Related parameter list:
Function code
Description
Default
P06.00
HDO output type
0: Open collector high-speed pulse output
1: Open collector output
P06.14
AO1 output
0:   Running frequency (0–Max. output frequency)
1:   Set frequency (0–Max. output frequency)
2:   Ramp reference frequency (0–Max. output frequency)
3:   Rotational speed (0–Speed corresponding to max. output frequency)
4:   Output current (0–Twice the VFD rated current)
5:   Output current (0–Twice the motor rated current)
6:   Output voltage (0–1.5 times the VFD rated voltage)
7:   Output power (0–Twice the motor rated power)
8:   Set torque (0–Twice the motor rated current)
9:   Output torque (Absolute value, 0–+/- Twice the motor rated torque)
10:   AI1 input (0–10V/0–20mA)
11:   AI2 input (0–10V)
12:   AI3 input (0–10V/0–20mA)
13:   HDIA input(0.00–50.00kHz)
14:   Value 1 set through Modbus/Modbus TCP (0–1000)
15:   Value 2 set through Modbus/Modbus TCP (0–1000)
16:   Value 1 set through PROFIBUS/CANopen/DeviceNet (0–1000)
17:   Value 2 set through PROFIBUS/CANopen/DeviceNet (0–1000)
18:   Value 1 set through Ethernet 1 (0–1000)
19:   Value 2 set through Ethernet 2 (0–1000)
20:   HDIB input (0.00–50.00kHz)
21:   Value 1 set through EtherCat/Profinet/EtherNetIP (0–1000)
22:   Torque current  (bipolar, 0–Triple the   motor rated current)
23:   Exciting current (bipolar, 0–Triple the motor rated current)
24:   Set frequency (bipolar, 0–Max. output frequency)
25:   Ramp reference frequency (bipolar, 0–Max. output frequency)
26:   Rotational speed (bipolar, 0–Speed corresponding to max. output frequency)
27:   Value 2 set through EtherCat/Profinet/EtherNetIP (0–1000)
28:   C_AO1 (Set P27.00 to 1. 0–1000)
29:   C_AO2 (Set P27.00 to 1. 0–1000)
30:   Rotational speed (0–Twice the motor rated synchronous speed)
31:   Output torque (Actual value, 0–Twice the motor rated torque)
32–47: Reserved
P06.15
Reserved
P06.16
HDO high-speed pulse output
P06.17
AO1 output lower limit
-300.0%–P06.19
0.0%
P06.18
AO1 output corresponding to lower limit
0.00V–10.00V
0.00V
P06.19
AO1 output upper limit
P06.17–300.0%
100.0%
P06.20
AO1 output corresponding to upper limit
0.00V–10.00V
10.00V
P06.21
AO1 output filter time
0.000s–10.000s
0.000s
P06.22P06.26
Reserved
0–65535
P06.27
HDO output lower limit
-300.0%–P06.29
0.0%
P06.28
HDO output corresponding to lower limit
0.00–50.00kHz
0.0kHz
P06.29
HDO output upper limit
P06.27–300.0%
100.0%
P06.30
HDO output corresponding to upper limit
0.00–50.00kHz
50.00kHz
P06.31
HDO output filter time
0.000s–10.000s
0.000s
5.5.11 Digital input
The VFD provides four programmable digital input terminals and two HDI input terminals. All the digital input terminal functions can be programmed by function codes. HDI input terminal can be set to act as high-speed pulse input terminal or common digital input terminal; if it is set to act as high-speed pulse input terminal, you can also set HDIA or HDIB high-speed pulse input to serve as the frequency reference and encoder signal input.
Note: Two different multifunction input terminals cannot be set as the same function.
Setting
Function
Description
No   function
The VFD   does not act even if there is signal input. Set unused terminals without   functions to avoid misaction.
Run forward (FWD)
Control the forward/reverse running of the   VFD by external terminals.
Run reversely (REV)
3
Three-wire   running control
Set the VFD running mode to 3-wire control mode   by this terminal. See P05.13 for details.
4
Jog   forward
For details about the frequency and   ACC/DEC time at jogging, see P08.06, P08.07 and P08.08.
5
Jog   reversely
6
Coast to stop
The VFD blocks output, and the stop process of motor is uncontrolled   by the VFD. This mode is applied in cases of large-inertia load and free stop   time; its definition is the same as P01.08, and it is mainly used in remote control.
7
Fault   reset
External fault reset function, same as the reset function of the STOP/RST   key on the keypad. You can use this function to reset faults remotely.
