Function    code
Default    value
Modify
P05.00
HDI input selection
0: High pulse input. See P05.49–P05.54
1: Digital input. See P05.09.
P05.01
S1 terminals function selection
0: No function
1: Forward rotation operation
2: Reverse rotation operation
3: 3-wire control operation
4: Forward jogging
5: Reverse jogging
6: Coast to stop
7: Fault reset
8: Operation pause
9: External fault input
10: Increasing frequency setting(UP)
11: Decreasing frequency setting(DOWN)
12: Frequency setting clear
13: Shift between A setting and B setting
14: Shift between combination setting and A   setting
15: Shift between combination setting and B   setting
16: Multi-step speed terminal 1
17: Multi-step speed terminal 2
18: Multi-step speed terminal 3
19: Multi- step speed terminal 4
20: Multi- step speed pause
21: ACC/DEC time 1
22: ACC/DEC time 2
23: Simple PLC stop reset
24: Simple PLC pause
25: PID control pause
26: Traverse Pause (stop at the current   frequency)
27: Traverse reset (return to the center   frequency)
28: Counter reset
29: Torque control disabling
30: ACC/DEC disabling
31: Counter trigging
32: Length reset
33: Cancel the frequency change setting   temporarily
34: DC brake
35: Shift the motor 1 into motor 2
36: Shift the command to the keypad
37: Shift the command to the terminals
38: Shift the command to the communication
39: Pre-magnetized command
40: Comsumption power clear
41: Comsumption power holding
42–60: Reserved
61: PID pole switching
62–63: Reserved
P05.02
S2 terminals function selection
4
P05.03
S3 terminals function selection
7
P05.04
S4 terminals function selection
P05.05
S5 terminals function selection
P05.06
S6 terminals function selection
P05.07
S7 terminals function selection
P05.08
S8 terminals function selection
P05.09
HDI terminal function selection
P05.10
Polarity selection of the input terminals
The function code is used to set the polarity of   the input terminals.
Set the bit to 0, the input terminal is anode.
Set the bit to 1, the input terminal is cathode.
Setting range: 0x000–0x1FF
0x000
P05.11
ON-OFF filter time
Set the sample filter time of S1–S8 and HDI   terminals. If the interference is strong, increase the parameter to avoid the   disoperation.
0.000–1.000s
0.010s
P05.12
Virtual terminals setting
0x000–0x1FF(0:   Disabled, 1: Enabled)
BIT0: S1 virtual terminal
BIT1: S2 virtual terminal
BIT2: S3 virtual terminal
BIT3: S4 virtual terminal
BIT4: S5 virtual terminal
BIT5: S6 virtual terminal
BIT6: S7 virtual terminal
BIT7: S8 virtual terminal
BIT8: HDI virtual terminal
Note: After a virtual terminal is enabled, the state   of the terminal can only be modified through communication, and the   communication address is 0x200A.
0x000
P05.13
Terminals control running mode
Set the control operation mode of the terminals.
0: 2-wire control 1; the enabling function and   direction determination function are integrated. This mode is widely used. It   determines the rotation direction by the defined FWD and REV terminals   command.
1: 2-wire control 2; the enabling function and the   direction determination function are separated. In this mode, FWD is the   enablingterminal, and the direction depends on the state of the defined REV.
2: 3-wire control 1; in this mode, SIn is the   enabling terminal, and the running command is generated by FWD and the   direction is controlled by REV. SIn must be in the closed state when the VFD   is running. The FWD terminal generates a rising edge signal, and the VFD   starts to run. The status of the REV terminal determines the running   direction. When the VFD stops, the SIn terminal needs to be disconnected to   complete the stopping.
The direction control is as follows during   operation:
SIn: 3-wire   control; FWD: Forward running; REV: Reverse running
3: 3-wire control mode 2. In this mode, SIn is   defined as the enabling terminal, the running command is determined by the   FWD or REV terminal, and the direction is determined by the FWD and REV   terminals. When the VFD is running, terminal SIn must be in the connected   state. Terminal FWD or REV generates a rising edge signal to run the VFD and   determine its running direction. To stop the running of the VFD, you need to   disconnect terminal SIn.
SlnFWDREVDirectionONOFF→ONONForwardOFFReverseONONOFF→ONForwardOFFReverseON→OFF  Decelerate to stop
SIn: 3-wire operation control; FWD: Forward   running; REV: Reverse running
Note:For the 2-wire running mode, when   the FWD/REV   terminal is valid, and the VFD stops because of the stop command from other   sources, the VFD won't work when the stopping command is canceled even the   control terminal FWD/REV is still valid;. Only when FWD/REV   is re-triggered, the VFD can start again. For example, the PLC single-cycle   stop command, fixed-period stop command, and the STOP/RST stop command that   is valid in terminal control mode (see P07.04).
