Function    code
Default    value
Modify
P04.00
Motor 1V/F curve setting
These function codes define the V/F curve of Goodrive300   motor 1 to meet the need of different loads.
0: Straight line V/F curve;applying to the constant torque load
1: Multi-dots V/F curve
2: 1.3th power low torque V/F curve
3: 1.7th power low torque V/F curve
4: 2.0th power low torque V/F curve
Curves 2–4 apply to the torque loads such as fans   and water pumps. Users can adjust according to the features of the loads to   achieve a best energy-consuming effect.
5: Customized V/F(V/F separation); on this mode, V   and F can be separated from adjusted through the frequency given channel set   by P00.06 or the voltage given channel set by P04.27 to change the feature of   the curve.
Note: Vb in the below picture is the motor rated   voltage and fb is the motor rated frequency.
P04.01
Torque boost of motor 1
Boost compensation can be given to the output   voltage for compensating the features of low frequency torque. P04.01 is   for the Max. Output voltage Vb.
P04.02 defines the percentage of closing frequency   of manual torque to fb. Torque boost can   improve the features of low frequency torque of V/F.
Torque boost should be selected according to the   load. The bigger the load is, the bigger the boost is. Too big torque boost   is inappropriate because the motor will run with over-magnetic, and the   current of the VFD will increase to raise the temperature of the VFD and   decrease the efficiency.
When the torque boost is set to 0.0%, the VFD is   automatic torque boost.
Torque boost threshold: under the threshold, the   torque boost is valid, but over the threshold, the torque boost is invalid.
Setting range of   P04.01: 0.0%: (automatic) 0.1%–10.0%
Setting range of   P04.02: 0.0%–50.0%
0.0%
P04.02
Torque boost close of motor 1
20.0%
P04.03
V/F
frequency 1 of motor 1
When P04.00 =1, the user can set V//F curve   through P04.03–P04.08.
V/F is   generally set according to the load of the motor.
Note:V1<V2<V3, f1<f2<f3. Too   high low frequency voltage will heat the motor excessively or cause damage.   The VFD may stall when overcurrent or overcurrent protection.
Setting range of P04.03: 0.00Hz–P04.05
Setting range of P04.04: 0.0%–110.0%
Setting range of P04.05: P04.03– P04.07
Setting range of P04.06: 0.0%–110.0% (the rated   voltage of motor 1)
Setting range of P04.07: P04.05– P02.02 (the   rated frequency of motor 1) or P04.05–P02.16 (the rated frequency of motor 1)
Setting range of P04.08: 0.0%–110.0% (the rated   voltage of motor 1)
0.00Hz
P04.04
V/F
voltgage 1 of motor 1
00.0%
P04.05
V/F
frequency 2 of motor 1
00.00
Hz
P04.06
V/F
voltgage 2 of motor 1
00.0%
P04.07
V/F
frequency 3 of motor 1
00.00
Hz
P04.08
V/F
voltage 3 of motor 1
00.0%
P04.09
V/F slip compensation gain of motor 1
This function code is used to compensate the   change of the rotation speed caused by load during compensation SVPWM control   to improve the rigidity of the motor. It can be set to the rated slip   frequency of the motor which is counted as below:
△f=fb-n×p/60
Of which, fb is the rated frequency of   the motor, its function code is P02.02; n is the rated rotating speed of the   motor and its function code is P02.03; p is the pole pair of the motor.   100.0% corresponds to the rated slip frequency△f.
Setting range: 0.0–200.0%
100.0%
P04.10
Vibration control factor at low frequency   of motor 1
In SVPWM control mode, current fluctuation may   occur to the motor at some frequency, especially the motor with big power.   The motor cannot run stably or overcurrent may occur. These phenomena can be   canceled by adjusting this parameter.
Setting range of   P04.10: 0–100
Setting range of   P04.11: 0–100
Setting range of   P04.12: 0.00Hz–P00.03 (Max. frequency)
10
P04.11
Vibration control factor at high frequency   of motor 1
10
P04.12
Vibration control threshold of motor 1
30.00 Hz
P04.13
Motor 2 V/F curve setting
This group of parameters defines the V/F setting modes   of Goodrive300 motor 2 to meet various requirements of different loads. See   P04.00–P04.12 for the detailed function code instruction.
Note: P04 group includess two sets of V/F parameters   of the motor which cannot display simultaneously. Only the selected V/F   parameter can be shown. The motor selection can be defined by terminals   function "the shift between motor 1 and motor 2".
P04.14
Torque boost of motor 2
0.0%
P04.15
Torque boost close of motor 2
20.0%
P04.16
V/F
frequency 1 of motor 2
0.00Hz
P04.17
V/F
voltage 1 of motor 2
00.0%
P04.18
V/F
frequency 2 of motor 2
00.00
Hz
P04.19
V/F
voltage 2 of motor 2
00.0%
P04.20
V/F
frequency 3 of motor 2
00.00
Hz
P04.21
V/F
voltage 3 of motor 2
00.0%
P04.22
V/F slip compensation gain of motor 2
100.0%
P04.23
Vibration control factor at low frequency   of motor 2
In SVPWM control mode, current fluctuation may occur to the motor on   some frequency, especially the motor with big power. The motor cannot run   stably or overcurrent may occur. These phenomena can be canceled by adjusting   this parameter.
Setting range of   P04.23: 0–100
Setting range of   P04.24: 0–100
Setting range of   P04.25: 0.00 Hz–P00.03 (Max. output frequency)
10
P04.24
Vibration control factor at high frequency   of motor 2
10
P04.25
Vibration control threshold of motor 2
30.00 Hz
P04.26
Energy-saving operation
0: No operation
1: Automatic   energy-saving operation
Motors with light   load will automatically adjust the output voltage to save energy.
P04.27
Voltage setting
Select the output setting channel at V/F curve   separation.
0: Keypad: the   output voltage is determined by P04.28.
1: AI1
2: AI2
3: AI3
4: HDI
5: Multi-step speed
6: PID
7: Modbus communication
8: PROFIBUS/CANopen communication
9: Ethernet communication
10: Reserved
Note: 100% corresponds   to the rated voltage of the motor.
P04.28
Keypad setting voltage
The function code is the voltage displaying when   the voltage is set through keypad.
Setting range: 0.0%–100.0%
100.0%
P04.29
Voltage increasing time
Voltage   increasing time is the time when the VFD accelerates from the output minimum   voltage to the output maximum voltage.
Voltage   decreasing time is the time when the VFD decelerates from the output maximum   voltage to the output minimum voltage.
Setting range: 0.0–3600.0s
5.0s
P04.30
5.0s
P04.31
Max. output voltage
Set the upper and low limit of the output voltage.
Setting range of   P04.31: P04.32–100.0%(the rated voltage of the motor)
Setting range of   P04.32: 0.0%– P04.31(the rated voltage of the motor)
100.0%
P04.32
Min. output voltage
0.0%
P04.33
Weaking   coefficient at constant power
Used during   field-weakening operation to adjust the output voltage of VFD in SVPWM mode.
Note: Invalid in constant-torque mode.
Setting range of P04.33: 1.00–1.30
1.00