8
Pause running
When the VFD   decelerates to stop, however, all the running parameters are in memory state,   including PLC parameter, wobbling frequency, and PID parameter. After this   signal disappears, the VFD restores to the state before stop.
9
External fault input
When an external fault signal is transmitted   to the VFD, the VFD releases a fault alarm and stops.
10
Increase   frequency setting (UP)
Used to change the frequency increase/decrease command when the   frequency is given by external terminals.
The terminal used to clear frequency   increase/decrease setting can clear the frequency value of auxiliary channel   set by UP/DOWN, thus restoring the reference frequency to the frequency given by   main reference frequency command channel.
12
Decrease   frequency setting (DOWN)
12
Clear   the frequency increase/decrease setting
13
Switch between A setting and B setting
Used to switch between the frequency setting channels.
A frequency reference channel and B frequency   reference channel can be switched by no. 13 function; the combination channel   set by P00.09 and the A frequency reference channel can be   switched by no. 14 function; the combination channel set by P00.09 and the B frequency reference channel can be switched by no. 15 function.
14
Switch between combination setting and A   setting
15
Switch   between combination setting and B setting
16
Multi-step speed terminal 1
A   total of 16-step speeds can be set by combining   digital states of these four terminals.
Note: Multi-step speed 1 is the low-order bit, multi-step speed 4 is the   high-order bit.
17
Multi-step speed terminal 2
18
Multi-step speed terminal 3
19
Multi-step speed terminal 4
20
Pause   multi-step speed running
Used to pause multi-step speed   selection function to keep the set value in present state.
21
ACC/DEC   time selection 1
The two terminals are   used to select four groups of acceleration/decoration time. (T indicates   Terminal in the following table.)
22
ACC/DEC time selection 2
23
Simple PLC stop reset
Used to restart simple PLC process and clear previous PLC state information.
24
Pause simple PLC
The program pauses during PLC execution, and keeps running in present   speed step. After this function is cancelled, simple PLC keeps running.
25
Pause PID control
PID is ineffective temporarily, and the VFD maintains present   frequency output.
26
Pause wobbling frequency (stopped at the   current frequency)
The VFD pauses at   current output. After this function is canceled, it continues   wobbling-frequency operation at current frequency.
27
Reset wobbling frequency (back to the   central frequency)
The set frequency of VFD returns to the   center frequency.
28
Counter   reset
The   counter is cleared.
29
Switch between speed control and torque   control
The VFD switches from torque control mode to speed control mode, or   vice versa.
30
Disable ACC/DEC
Used to ensure the VFD is   not be impacted by external signals (except for stop command), and the VFD   maintains the present output frequency.
31
Trigger the counter
Used to enable the counter   to cunt pulses.
33
Clear the frequency increase/decrease   setting temporarily
When   the terminal is closed, the frequency value set by UP/DOWN can   be cleared to restore the reference frequency to the frequency given by   frequency command channel; when terminal is disconnected, it will revert to   the frequency value after frequency increase/decrease setting.
34
DC braking
The VFD immediately starts DC braking once after the command is   valid.
35
Switch between motor 1 and motor 2
When the function is valid, the switchover   between the two motors can be controlled.
36
Switch the running command channel to   keypad
When the function is enabled, the running   command channel is switched to keypad. When the function is disabled, the   running command channel is restored to the previous setting.
37
Switch the running command channel to   terminal
When the function is enabled, the running   command channel is switched to terminal. When the function is disabled, the   running command channel is restored to the previous setting.
38
Switch the running command channel to   communication
When the function is enabled, the running   command channel is switched to communication. When the function is disabled,   the running command channel is restored to the previous setting.
39
Pre-exciting command
When this terminal is valid, motor pre-exciting is started and   continues until this terminal becomes invalid.
40
Clear electricity consumption
When this command becomes valid, the   electricity consumption quantity of the VFD is cleared.
41
Keep electricity consumption
When this command is valid, the present running of the VFD has no   impact on the electricity consumption   quantity.
42
Switch the setting source of braking   torque upper limit to keypad
When this command is valid, the upper limit of the torque is set   through the keypad.
43
Position reference point input
Valid only for S1, S2, and S3.
44
Disable spindle orientation
Used to disable spindle orientation.
45
Spindle zeroing / Local positioning   zeroing
Used to trigger and enable spindle orientation.