P05.14
Switch-on delay of S1 terminal
The function code defines the corresponding delay   time of electrical level of the programmable terminals during switching on   and switching off.
Setting range: 0.000–50.000s
0.000s
P05.15
Switch-off delay of S1 terminal
0.000s
P05.16
Switch-on delay of S2 terminal
0.000s
P05.17
Switch-off delay of S2 terminal
0.000s
P05.18
Switch-on delay of S3 terminal
0.000s
P05.19
Switch-off delay of S3 terminal
0.000s
P05.20
Switch-on delay of S4 terminal
0.000s
P05.21
Switch-off delay of S4 terminal
0.000s
P05.22
Switch-on delay of S5 terminal
0.000s
P05.23
Switch-off delay of S5 terminal
0.000s
P05.24
Switch-on delay of S6 terminal
0.000s
P05.25
Switch-off delay of S6 terminal
0.000s
P05.26
Switch-on delay of S7 terminal
0.000s
P05.27
Switch-off delay of S7 terminal
0.000s
P05.28
Switch-on delay of S8 terminal
0.000s
P05.29
Switch-off delay of S8 terminal
0.000s
P05.30
Switch-on delay of HDI terminal
0.000s
P05.31
Switch-off delay of HDI terminal
0.000s
P05.32
Lower limit of AI1
The function code defines the relationship between   the analog input voltage and its corresponding set value. If the analog input   voltage beyond the set minimum or maximum input value, the VFD will count at   the minimum or maximum one.
When the analog input is the current input, the   corresponding voltage of 0–20 mA is 0–10V.
In different cases, the corresponding rated value   of 100.0% is different. See the application for detailed information.
The figure below illustrates different   applications:
Input filter time: this parameter is used to   adjust the sensitivity of the analog input. Increasing the value properly can   enhance the anti-interference of the analog, but weaken the sensitivity of   the analog input.
Note: Analog AI1 and AI2 can support 0–10V or 0–20mA   input, when AI1 and AI2 selects 0–20mA input, the corresponding voltage of   20mA is 5V. AI3 can support the output of -10V–+10V.
Setting range of P05.32: 0.00V–P05.34
Setting range of P05.33: -100.0%–100.0%
Setting range of P05.34: P05.32–10.00V
Setting range of P05.35: -100.0%–100.0%
Setting range of P05.36: 0.000s–10.000s
Setting range of P05.37: 0.00V–P05.39
Setting range of P05.38: -100.0%–100.0%
Setting range of P05.39: P05.37–10.00V
Setting range of P05.40: -100.0%–100.0%
Setting range of P05.41: 0.000s–10.000s
Setting range of P05.42: -10.00V–P05.44
Setting range of P05.43: -100.0%–100.0%
Setting range of P05.44: P05.42–P05.46
Setting range of P05.45: -100.0%–100.0%
Setting range of P05.46: P05.44–10.00V
Setting range of P05.47: -100.0%–100.0%
Setting range of P05.48: 0.000s–10.000s
0.00V
P05.33
Corresponding setting of the lower limit of   AI1
0.0%
P05.34
Upper limit of AI1
10.00V
P05.35
the upper limit of AI1
100.0%
P05.36
AI1 input filter time
0.100s
P05.37
Lower limit of AI2
0.00V
P05.38
Corresponding setting of the lower limit of   AI2
0.0%
P05.39
Upper limit of AI2
10.00V
P05.40
the upper limit of AI2
100.0%
P05.41
AI2 input filter time
0.100s
P05.42
Lower limit of
AI3
-10.00V
P05.43
Corresponding setting of the lower limit of   AI3
-100.0%
P05.44
Middle value of AI3
0.00V
P05.45
Corresponding middle setting of  AI3
0.0%
P05.46
Upper limit of AI3
10.00V
P05.47
the upper limit of AI3
100.0%
P05.48
AI3 input filter time
0.100s
P05.49
HDI high-speed pulse input function
selection
The function selection when HDI terminals   is high-speed pulse input
0: Frequency setting input, frequency   setting source
1: Counter input, high-speed pulse counter   input terminals
2: Length counting input, length counter   input terminals
P05.50
Lower limit frequency of HDI
0.000kHz–P05.52
0.000
kHz
P05.51
Corresponding setting of HDI low frequency   setting
-100.0%–100.0%
0.0%
P05.52
Upper limit frequency of HDI
P05.50–50.000kHz
50.000
kHz
P05.53
Corresponding setting of upper limit   frequency of HDI
-100.0%–100.0%
100.0%
P05.54
HDI frequency input filter time
0.000s–10.000s
0.010s