P03.00
Speed
loop proportional gain1
The   parameters P03.00–P03.05 only apply to vector control mode. Below the switching frequency 1 (P03.02), the speed loop PI parameters are: P03.00 and   P03.01. Above the switching frequency 2 (P03.05), the speed loop PI   parameters are: P03.03 and P03.04. PI parameters are gained according to the   linear change of two groups of parameters. It is shown as below:
Setting   the proportional coefficient and integral time of the adjustor can change the   dynamic response performance of vector control speed loop. Increasing the   proportional gain and decreasing the integral time can speed up the dynamic   response of the speed loop. But too high proportional gain and too low   integral time may cause system vibration and overshoot. Too low proportional   gain may cause system vibration and speed static deviation.
PI has a close relationship with the inertia of the   system. Adjust on the base of PI according to different loads to meet various   demands.
Setting range of   P03.00: 0–
200.0
Setting range of   P03.01: 0.000–
10.000s
Setting range of   P03.02: 0.00Hz–
P03.05
Setting range of   P03.03: 0–
200.0
Setting range of   P03.04: 0.000–
10.000s
Setting range of   P03.05: P03.02–
P00.03 (Max. output frequency)
20.0
P03.01
Speed
loop
integral
time 1
0.200s
P03.02
Low
switching
frequency
5.00Hz
P03.03
Speed
loop proportional gain 2
20.0
P03.04
Speed
loop
integral
time 2
0.200s
P03.05
High switching
frequency
10.00
Hz
P03.06
Speed
loop
output
filter
0–8 (corresponds   to 0–28/10ms)
P03.07
Compen-
sation coefficient
 of
electromo-
tion
slip
Slip   compensation coefficient is used to adjust the slip frequency of the vector   control and improve the speed control accuracy of the system. Adjusting the   parameter properly can control the speed steady-state error.
Setting range: 50%–200%
100%
P03.08
Compensation coefficient of braking slip
100%
P03.09
Current
loop percentage coefficient P
1 These two parameters adjust the PI adjustment parameter of the   current loop which affects the dynamic response speed and control accuracy   directly. Generally, users do not need to change the default value.
2 Only apply to the   vector control mode without PG 0 (P00.00=0).
Setting range: 0–
65535
1000
P03.10
Current
 loop
 integral coefficient 1
1000
P03.11
Torque
setting method
This parameter is   used to enable the torque control mode, and set the torque.
0: Torque control is   invalid
1: Keypad setting   torque (P03.12)
2: Analog AI1 setting torque
3: Analog AI2 setting torque
4: Analog AI3 setting torque
5: Pulse frequency   HDI setting torque
6: Multi-step torque   setting
7: Modbus   communication setting torque
8: PROFIBUS\CANopen   communication setting torque
9: Ethernet   communication setting torque
10: Reserved
Note: For setting modes of   2–10, 100% corresponds to three times of the rated current of the motor.
P03.12
Keypad setting
torque
Setting range: -300.0%–300.0% (rated current of the motor)
50.0%
P03.13
Torque reference
 filter
time
0.000–10.000s
0.010s
P03.14
Upper frequency
 of
forward rotation
in vector control
0: Keypad (P03.16 sets P03.14, P03.17 sets   P03.15)
1: AI1
2: AI2
3: AI3
4: Pulse frequency HDI setting upper-limit   frequency
5: Multi-step setting upper-limit frequency
6: Modbus communication setting upper-limit   frequency
7: PROFIBUS\CANopen communication setting   upper-limit frequency
8: Ethernet communication setting upper-limit   frequency
9: Reserved
Note: For setting modes of 1–9,   100% corresponds to the maximum frequency.
P03.15
Upper frequency
 of
reverse rotation
in vector control
P03.16
Keypad setting
for upper frequency
of forward rotation
This   function is used to set the upper limit of the frequency. P03.16 sets the   value of P03.14; P03.17 sets the value of P03.15.
Setting range: 0.00 Hz–P00.03 (Max. output   frequency)
50.00 Hz
P03.17
Keypad setting
for upper frequency
 of reverse rotation
50.00 Hz
P03.18
Upper   electro-
motion
 torque
source
This function code is used to select the   electromotion and braking torque upper-limit setting source selection.
0: Keypad setting upper-limit frequency(P03.20 sets P03.18, P03.21 sets P03.19)
1: AI1
2: AI2
3: AI3
4: HDI
5: Modbus communication
6: PROFIBUS\CANopen communication
7: Ethernet communication
8: Reserved
Note: For setting modes   of 1–9, 100% corresponds to three times of the motor current.
P03.19
Upper
braking   torque
source
P03.20
Keypad setting
of
electro-
motion
torque
The function code is used to set the limit of the   torque.
Setting   range: 0.0–300.0% (motor rated current)
180.0%
P03.21
Keypad setting
 of
braking  torque
180.0%
P03.22
Weake-
ning
coeffi-
cient in constant power
 zone
The usage of motor   in weakening control.
Function code P03.22   and P03.23 are effective at constant power. The motor will enter into the   weakening state when the motor runs at rated speed. Change the weakening   curve by modifying the weakening control coefficienct. The bigger the   weakening control coefficienct is, the steeper the weak curve is.
Setting range of   P03.22: 0.1
–2.0
Setting range of   P03.23: 10%–
100%
0.3
P03.23
Lowest
weake-
ning
point
in
constant power
zone
20%
P03.24
Max.
voltage
limit
P03.24 set the Max.   Voltage of the VFD, which is dependent on the site situation.
Setting range: 0.0–120.0%
100.0%
P03.25
Pre-exciting time
Preactivate the   motor when the VFD starts up. Build up a magnetic field inside the VFD to   improve the torque performance during the starting process.
The setting time:
0.000–
10.000s
0.300s
P03.26
Weak magnetic   propor-
tional
gain
0–8000
Note: P03.24–P03.26   are invalid for the vector mode.
1000
P03.27
Vector
control   speed
0: Display the   actual value
1: Display the   setting value
P03.28
Compen-
sation   coefficient
of static friction
0.0–100.0%
Adjust P03.28 to   compensate the coefficient of static friction. Only valid when setting in   1Hz.
0.0%
P03.29
Compen-
sation   coefficient
 of
dynamic friction
0.0–100.0%
Adjust P03.29 to compensate the coefficient of   static friction. Only valid when setting in 1Hz.
0.0%