46
Spindle zero position selection 1
Spindle zero position selection 1 made   through terminals
47
Spindle zero position selection 2
Spindle zero position selection 2 made   through terminals
48
Spindle scale division selection 1
Spindle scale division selection 1 made   through terminals
49
Spindle scale division selection 2
Spindle scale division selection 2 made   through terminals
50
Spindle scale division selection 3
Spindle scale division selection 3 made   through terminals
51
Terminal for switching between position   control and speed control
Used to switch between position control and   speed control
52
Disable pulse input
When this function is valid, pulse input is   invalid.
53
Clear position deviation
Used to clear the input deviation of the   position loop.
54
Switch position proportional gains
Used to switch position proportional gains.
55
Enable cyclic digital positioning
When the digital positioning mode is valid,   the cyclic digital positioning function can be enabled.
56
Emergency stop
When   this command is valid, the motor decelerates to emergency stop according to   the time set by P01.25.
57
Motor overtemperature fault input
The motor stops at   motor over-temperature fault input.
59
Switch from FVC to space voltage vector   control
When this terminal is valid in stop state, the space voltage vector   control mode is used.
60
Switch to FVC control
When this terminal is valid in stop state, the FVC mode is used.
61
Switch PID polarities
Used   together with P09.03.
62
Reserved
63
Enable servo
When the thousands place of P21.00   determines to enable servo, the servo enabling terminal is valid, which   controls to VFD to enter zero servo control. At this time, a start command is   not required.
64
Limit on forward running
Used to specify the limit on forward   running.
65
Limit on reverse running
Used to specify the limit on reverse   running.
66
Clear encoder counting
Used to clear encoder counting.
67
Increase pulses
When the   terminal function is valid, the pulse input is increased according to the P21.27 pulse speed.
68
Enable pulse superposition
When   the pulse superimposition is enabled, pulse increase and pulse decrease are   effective.
69
Decrease pulses
When   the terminal function is valid, the pulse input is decreased according to the   P21.27 pulse speed.
70
Electronic gear selection
When the   terminal is valid, the proportional numerator is switched to the P21.30 numerator of the   2nd command ratio.
71
Switch   to mater
In stopped state, if the   function is valid, the master is used.
72
Switch   to slave
In stopped state, if the   function is valid, the slave is used.
73
Trigger   fire mode control
If fire mode control is   triggered, P28.25 is valid.
74–79
Reserved
Function code
Description
Default
P05.00
HDI input type
0x00–0x11
Ones: HDIA input   type
0: HDIA is   high-speed pulse input
1: HDIA is   digital input
Tens: HDIB input   type
0: HDIB is   high-speed pulse input
1: HDIB is   digital input
0x00
P05.01
Function of S1 terminal
0: No function
1: Forward running
2: Reverse running
3: 3-wire control/Sin
4: Forward jogging
5: Reverse jogging
6: Coast to stop
7: Fault reset
8: Running pause
9: External fault input
10: Frequency increase   (UP)
11: Frequency decrease   (DOWN)
12: Clear frequency   increase/decrease setting
13: Switch-over between setup   A and setup B
14: Switch-over between   combination setting and A setting
15: Switch-over between   combination setting and setup B
16: Multi-step speed terminal 1
17: Multi-step speed terminal 2
18: Multi-step speed terminal 3
19: Multi-step speed terminal 4
20: Multi-step speed pause
21: ACC/DEC time selection 1
22: ACC/DEC time selection 2
23: Simple PLC stop reset
24: Simple PLC pause
25: PID control pause
26: Wobbling frequency pause
27: Wobbling frequency reset
28: Counter reset
29: Switching between speed control and torque control
30: ACC/DEC disabled
31: Counter trigger
32: Reserved
33: Clear frequency   increase/decrease setting temporarily
34: DC brake
35: Switching between motor 1   and motor 2
36: Command switches to keypad
37: Command switches to   terminal
38: Command switches to   communication
39: Pre-exciting command
40: Zero out power consumption   quantity
41: Maintain power consumption   quantity
42: Source of upper torque   limit switches to keypad
56: Emergency stop
57: Motor over-temperature   fault input
59: Switch to V/F control
60: Switch to FVC control
61: PID polarity switch-over
66: Zero out encoder counting
67: Pulse increase
68: Enable pulse superimposition
