Function    code
Default    value
Modify
P13.00
Reduction coefficient   of source current
0.0–100.0%
80.0%
P13.01
Original pole test mode
0: No test
1: High-frequency   superposition (reserved)
2: Pulse   superposition
P13.02
Source current 1
Source current   is the positioning current of the magnetic pole position. Source current 1 is   valid under the frequency point of current shifting. Increasing the value can   raise the starting torque.
Setting   range: 0.0%–100.0% (rated current of the motor)
20.0%
P13.03
Source current 2
Source   current is directional current of the magnetic pole position. Source current   2 is valid under the frequency point of current shifting. There is no need to   modify the value generally.
10.0%
P13.04
Shift frequency of   source current
Valid   frequency shifting point between source current 1 and current 2.
Setting   range: 0.00Hz–P00.03 (Max. frequency)
10.00 Hz
P13.05
Superposing frequency (reserved)
200–1000Hz
500Hz
P13.06
Pulse superposing voltage
0.0–300.0% (rated voltage of the motor)
40.0%
P13.07
Reserved
0–65535
P13.08
Control   parameter 1
0–65535
P13.09
Control   parameter 2
0–655.35
2.00
P13.10
Reserved
0–65535
P13.11
Maladjustment   detection time
Adjust the response   of anti-maladjustment. Bigger load inertia may increase the value, but the   response will be slower.
Setting range:   0.0–10.0s
0.5s
P13.12
High frequency   compensation coefficient
When the motor speed   is faster than the rated speed, the parameter is valid, if vibration occurs   to the motor, please adjust the parameter.
Setting   range: 0–100.0%
0.0%
P13.13
Braking current of short-circuit
When P01.00=0 during   the starting of the VFD, set P13.14 to a non-zero value to enter the short   circuit braking.
When the running   frequency is lower than P01.09 during the stopping of the VFD, set 13.15 to a   non-zero value to enter into stopping short circuited braking and then carry   out the DC braking at the time set by P01.12 (refer to the instruction of   P01.09–P01.12) .
Setting range of   P13.13: 0.0–150.0%(the VFD)
Setting range of   P13.14: 0.00–50.00s
Setting range of   P13.15: 0.00–50.00s
0.0%
P13.14
Braking retention   time before  starting
0.00s
P13.15
The braking   retention time when stopping
0.00s