Function    code
Default    value
Modify
P14.00
Local
commun-
ication
address
Setting range:1–247
When the master   is writing the frame, the communication address of the slave is set to 0; the   address is the communication address. All slaves on the Modbus fieldbus can   receive the frame, but the salve doesn’t answer.
The communication   of the drive is unique in the communication net. This is the fundamental for   the point to point communication between the upper monitor and the drive.
Note: The address of the slave cannot set to 0.
P14.01
Commun-
ication
baud
ratio
Set the digital   transmission speed between the upper monitor and the VFD.
0: 1200BPS
1: 2400BPS
2: 4800BPS
3: 9600BPS
4: 19200BPS
5: 38400BPS
6: 57600BPS
7: 115200BPS
Note: The baud rate between the upper PC and the VFD must be the same.   Otherwise, the communication is not applied. The bigger the baud rate, the   quicker the communication speed.
4
P14.02
Digital bit checkout
The data format   between the upper monitor and the VFD must be the same. Otherwise, the   communication is not applied.
0: No check (N,8,1) for RTU
1: Even check (E,8,1) for RTU
2: Odd check (O,8,1) for RTU
3: No check (N,8,2) for RTU
4: Even check (E,8,2) for RTU
5: Odd check(O,8,2) for RTU
P14.03
Answer delay
0–200ms
The interval time   when the drive receives the data and sent it to the upper monitor. If the   answer delay is shorter than the system processing time, then the answer   delay time is the system processing time, if the answer delay is longer than   the system processing time, then after the system deal with the data, waits   until achieving the answer delay time to send the data to the upper monitor.
5
P14.04
Fault time of communication overtime
0.0(invalid), 0.1–60.0s
When the function   code is set as 0.0, the communication overtime parameter is invalid.
When the function   code is set as non-zero, if the interval time between two communications   exceeds the communication overtime, the system will report "485   communication faults" (CE).
Generally, set it   as invalid; set the parameter in the continuous communication to monitor the   communication state.
0.0s
P14.05
Transmission fault processing
0: Alarm and stop freely
1: No alarm and continue to run
2: No alarm and stop according to the stop mode   (only under the communication control)
3: No alarm and stop according to the stop mode   (under all control modes)
P14.06
Communication processing
0x00–0x11
LED ones:
0: Write with response: the VFD will   respond to all reading and writing commands of the upper monitor.
1: Write without response: the VFD only   responds to the reading command other than the writing command of the drive. The communication efficiency can be increased by this method.
LED tens:
0: Communication encrypting is invalid
1: Communication encrypting is valid
0x00