69: Pulse decrease
70: Electronic gear selection
71: Switch to the master
72: Switch to the slave
73: Trigger fire mode control
74–79:   Reserved
P05.02
Function of S2   terminal
4
P05.03
Function of S3   terminal
7
P05.04
Function of S4   terminal
P05.05
Function of HDIA   terminal
P05.06
Function of HDIB   terminal
P05.07
Reserved
P05.08
Polarity of input terminal
0x00–0x3F
0x00
P05.09
Digital filter time
0.000–1.000s
0.010s
P05.10
Virtual terminal   setting
0x00–0x3F   (0: Disable; 1: Enable)
BIT0: S1 virtual terminal
BIT1: S2 virtual terminal
BIT2: S3 virtual terminal
BIT3: S4 virtual terminal
BIT4: HDIA virtual terminal
BIT8: HDIB   virtual terminal
0x00
P05.11
2/3-wire control   mode
0: 2-wire control 1
1: 2-wire control 2
2: 3-wire control 1
3: 3-wire control   2
P05.12
S1 terminal switch-on delay
0.000–50.000s
0.000s
P05.13
S1 terminal switch-off delay
0.000–50.000s
0.000s
P05.14
S2 terminal switch-on delay
0.000–50.000s
0.000s
P05.15
S2 terminal switch-off delay
0.000–50.000s
0.000s
P05.16
S3 terminal switch-on delay
0.000–50.000s
0.000s
P05.17
S3 terminal switch-off delay
0.000–50.000s
0.000s
P05.18
S4 terminal switch-on delay
0.000–50.000s
0.000s
P05.19
S4 terminal switch-off delay
0.000–50.000s
0.000s
P05.20
HDIA terminal switch-on delay
0.000–50.000s
0.000s
P05.21
HDIA terminal switch-off delay
0.000–50.000s
0.000s
P05.22
HDIB terminal switch-on delay
0.000–50.000s
0.000s
P05.23
HDIB terminal switch-off delay
0.000–50.000s
0.000s
P07.39
Input terminal state of present fault
P17.12
Digital input terminal state
5.5.12 Digital output
The VFD provides two groups of relay output terminals, one open collector Y output terminal and one high-speed pulse output (HDO) terminal. All the digital output terminal functions can be programmed by function codes, of which the high-speed pulse output terminal HDO can also be set to high-speed pulse output or digital output by function code.
The following table lists the function code options. A same output terminal function can be repeatedly selected.
Setting
Function
Description
Invalid
Output terminal has no function
In running
Output ON signal when there is frequency output during running
In forward running
Output ON signal when there is frequency   output during forward running
3
In reverse running
Output ON signal when there is frequency output during reverse running
4
In jogging
Output ON signal when there is frequency output during jogging
5
VFD fault
Output ON signal when VFD fault occurred
6
Frequency level   detection FDT1
Refer to P08.32 and P08.33.
7
Frequency level   detection FDT2
Refer to P08.34 and P08.35.
8
Frequency reached
Refer to P08.36.
9
Running in zero speed
Output ON signal when the VFD output frequency and reference frequency   are both zero.
10
Reach upper limit   frequency
Output ON signal   when the running frequency reaches upper limit frequency
11
Reach lower limit   frequency
Output ON signal   when the running frequency reached lower limit frequency
12
Ready to run
Main circuit and   control circuit powers are established, the protection functions do not act;   when the VFD is ready to run, output ON signal.
13
In pre-exciting
Output ON signal   during pre-exciting of the VFD
14
Overload pre-alarm
Output ON signal   after the pre-alarm time elapsed based on the pre-alarm threshold; see P11.08P11.10 for details.
15
Underload pre-alarm
Output ON signal   after the pre-alarm time elapsed based on the pre-alarm threshold; see P11.11P11.12 for details.
16
Simple PLC state completed
Output signal when current stage of simple PLC is completed
17
Simple PLC cycle   completed
Output signal when a single cycle of simple PLC operation is completed
23
Virtual terminal output of Modbus/Modbus   TCP communication
Output corresponding signal based on the set value of Modbus/Modbus TCP; output ON   signal when it is set to 1, output OFF signal when it is set to 0
24
Virtual terminal output of POROFIBUS/CANopen/DeviceNET communication
Output corresponding signal based on the set value of PROFIBUS\CANopen;   output ON signal when it is set to 1, output OFF signal when it is set to 0
25
Virtual terminal output of Ethernet communication
Output corresponding signal based on the set value of Ethernet; output   ON signal when it is set to 1, output OFF signal when it is set to 0.
26
DC bus voltage   established
Output is valid when the bus voltage is above the undervoltage   threshold of the inverter
27
Z pulse output
Output is valid when the encoder Z pulse is arrived, and is invalid   after 10 ms.
