keypad communication fault
lThe   connection of the keypad wires is not good or broken.
lThe   keypad wire is too long and affected by strong interference.
lThere is   circuit fault on the communication of the keypad and main board.
lCheck the   keypad wires and ensure whether there is mistake.
lCheck the   environment and avoid the interference source.
lChange   the hardware and ask for service.
UPE
Parameters uploading fault
lChange   hardware and ask for service.
DNE
Parameters downloading fault
lThere is   mistake on the data storage of the keypad.
lRepack-up   the data in the keypad.
E-DP
PROFIBUS communication fault
lCorresponding   resistor is not dialed
lThe files   of main stop GSD does not set sound
lThe   peripheral interference is too large.
lCheck   related setting
lCheck the   surrounding environment, and eliminate interference effects.
E-NET
Ethernet communication fault
lEthernet   address is set improperly.
lEthernet   communication is wrong
lCheck the   relative setting.
lCheck the   communication method selection.
E-CAN
CANopen communication fault
lThe   connection is not sound
lThe   communication baud rate is not matched
lCheck the   connection
lDraw out   the matching resistor
lSet the   same baud rate
ETH1
Grounding shortcut fault 1
lThe   output of the VFD is short circuited with the ground.
lThere is   fault in the current detection circuit.
lThe   actual motor power sharply differs from the VFD power.
lCheck if   the connection of the motor is normal or not
lChange   the hall
lSet motor   parameters correctly.
ETH2
Grounding shortcut fault 2
lChange   the Hall
dEu
Speed deviation fault
lThe load   is too heavy or stalled.
lCheck the   load and ensure it is normal. Increase the detection time.
lCheck   whether the control parameters are normal.
STo
Maladjustment fault
lThe   control parameters of the synchronous motors not set properly.
lThe   autotune parameter is not right.
lThe VFD   is not connected to the motor.
lCheck   whether the control parameter is set properly or not.
lIncrease   the maladjustment detection time.
LL
Electronic underload fault
lThe VFD   will report the underload pre-alarm according to the set value.
lCheck the   load and the underload pre-alarm threshold.
ENC1O
Encoder offline fault
lEncoder   line sequence error, or signal wire is connected improperly
lCheck   encoder wiring
ENC1D
Encoder reverse fault
lEncoder   speed signal is contrary to running direction of the motor
lReset   encoder direction
ENC1Z
Encoder pulse Z offline
lZ signal   wire is disconnected
lCheck Z   signal wiring
OT
Motor over-temperature fault
lMotor   overtemperature input terminal is valid
lTemperature   detection resistor is abnormal
lMotor   runs in overload condition in long time or it is abnormal
lCheck the   wiring of motor overtemperature input terminal (terminal function 57)
lCheck whether   temperature sensor functions normally
lCheck and   maintain the motor.
8.5.2 Other states
Code
State    type
Possible    cause
Solution
PoFF
System power off
System   power off or bus voltage is too low
Check   grid environment
Communication between keypad and main   control plate failed
Keypad is   connected improperly
Check the   installation of keypad