4.3.1 Main circuit connection diagram
4.3.1.1 Main circuit connection diagram of VFDs of AC 3PH 380V (-15%)–440V (+10%)
Figure 4-7 Main circuit connection diagram of 380V VFDs
The fuse, DC reactor, braking unit, braking resistor, input reactor, input filter, output reactor, output filter are optional parts. Please refer to Peripheral Optional Parts for detailed information.
A1 and A2 are optional parts.
P1 and (+) are short circuited in factory for the VFDs of 380V (≥37kW), if need to connect with the DC rector, please remove the contact tag between P1 and (+).
Before connecting the braking resistor cable, remove the yellow labels of PB, (+), and (-) from the terminal blocks. Otherwise, poor connection may occur.
4.3.1.2 Main circuit connection diagram of VFDs of 3PH 380V (-10%)–550V (+10%)
Figure 4-8 Connection diagram of main circuit for the VFDs of 500V
P1 and (+) are short circuited in factory for the VFDs of 500V (≥22kW), if need to connect with the DC rector, please remove the contact tag between P1 and (+).
4.3.1.3 Main circuit connection diagram of VFDs of AC 3PH 520V (-15%)–690V (+10%)
Figure 4-9 Connection diagram of main circuit for the VFDs of 660V
A1 and A2 are standard parts.
P1 and (+) are short circuited in factory, if it needs to connect with the DC rector, please remove the contact tag between P1 and (+).
4.3.2 Main circuit terminals diagram
Figure 4-10 Main circuit terminals diagram of VFDs of 380V (1.5–2.2kW)
Figure 4-11 Main circuit terminals diagram of VFDs of 380V (4–5.5kW)
Figure 4-12 Main circuit terminals diagram of VFDs of 380V (7.5–11kW) and 500V (4–18.5kW)
Figure 4-13 Main circuit terminals diagram of VFDs of 380V (15–18kW)
Figure 4-14 Main circuit terminals diagram of VFDs of 380V (22–30kW)
Figure 4-15 Main circuit terminals diagram of VFDs of 380V (37–55kW), 500V (22–55kW), and 660V (22–45kW)
Figure 4-16 Main circuit terminals diagram of VFDs of 380V (75–110kW), 500V (75kW), and 660V (55–132kW)
Figure 4-17 Main circuit terminals diagram of VFDs of 380V (132–200kW) and 660V (160–220kW)
Figure 4-18 Main circuit terminals diagram of VFDs of 380V (220–315kW) and 660V (250–350kW)
Figure 4-19 Main circuit terminals diagram of VFDs of 380V (350–500kW) and 660V (400–630kW)
Terminal
Terminal    name
Function    description
380V (≤30kW)
380V (≥37kW)
500V (≤18.5kW)
500V (≥22kW)
660V
R,S,T
Power input of the main circuit
3-phase AC input terminals which are   generally connected with the power supply.
U,V,W
VFD output
3-phase AC output terminals which are   generally connected with the motor.
P1
DC reactor terminal 1
P1 and (+) are connected with the terminals   of the DC reactor.
(+) and (-) are connected with the   terminals of the braking unit.
PB and (+) are connected with the terminals   of the braking resistor.
Braking resistor 1
DC reactor terminal 2, braking unit   terminal 1
Braking unit terminal 2
PB
Braking
resistor 2
PE
380V/500V/660V: the grounding resistor is   less than 10 Ohm
Protective grounding terminals. Every   machine is provided with 2 PE terminals as the standard configuration. These   terminals must be grounded with proper techniques.
A1 and   A2
Control power supply terminal
Optional parts for 380V VFDs, standard   parts for 660V VFDs (connected with external 220V control power supply),   enabling a VFD to use an auxiliary power supply when no power is applied in   the input main circuit, thus facilitating the commissioning of the VFD and   improving safety during the commissioning.
Do not use an asymmetrically constructed motor cable. If there is a symmetrically constructed grounding conductor in the motor cable in addition to the conductive shield, connect the grounding conductor to the grounding terminal at the VFD and motor ends.
Braking resistor, braking unit and DC reactor are optional parts.
Route the motor cable, input power cable and control cables separately.
If the terminal description is "/", the machine does not provide the terminal as the external terminal.
4.3.3 Main circuit terminal wiring
1.    Connect the ground line of input power cable to the ground terminal of VFD (PE) directly, and connect 3PH input cable to R, S and T and fasten up.
2.    Connect the ground line of motor cable to the ground terminal of the VFD, and connect the 3PH motor cable to U, V, W and fasten up.
3.    Connect the brake resistor which carries cables to the designated position.
4.    Fasten up all the cables on the outside of the VFD if allowed.
Figure 4-20 Correct installation of the screw
 4.3.4 Control circuit wiring diagram
Figure 4-21 Control circuit wiring
4.3.5  Control circuit terminal diagram
Figure 4-22 Control circuit terminals
Terminal name
Description
+10V
Local power supply +10 V
AI1
1. Input range: AI1/AI2 voltage and current can be chosen: 0–10   V/0–20mA; AI1 can be shifted by J3 while AI2 can be shifted by J4; AI3: -10   V–+10 V
2. Input impedance: voltage input: 20kΩ; current input: 500Ω
3. Resolution: the minimum one is 5m V when 10 V corresponds to   50 Hz
4. Deviation ±1%, 25°C
AI2
AI3
GND
+10 V reference null potential
AO1
1. Output range: 0–10 V or 0–20mA; The voltage or the current   output is depended on the jumper. AO1 is switched by J1 and AO2 is switched   by J2
2. Deviation±1%, 25°C
AO2
Terminal name
Description
RO1A
RO1 relay output; RO1A is NO, RO1B is NC,   RO1C is common port
Contact capacity: 3A/AC250V, 1A/DC30V
RO1B
RO1C
RO2A
RO2 relay output; RO2A is NO, RO2B is NC, RO2C is   common port
RO2B
RO2C
Terminal name
Description
HDO
1. Switch   capacity: 200mA/30V;
2. Range   of output frequency: 0–50kHz
COM
Common   port of +24V
CME
Common   port of open collector output
Y
2. Range   of output frequency: 0–1kHz
485+
For 485   communication port, 485 differential signal port and standard 485   communication interfaces, use twisted pairs or shielded cables.
485-
Terminal name
Description
PE
Grounding   terminal
PW
Provide   input digital working power from external to internal;
Voltage   range: 12–30V.
24V
The VFD provides user power; the maximum output current   is 200mA
COM
Common port of +24V
S1
Digital input 1
1. Internal   impedance: 3.3kΩ
2. Accept   12–30V voltage input
3. This   terminal is bi-directional input terminal and supports NPN/PNP connection   modes
4. Max.   input frequency: 1kHz
5. All   are programmable digital input terminals, and users can set the terminal   function via function codes
S2
Digital input 2
S3
Digital input 3
S4
Digital input 4
S5
Digital input 5
S6
Digital input 6
S7
Digital input 7
S8
Digital input 8
HDI
Besides   S1–S8 functions, it can also act as high frequency pulse input channel
Max.   input frequency: 50kHz
4.3.6 Input /Output signal connection figure
Use U-shaped short-circuit connectors to set NPN mode or PNP mode and the internal or external power supply. The default setting is NPN internal mode.
Figure 4-23 U-shaped short-circuit positions
If the signal is from NPN transistor, set the U-shaped short-circuit connector between +24V and PW as follows according to the used power supply.
Figure 4-24 NPN modes
If the signal is from PNP transistor, set the U-shaped short-circuit connector as follows according to the used power supply.
Figure 4-25 PNP modes