28
During pulse superposition
Output is valid when the pulse superposition terminal input function is   valid
29
STO action
Output when STO fault occurred
30
Positioning completed
Output is valid when position control positioning is completed
31
Spindle zeroing completed
Output is valid when spindle zeroing is completed
32
Spindle scale-division   completed
Output is valid when spindle scale-division is completed
33
In speed limit
Output is valid when the frequency is limited
34
Virtual terminal output of EtherCat/Profinet/EtherNetIP communication
The corresponding   signal is output according to the set value of Profinet communication. When it   is set to 1, the ON signal is output, and when it is set to 0, the OFF signal   is output.
35
Reserved
36
Speed/position control   switch-over completed
Output is valid when   the mode switch-over is completed
37–40
Reserved
41
C_Y1
C_Y1 from PLC (You   need to set P27.00 to 1.)
42
C_Y2
C_Y2 from PLC (You   need to set P27.00 to 1.)
43
C_HDO
C_HDO from PLC (You   need to set P27.00 to 1.)
44
C_RO1
C_RO1 from PLC(You need to set P27.00 to 1.)
45
C_RO2
C_RO2 from PLC (You need to set P27.00 to 1.)
46
C_RO3
C_RO3 from PLC (You need to set P27.00 to 1.)
47
C_RO4
C_RO4 from PLC (You need to set P27.00 to 1.)
48–63
Reserved
Function code
Description
Default
P06.00
HDO output type
P06.01
Y1 output selection
0: Invalid
1: In running
2: In forward running
3: In reverse running
4: In jogging
5: VFD fault
6: Frequency level detection FDT1
7: Frequency level detection FDT2
8: Frequency reached
9: Running in zero speed
10: Reach upper limit frequency
11: Reach lower limit frequency
12: Ready to run
13: In pre-exciting
14: Overload pre-alarm
15: Underload pre-alarm
16: Simple PLC stage completed
17: Simple PLC cycle completed
18: Reach set   counting value
19: Reach   designated counting value
20: External   fault is valid
21: Reserved
22: Reach running   time
23: Virtual   terminal output of Modbus/Modbus TCP communication
24: Virtual   terminal output of PROFIBUS/CANopen/DeviceNET communication
25: Virtual   terminal output of Ethernet communication
26: DC bus   voltage established
27: Z   pulse output
28: In pulse   superposition
29: STO   action
30: Positioning   completed
31: Spindle   zeroing completed
32: Spindle   scale-division completed
33: In   speed limit
34: Virtual   terminal output of EtherCat/Profinet/EtherNetIP   communication
35:   Reserved
36: Speed/position   control switch-over completed
37: Reach any frequency
38–40:   Reserved
41: C_Y1 from PLC (You need to set P27.00 to 1.)
42: C_Y2 from PLC   (You need to set P27.00 to 1.)
43: C_HDO from   PLC (You need to set P27.00 to 1.)
44: C_RO1 from   PLC (You need to set P27.00 to 1.)
45: C_RO2 from   PLC (You need to set P27.00 to 1.)
46: C_RO3 from   PLC (You need to set P27.00 to 1.)
47: C_RO4 from   PLC (You need to set P27.00 to 1.)
48–63:   Reserved
P06.02
HDO output selection
P06.03
RO1 output selection
P06.04
RO2 output selection
5
P06.05
Output terminal polarity selection
0x00–0x0F
0x00
P06.06
Y switch-on delay
0.000–50.000s
0.000s
P06.07
Y switch-off delay
0.000–50.000s
0.000s
P06.08
HDO switch-on delay
0.000–50.000s   (valid only when P06.00=1)
0.000s
P06.09
HDO switch-off delay
0.000s
P06.10
RO1 switch-on delay
0.000–50.000s
0.000s
P06.11
RO1 switch-off delay
0.000–50.000s
0.000s
P06.12
RO2 switch-on delay
0.000–50.000s
0.000s
P06.13
RO2 switch-off delay
0.000–50.000s
0.000s
P07.40
Output terminal status at present fault
P17.13
Digital output terminal status
5.5.13 Simple PLC
Simple PLC is a multi-step speed generator, and the VFD can change the running frequency and direction automatically based on the running time to fulfill process requirements. Previously, such function was realized with external PLC, while now, the VFD itself can achieve this function.
The VFD can realize 16-step speeds control, and provide four groups of acceleration/deceleration time for you to choose.
After the set PLC completes one cycle (or one segment), one ON signal can be output by the multifunction relay.
