Goodrive310-UL series VFDs have 2 relay output terminals and 1 Y output terminal and 1 high speed pulse output terminal in the standard configuration. All functions of the digital input terminals are programmable by the function codes. Open collector pole input can be selected into high speed pulse input terminal or common switch input terminal by function code.
The table below describes the option of the four function parameters and selecting the repeated output terminal function is allowed.
Set value
Function
Instructions
Invalid
The output terminal has no function.
Running
Output ON signal when the VFD is running and there is frequency output.
Forward running
Output ON signal when the VFD is running forward and there is frequency output.
3
Reverse running
Output ON signal when the VFD is running reverse and there is frequency output.
4
Jogging
Output ON signal when the VFD is jogging and there is frequency output.
5
VFD fault
Output ON signal when the VFD is in fault
6
FDT1
Please refer to P08.32 and P08.33 for detailed information.
7
FDT2
Please refer to P08.34 and P08.35 for detailed information.
8
Frequency arrival
Please refer to P08.36 for detailed information.
9
Zero-speed running
Output ON signal when the output frequency and given frequency of the VFD is 0 at the same time.
10
Upper-limit frequency arrival
Output ON signal when the running frequency of the VFD is the upper limit frequency.
11
Output ON signal when the running frequency of the VFD is the lower limit frequency.
12
Ready
When the main circuit and the control circuit is established and the protection function of the VFD is not active. The VFD is in the running state and it will output ON signal.
13
Pre-exciting
Output ON signal when the VFD is in the pre-exciting state.
14
Overload pre-alarm
Output ON signal if the VFD is beyond the pre-alarm point. Refer to P11.08–P11.10 for the detailed instruction.
15
Underload pre-alarm
Output ON signal if the VFD is beyond the pre-alarm point. Refer to P11.11–P11.12 for the detailed instruction.
16
Simple PLC stage completion
Output signal if the simple PLC stage is completed.
17
 Simple PLC cycle completion
Output signal if the simple PLC cycle is completed.
18
Set counting arrival
Output ON signal if the detected counting exceeds the set value of P08.25.
19
Fixed counting arrival
Output ON signal if the detected counting exceeds the set value of P08.26.
20
External fault valid
Output ON signal if external fault occurs.
21
Length arrival
Output ON signal if the actual detected length exceeds the se length by P08.19.
22
Running time arrival
Output ON signal if the accumulative running time of the VFD exceeds the setting time by P08.27.
23
MODBUS communication virtual terminal output
Output corresponding signal according to the setting value of MODBUS. Output ON signal if the setting value is 1 and output OFF signal if the setting value is 0.
24
POROFIBUS communication virtual terminal output
Output corresponding signal according to the setting value of PROFIBUS/CANOPEN. Output ON signal if the setting value is 1 and output OFF signal if the setting value is 0.
26
Voltage establishment finished
The output is valid when the bus voltage reaches the undervoltage point.
27–30
Reserved
Related parameters list:
Function code
Default value
P06.00
HDO output
0: Open collector pole high speed pulse output
1: Open collector pole output
P06.01
Y output
0: Invalid
1: In operation
2: Forward rotation operation
3: Reverse rotation operation
4: Jogging operation
5: The VFD fault
6: Frequency degree test FDT1
7: Frequency degree test FDT2
8: Frequency arrival
9: Zero speed running
10: Upper limit frequency arrival
11: Lower limit frequency arrival
12: Ready for operation
13: Pre-magnetizing
14: Overload pre-alarm
15: Underload pre-alarm
16: Completion of simple PLC stage
17: Completion of simple PLC cycle
18: Setting count value arrival
19: Defined count value arrival
20: External fault valid
21: Length arrival
22: Running time arrival
23: MODBUS communication virtual terminals output
24: PROFIBUS/CANopen communication virtual terminals output
25: Ethernet communication virtual terminals output
26: Voltage establishment finished
27–30: Reserved
P06.02
HDO output
P06.03
Relay RO1 output
P06.04
Relay RO2 output
5
P06.05
Polarity of output terminals
0x00–0x0F
0x00
P06.06
Y switch-on delay time
0.000–50.000s
0.000s
P06.07
Y switch-off delay time
0.000–50.000s
0.000s
P06.08
HDO switch-on delay time
0.000–50.000s (valid only when P06.00=1)
0.000s
P06.09
HDO switch-off delay time
0.000s
P06.10
RO1 switch-on delay time
0.000–50.000s
0.000s
P06.11
RO1 switch-off delay time
0.000–50.000s
0.000s
P06.12
RO2 switch-on delay time
0.000–50.000s
0.000s
P06.13
RO2 switch-off delay time
0.000–50.000s
0.000s
P07.38
The max temperature at present fault
P17.13
Digital output terminals state