Goodrive300 series VFDs have 2 relay output terminals, 1 open collector output terminal Y, and 1 high-speed pulse output terminal (HDO) in the standard configuration. All functions of the digital output terminals are programmable by using function codes, where the HDO can be set to high-speed pulse output or switch output through function codes.
The following table is the option of the four function parameters and selecting the repeated output terminal function is allowed.
Set value
Function
Instructions
Invalid
The output terminal has no function.
Running
Output ON signal when the VFD is running and there   is frequency output.
Forward running
Output ON signal when the VFD is running forward   and there is frequency output.
3
Reverse running
Output ON signal when the VFD is running reverse   and there is frequency output.
4
Jogging
Output ON signal when the VFD is jogging and there   is frequency output.
5
VFD fault
Output ON signal when the VFD is in fault
6
FDT1
Please refer to P08.32 and P08.33 for detailed   information.
7
FDT2
Please refer to P08.34 and P08.35 for detailed   information.
8
Frequency arrival
Please refer to P08.36 for detailed information.
9
Zero-speed   running
Output ON signal when the output frequency and   given frequency of the VFD is 0 at the same time.
10
Upper-limit   frequency arrival
Output ON signal when the running frequency of the   VFD is the upper limit frequency.
11
Output ON signal when the running frequency of the   VFD is the lower limit frequency.
12
Ready
When the   main circuit and the control circuit is established and the protection   function of the VFD is not active. The VFD is in the running state and it   will output ON signal.
13
Pre-exciting
Output ON   signal when the VFD is in the pre-exciting state.
14
Overload   pre-alarm
Output ON signal if the VFD is beyond the   pre-alarm point. Refer to P11.08–P11.10 for the detailed instruction.
15
Underload   pre-alarm
Output ON   signal if the VFD is beyond the pre-alarm point. Refer to P11.11–P11.12 for   the detailed instruction.
16
Simple PLC stage completion
Output signal if the simple PLC stage is   completed.
17
 Simple PLC cycle completion
Output signal if the simple PLC cycle is   completed.
18
Set counting   arrival
Output ON   signal if the detected counting exceeds the set value of P08.25.
19
Fixed counting   arrival
Output ON   signal if the detected counting exceeds the set value of P08.26.
20
External fault   valid
Output ON   signal if external fault occurs.
21
Length arrival
Output ON   signal if the actual detected length exceeds the set length by P08.19.
22
Running time   arrival
Output ON   signal if the accumulative running time of the VFD exceeds the setting time   by P08.27.
23
Modbus   communication virtual terminal output
Output corresponding signal according to the   setting value of Modbus. Output ON signal if the setting value is 1   and output OFF signal if the setting value is 0.
24
POROFIBUS   communication virtual terminal output
Output a corresponding signal according to the set   value of PROFIBUS/CANOPEN. Output the signal of ON if the set value is   1 and output the signal of OFF if the set value is 0.
25
Ethernet   communication
Virtual terminal   output
Output a corresponding signal according to the set   value of Ethernet. Output the signal of ON if the set value is 1 and   output the signal of OFF if the set value is 0.
26
DC bus voltage establishment   finished
The output is vlaid when the bus voltage reaches   the undervoltage point of the inverter.
27–30
Reserved
Related parameters
Function code
Default value
P06.00
HDO output
0: Open collector high-speed pulse output
1: Open collector output
P06.01
Y output
0: Invalid
1: In operation
2: Forward rotation operation
3: Reverse rotation operation
4: Jogging operation
5: The VFD fault
6: Frequency degree test FDT1
7: Frequency degree test FDT2
8: Frequency arrival
9: Zero speed running
10: Upper limit frequency arrival
11: Lower limit frequency arrival
12: Ready for operation
13: Pre-magnetizing
14: Overload pre-alarm
15: Underload pre-alarm
16: Completion of simple PLC stage
17: Completion of simple PLC cycle
18: Set count value reached
19: Specified count value reached
20: External fault valid
21: Length arrival
22: Running time arrival
23: Modbus communication virtual terminals   output
24: PROFIBUS/CANopen communication virtual terminals output
25: Ethernet communication virtual   terminals output
26:   Voltage establishment finished
27–30:   Reserved
P06.02
HDO output
P06.03
Relay RO1 output
P06.04
Relay RO2 output
5
P06.05
Polarity of output terminals
0x00–0x0F
0x00
P06.06
Y switch-on delay time
0.000–50.000s
0.000s
P06.07
Y switch-off delay time
0.000–50.000s
0.000s
P06.08
HDO switch-on delay time
0.000–50.000s
(valid only when P06.00=1)
0.000s
P06.09
HDO switch-off delay time
0.000–50.000s
0.000s
P06.10
RO1 switch-on delay time
0.000–50.000s
0.000s
P06.11
RO1 switch-off delay time
0.000–50.000s
0.000s
P06.12
RO2 switch-on delay time
0.000–50.000s
0.000s
P06.13
RO2 switch-off delay time
0.000–50.000s
0.000s
P07.40
Output terminals state at current fault
P17.13
Digital output terminals state