Function code
Description
Default
P05.01P05.06
Digital input function selection
24: Pause simple PLC
25: Pause PID control
P06.01P06.04
Digital output function selection
16: Simple PLC stage reached
17: Simple PLC cycle reached
P10.00
Simple PLC mode
0: Stop after   running once
1: Keep running   in the final value after running once
2: Cyclic running
P10.01
Simple PLC memory selection
0: No memory   after power off
1: Memory after power off
P10.02
Multi-step speed 0
-100.0–100.0%
0.0%
P10.03
Running time of step 0
0.0–6553.5s   (min)
0.0s
P10.04
Multi-step speed 1
-100.0–100.0%
0.0%
P10.05
Running time of step 1
0.0–6553.5s   (min)
0.0s
P10.06
Multi-step speed 2
-100.0–100.0%
0.0%
P10.07
Running time of step 2
0.0–6553.5s   (min)
0.0s
P10.08
Multi-step speed 3
-100.0–100.0%
0.0%
P10.09
Running time of step 3
0.0–6553.5s   (min)
0.0s
P10.10
Multi-step speed 4
-100.0–100.0%
0.0%
P10.11
Running time of step 4
0.0–6553.5s   (min)
0.0s
P10.12
Multi-step speed 5
-100.0–100.0%
0.0%
P10.13
Running time of step 5
0.0–6553.5s   (min)
0.0s
P10.14
Multi-step speed 6
-100.0–100.0%
0.0%
P10.15
Running time of step 6
0.0–6553.5s   (min)
0.0s
P10.16
Multi-step speed 7
-100.0–100.0%
0.0%
P10.17
Running time of step 7
0.0–6553.5s   (min)
0.0s
P10.18
Multi-step speed 8
-100.0–100.0%
0.0%
P10.19
Running time of step 8
0.0–6553.5s   (min)
0.0s
P10.20
Multi-step speed 9
-100.0–100.0%
0.0%
P10.21
Running time of step 9
0.0–6553.5s   (min)
0.0s
P10.22
Multi-step speed 10
-100.0–100.0%
0.0%
P10.23
Running time of step 10
0.0–6553.5s   (min)
0.0s
P10.24
Multi-step speed 11
-100.0–100.0%
0.0%
P10.25
Running time of step 11
0.0–6553.5s   (min)
0.0s
P10.26
Multi-step speed 12
-100.0–100.0%
0.0%
P10.27
Running time of step 12
0.0–6553.5s   (min)
0.0s
P10.28
Multi-step speed 13
-100.0–100.0%
0.0%
P10.29
Running time of step 13
0.0–6553.5s   (min)
0.0s
P10.30
Multi-step speed 14
-100.0–100.0%
0.0%
P10.31
Running time of step 14
0.0–6553.5s   (min)
0.0s
P10.32
Multi-step speed 15
-100.0–100.0%
0.0%
P10.33
Running time of step 15
0.0–6553.5s   (min)
0.0s
P10.34
ACC/DEC time of steps 0–7 of simple PLC
0x0000–0XFFFF
0000
P10.35
ACC/DEC time of steps 8–15 of simple PLC
0x0000–0XFFFF
0000
P10.36
PLC restart mode
0: Restart from step 1
1:   Resume from the paused step
P17.00
Set frequency
0.00Hz–P00.03 (Max. output frequency)
0.00Hz
P17.27
Simple   PLC and present stage number of multi-step speed
Displays the present stage of the simple   PLC function.
5.5.14  Multi-step speed running
The VFD can set 16-step speeds, which are selectable by multi-step speed terminals 1–4, corresponding to multi-step speed 0 to multi-step speed 15.
