5.5.19 Fault handling
The following provides fault handling information.
Related parameter list:
Function code
Description
Default
P07.27
Present fault type
0: No fault
1: Inverter unit U-phase protection (OUt1)
2: Inverter unit V-phase protection (OUt2)
3: Inverter unit W-phase protection (OUt3)
4: Overcurrent during acceleration (OC1)
5: Overcurrent during deceleration (OC2)
6: Overcurrent during constant speed   running (OC3)
7: Overvoltage during acceleration (OV1)
8: Overvoltage during deceleration (OV2)
9: Overvoltage during constant speed   running (OV3)
10: Bus undervoltage fault (UV)
11: Motor overload (OL1)
12: VFD overload (OL2)
13: Phase loss on input side (SPI)
14: Phase loss on output side (SPO)
15: Rectifier module overheat (OH1)
16: Inverter module overheat (OH2)
17: External fault (EF)
18: Modbus/Modbus TCP communication fault   (CE)
19: Current detection fault (ItE)
20: Motor autotuning fault (tE)
21: EEPROM operation error (EEP)
22: PID feedback offline fault (PIDE)
23: Braking unit fault (bCE)
24: Running time reached (END)
25: Electronic overload (OL3)
26: Keypad   communication error (PCE)
27: Parameter upload error (UPE)
28: Parameter download error (DNE)
29: Profibus DP communication fault (E-DP)
30: Ethernet communication fault (E_NET)
31: CANopen communication fault (E-CAN)
32: To-ground short-circuit fault 1 (ETH1)
33: To-ground short-circuit fault 2 (ETH2)
34: Speed deviation fault (dEu)
35: Mal-adjustment fault (STo)
36: Underload fault (LL)
37: Encoder disconnection fault (ENC1O)
38: Encoder direction reversal fault   (ENC1D)
39: Encoder Z-pulse disconnection fault   (ENC1Z)
40: Safe torque off (STO)
41: Channel 1 safety circuit exception   (STL1)
42: Channel 2 safety circuit exception   (STL2)
43: Exception in both channels 1 and 2   (STL3)
44: Safety code FLASH CRC fault (CrCE)
45: PLC card customized fault 1 (P-E1)
46: PLC card customized fault 2 (P-E2)
47: PLC card customized fault 3 (P-E3)
48: PLC card customized fault 4 (P-E4)
49: PLC card customized fault 5 (P-E5)
50: PLC card customized fault 6 (P-E6)
51: PLC card customized fault 7 (P-E7)
52: PLC card customized fault 8 (P-E8)
53: PLC card customized fault 9 (P-E9)
54: PLC card customized fault 10 (P-E10)
55: Duplicate expansion card type (E-Err)
56: Encoder UVW lost (ENCUV)
57: Profinet communication   timeout fault (E-PN)
58: CAN communication fault (SECAN)
59: Motor overtemperature fault (OT)
60: Failure to identify the card at slot 1   (F1-Er)
61: Failure to identify the card at slot 2   (F2-Er)
62: Failure to identify the card at slot 3   (F3-Er)
63: Communication timeout of the card at   slot 1 (C1-Er)
64: Communication timeout of the card at   slot 2 (C2-Er)
65: Communication timeout of the card at   slot 3 (C3-Er)
66: EtherCAT communication fault (E-CAT)
67: Bacnet communication fault (E-BAC)
68: DeviceNet communication fault (E-DEV)
69: CAN slave fault in   master/slave synchronization (S-Err)
70: Expansion   card PT100 overtemperature (OtE1)
71: Expansion   card PT1000 overtemperature (OtE2)
72:   EthernetIP communication timeout (E-EIP)
P07.28
Last fault type
P07.29
2nd-last fault type
P07.30
3rd-last fault type
P07.31
4th-last fault type
P07.32
5th-last fault type
P07.33
Running frequency at present fault
0.00Hz
P07.34
Ramp reference frequency at present fault
0.00Hz
P07.35
Output current at present fault
0V
P07.36
0.0A
P07.37
Bus voltage at present fault
0.0V
P07.38
Max. temperature at present fault
0.0°C
P07.39
Input terminal status at present fault
P07.40
Output terminal status at present fault
P07.41
Running frequency at last fault
0.00Hz
P07.42
Ramp reference frequency at last fault
0.00Hz
P07.43
Output voltage at last fault
0V
P07.44
Output current at last fault
0.0A
P07.45
Bus voltage at last fault
0.0V
P07.46
Max. temperature at last fault
-20.0–120.0°C
0.0°C
P07.47
Input terminal status at last fault
P07.48
Output terminal status at last fault
P07.49
Running frequency at 2nd-last fault
0.00Hz
P07.50
Ramp reference frequency at 2nd-last   fault
0.00Hz
P07.51
Output voltage at 2nd-last fault
0V
P07.52
Output current at 2nd-last fault
0.0A
P07.53
Bus voltage at 2nd-last fault
0.0V
P07.54
Max temperature at 2nd-last fault
-20.0–120.0°C
0.0°C
P07.55
Input terminal status at 2nd-last fault
P07.56
Output terminal status at 2nd-last fault