Function    code
Default    value
Modify
P02.00
Motor
 type
0: Asynchronous   motor
1: Synchronous motor
Note: Switch the current motor by the switching   channel of P08.31.
P02.01
Rated
power
of
asynch-
ronous
motor
0.1–
3000.0kW
Set the parameters   of the controlled AM.
In order to ensure   control performance, set the value of P02.01–P02.05 based on the nameplate   parameters.
Goodrive35 series VFD   provides parameter autotuning function. The accurate parameter autotuning   requires proper parameter setup.
In order to ensure   control performance, configure the motor based on the motor which matches   with the VFD. If the gap between motor power and the matched motor is too   large, the control performance of the VFD will be deteriorated greatly.
Note: P02.02–P02.10   can be initialized by resetting rated motor power P02.01.
Depend on model
P02.02
Rated
freque-
ncy of
asynch-
ronous
 motor
0.01Hz–
P00.03
 (Max. output frequency)
50.00
Hz
P02.03
Rated
 speed
 of
asynch-
ronous
 motor
1–
36000rpm
Depend on model
P02.04
Rated
voltage
 of
asynch-
ronous
 motor
0–
1200V
Depend on model
P02.05
Rated
current
of
asynch-
ronous
 motor
0.8–
6000.0A
Depend on model
P02.06
Stator
 resistor
 of
asynch-
ronous
 motor
0.001–
5.535Ω
After motor   parameter autotuning finishes, the setting value of P02.06–
P02.10 will be   updated automatically. These parameters are the basic parameters for   high-performance vector control, which will impact the control performance   directly.
Note: Users   cannot change this group of parameters at will.
Depend on model
P02.07
Rotor
 resistor
 of
asynch-
ronous
 motor
0.001–
65.535Ω
Depend on model
P02.08
Leakage
 induct-
ance
of
asynch-
ronous
 motor
0.1–
6553.5 mH
Depend on model
P02.09
Mutual
induct-
ance
 of
asynch-
ronous
 motor
0.1–6553.5   mH
Depend on model
P02.10
Non-
load
current
 of
asynch-
ronous
 motor
0.1–
6553.5A
Depend on model
P02.11
Magn-
etic
satura-
tion
coeffi-
cient 1
 for the
 iron
core
of AM1
0.0–
100.0%
80.0%
P02.12
Magn
-etic
satura-
tion
coeffi-
cient
 2 for
the
iron
 core
of AM1
0.0–
100.0%
68.0%
P02.13
Magn-
etic
satura-
tion
coeffi-
cient 3
 for
the
iron
core
of AM1
0.0–
100.0%
57.0%
P02.14
Magn-
etic
satura-
tion
coeffi-
cient 4
 for
the
iron
core
of AM1
0.0–
100.0%
40.0%
P02.15
Rated
power
 of
synch-
ronous
 motor
0.1–
3000.0kW
Set the parameters   of the controlled synchronous motor (SM).
To ensure the   control performance, se the values of P02.15 to P02.19 properly according to   the parameters on the name plate of the SM.
Goodrive300 VFDs   provide the parameter autotuning function. Correct parameter autotuning   depends on the correct setting of the name plate parameters of the motor.
To ensure the   control performance, configure the standard matched motor for the VFD. If the   power of the motor configured is greatly different from that of the standard   matched one, the control performance of the VFD degrades significantly.
Note:   P02.16   to P02.19 may be initialized by resetting the rated power of the motor   (P02.15).
Depend on model
P02.16
Rated
frequ-
ency
of
synch-
ronous
 motor
0.01Hz–
P00.03
 (Max.
frequency)
50.00
Hz
P02.17
Number
 of poles
 pairs
for
synch-
ronous
motor
1–50
P02.18
Rated
voltage
 of
synch-
ronous
 motor
0–
1200V
Depend on model
P02.19
Rated
current
 of
synch-
ronous
 motor
0.8–
6000.0A
Depend on model
P02.20
Stator
resistor
 of
synch-
ronous
 motor
0.001–
65.535Ω
After the motor   parameter autotuning is properly complete, the values of P02.20 to P02.22 are   updated automatically. These parameters are the benchmark parameters of   high-performance vector control, directly affecting the control performance.
When P00.15=1   (rotating autotuning), the set value of P02.23 may be automatically updated   by autotuning, In this case, there is no need to change the value of P02.23.   When P00.15=2 (static autotuning), the set value of P02.23 cannot be updated   by autotuning. In this case, calculate and manually change the value of   P02.23.
Depend on model
P02.21
Direct
axis
induct-
ance
of
synch-
ronous
motor
0.01–
655.35mH
Depend on model
P02.22
Quad-
rature
 axis
induct
-ance
 of
synch-
ronous
 motor 1
0.01–
655.35mH
Depend on model
P02.23
Back
 EMF
constant
 of
synch-
ronous
motor
When P00.15=2, the set value of P02.23 cannot be updated by autotuning,   please count according to the following method.
The   counter-electromotive force constant can be counted according to the   parameters on the name plate of the motor. There are three ways to count:
1. If the name plate   designate the counter-electromotive force constant Ke, then:
E=(Ke×nN×2π)/   60
2. If the name plate   designate the counter-electromotive force constant E’(V/1000r/min), then:
E=E’×nN/1000
3. If the name plate   does not designate the above parameters, then:
E=P/√3×I
In the above   formulas: nN is the rated rotation speed, P is the rated power and   I is the rated current.
Setting range:   0–10000
300
P02.24
Initial
 pole
 position
 of
synch-
ronous
 motor
(reserved)
0x0000–
0xFFFF
P02.25
Identifi-
cation
 current
 of
synch-
ronous
motor
(reserved)
0%–50%
 (rated current of the motor)
10%
P02.26
Motor
over-
load
prote-
ction
0: No protection
1: Common motor   (with low speed compensation). Because the heat-releasing effect of the   common motors will be weakened, the corresponding electric heat protection   will be adjusted properly. The low speed compensation characteristic   mentioned here means reducing the threshold of the overload protection of the   motor whose running frequency is below 30Hz.
2: Variable   frequency motor (without low speed compensation) Because the heat-releasing   effect of the specific motors won’t be impacted by the rotation speed, it is   not necessary to adjust the protection value during low-speed running.
P02.27
Motor
over-
load
prote-
ction
coeffi-
cient
Times of motor   overload M = Iout/(In×K)
In is the rated   current of the motor, Iout is the output current of the VFD and K is the   motor protection coefficient.
The smaller K is,   the greater M is, and the more likely protection is implemented.
When M=116%,   protection is performed after motor overload lasts for 1 hour; when M=150%,   protection is performed after motor overload lasts for 12 minutes; when   M=180%, protection is performed after motor overload lasts for 5 minutes;   when M=200%, protection is performed after motor overload lasts for 60   seconds; and when M≥   400%, protection is performed immediately.
Setting   range:
20.0%–120.0%
100.0%
P02.28
Corre-
ction
 coeffi
cient
of
motor
power
Correct the power   displaying of motor 1.
Only impact the displaying   value other than the control performance of the VFD.
Setting range:
0.00–3.00
1.00
P02.29
Para-
meter display of motor 1
0: Display according   to the motor type
1: Display all