Function code
Description
Default
P05.01P05.06
20: Pause multi-step speed running
P10.02
Multi-step speed 0
-100.0–100.0%
0.0%
P10.03
0.0–6553.5s   (min)
0.0s
P10.04
Multi-step speed 1
-100.0–100.0%
0.0%
P10.05
0.0–6553.5s   (min)
0.0s
P10.06
Multi-step speed 2
-100.0–100.0%
0.0%
P10.07
0.0–6553.5s   (min)
0.0s
P10.08
Multi-step speed 3
-100.0–100.0%
0.0%
P10.09
0.0–6553.5s   (min)
0.0s
P10.10
Multi-step speed 4
-100.0–100.0%
0.0%
P10.11
0.0–6553.5s   (min)
0.0s
P10.12
Multi-step speed 5
-100.0–100.0%
0.0%
P10.13
0.0–6553.5s   (min)
0.0s
P10.14
Multi-step speed 6
-100.0–100.0%
0.0%
P10.15
0.0–6553.5s   (min)
0.0s
P10.16
Multi-step speed 7
-100.0–100.0%
0.0%
P10.17
0.0–6553.5s   (min)
0.0s
P10.18
Multi-step speed 8
-100.0–100.0%
0.0%
P10.19
0.0–6553.5s   (min)
0.0s
P10.20
Multi-step speed 9
-100.0–100.0%
0.0%
P10.21
0.0–6553.5s   (min)
0.0s
P10.22
Multi-step speed 10
-100.0–100.0%
0.0%
P10.23
0.0–6553.5s   (min)
0.0s
P10.24
Multi-step speed 11
-100.0–100.0%
0.0%
P10.25
0.0–6553.5s   (min)
0.0s
P10.26
Multi-step speed 12
-100.0–100.0%
0.0%
P10.27
0.0–6553.5s   (min)
0.0s
P10.28
Multi-step speed 13
-100.0–100.0%
0.0%
P10.29
0.0–6553.5s   (min)
0.0s
P10.30
Multi-step speed 14
-100.0–100.0%
0.0%
P10.31
0.0–6553.5s   (min)
0.0s
P10.32
Multi-step speed 15
-100.0–100.0%
0.0%
P10.33
0.0–6553.5s   (min)
0.0s
P10.34
0x0000–0XFFFF
0000
P10.35
0x0000–0XFFFF
0000
P17.27
5.5.15 PID control
PID control, a common mode for process control, is mainly used to adjust the VFD output frequency or output voltage through performing scale-division, integral and differential operations on the difference between feedback signal of controlled variables and signal of the target, thus forming a negative feedback system to keep the controlled variables above the target. It is suitable for flow control, pressure control, temperature control, etc. Diagram of basic principles for output frequency regulation is shown in the figure below.
Introduction to the working principles and control methods for PID control
Proportional control (Kp): When the feedback deviates from the reference, the output will be proportional to the deviation, if such deviation is constant, the regulating variable will also be constant. Proportional control can respond to feedback changes rapidly, however, it cannot eliminate the error by itself. The larger the proportional gain, the faster the regulating speed, but too large gain will result in oscillation. To solve this problem, first, set the integral time to a large value and the derivative time to 0, and run the system by proportional control, and then change the reference to observe the deviation between feedback signal and the reference (static difference), if the static difference is (e.g., increase the reference, and the feedback variable is always less than the reference after system stabilizes), continue increasing the proportional gain, otherwise, decrease the proportional gain; repeat such process until the static error becomes small.
Integral time (Ti): When feedback deviates from reference, the output regulating variable accumulates continuously, if the deviation persists, the regulating variable will increase continuously until deviation disappears. Integral regulator can be used to eliminate static difference; however, too large regulation may lead to repetitive overshoot, which will cause system instability and oscillation. The feature of oscillation caused by strong integral effect is that the feedback signal fluctuates up and down based on the reference variable, and fluctuation range increases gradually until oscillation occurred. Integral time parameter is generally regulated gradually from large to small until the stabilized system speed fulfills the requirement.
Derivative time (Td): When the deviation between feedback and reference changes, output the regulating variable which is proportional to the deviation variation rate, and this regulating variable is only related to the direction and magnitude of the deviation variation rather than the direction and magnitude of the deviation itself. Differential control is used to control the feedback signal variation based on the variation trend. Differential regulator should be used with caution as it may easily enlarge the system interferences, especially those with high variation frequency.
When the frequency command selection (P00.06, P00.07) is 7 or the voltage setting channel selection (P04.27) is 6, the VFD is process PID controlled.
5.5.15.1 General procedures for PID parameter settings
a. Determining proportional gain P
When determining proportional gain P, first, remove the integral term and derivative term of PID by making Ti=0 and Td=0 (see PID parameter setup for details), thus turning PID into pure proportional control. Set the input to 60%–70% of the max. allowable value, and increase proportional gain P gradually from 0 until system oscillation occurred, and then in turn, decrease proportional gain P gradually from current value until system oscillation disappears, record the proportional gain P at this point and set the proportional gain P of PID to 60%–70% of current value. This is whole commissioning process of proportional gain P.
b. Determine integral time Ti
After proportional gain P is determined, set the initial value of a larger integral time Ti, and decrease Ti gradually until system oscillation occurred, and then in turn, increase Ti until system oscillation disappears, record the Ti at this point, and set the integral time constant Ti of PID to 150%–180% of current value. This is the commissioning process of integral time constant Ti.
c. Determining derivative time Td
The derivative time Td is generally set to 0.
If you need to set Td to another value, set in the same way with P and Ti, namely set Td to 30% of the value when there is no oscillation.
d. Empty system load, perform load-carrying joint debugging, and then fine-tune PID parameter until fulfilling the requirement.
5.5.15.2 PID adjusting methods
After setting the parameters controlled by PID, you can adjust these parameters by the following means.
Control overshoot: When overshoot occurred, shorten the derivative time (Td) and prolong integral time (Ti).
Stabilize the feedback value as fast as possible:  when overshoot occurred, shorten integral time (Ti) and prolong derivative time (Td) to stabilize control as fast as possible.
Control long-term vibration:  If the cycle of periodic vibration is longer than the set value of integral time (Ti), it indicates the integral action is too strong, prolong the integral time (Ti) to control vibration.
Control short-term vibration: If the vibration cycle is short is almost the same with the set value of derivative time (Td), it indicates derivative action is too strong, shorten the derivative time (Td) to control vibration. When derivative time (Td) is set to 0.00 (namely no derivative control), and there is no way to control vibration, decrease the proportional gain.
Function code
Description
Default
P09.00
PID reference source
0: Keypad   (P09.01)
1: AI1
2: AI2
3: AI3
4:   High-speed pulse HDIA
5: Multi-step   running
6:   Modbus/Modbus TCP communication
7: PROFIBUS/CANopen/DevicneNET   communication
8:   Ethernet communication
9:   High-speed pulse HDIB communication
10:   EtherCat/Profinet/EtherNetIP communication
11:   Programmable expansion card
12:   Reserved
P09.01
PID reference preset through keypad
-100.0%–100.0%
0.0%
P09.02
PID feedback source
0: AI1
1: AI2
2: AI3
3: High-speed pulse HDIA
4: Modbus/Modbus TCP communication
5:   PROFIBUS/CANopen/DevicneNET communication
6:   Ethernet communication
7: High-speed   pulse HDIB
8:   EtherCat/Profinet/EtherNetIP communication
9:   Programmable expansion card
10:   Reserved
P09.03
PID output characteristics selection
0: PID output is   positive characteristic
1: PID output is negative characteristic
P09.04
Proportional gain (Kp)
0.00–100.00
1.80
P09.05
Integral time (Ti)
0.01–10.00s
0.90s
P09.06
Differential time (Td)
0.00–10.00s
0.00s
P09.07
Sampling period (T)
0.000–10.000s
0.100s
P09.08
PID control deviation limit
0.0–100.0%
0.0%
P09.09
PID output upper limit
P09.10–100.0% (max. frequency or voltage)
100.0%
P09.10
PID output lower limit
-100.0%–P09.09 (max. frequency or voltage)
0.0%
P09.11
Feedback offline detection value
0.0–100.0%
0.0%
P09.12
Feedback offline detection time
0.0–3600.0s
1.0s
P09.13
PID control   selection
0x0000–0x1111
Ones place:
0: Continue integral control after the frequency reaches upper/lower   limit
1: Stop integral control after the frequency reaches upper/lower limit
Tens place:
0: The same with the main reference direction
1: Contrary to the main reference direction
Hundreds place:
0: Limit as per the max. frequency
1: Limit as per A frequency
Thousands place:
0: A+B frequency, acceleration /deceleration of main reference A   frequency source buffering is invalid
1: A+B frequency,   acceleration/ deceleration of main reference A frequency source buffering is   valid, acceleration/deceleration is determined by P08.04 (acceleration time 4).
0x0001
P09.14
Low   frequency proportional gain (Kp)
0.00–100.00
1.00
P09.15
ACC/DEC   time of PID command
0.0–1000.0s
0.0s
P09.16
PID output filter time
0.000–10.000s
0.000s
P09.17
Reserved
-100.0–100.0%
0.0%
P09.18
Low frequency   integral time (Ti)
0.00–10.00s
0.90s
P09.19
Low   frequency differential time (Td)
0.00–10.00s
0.00s
P09.20
Low   frequency point for PID parameter switching
0.00–P09.21
5.00Hz
P09.21
High   frequency point for PID parameter switching
P09.20–P00.04
10.00Hz
P17.00
Set frequency
0.00Hz
P17.23
PID reference value
-100.0–100.0%
0.0%
P17.24
PID feedback value
-100.0–100.0%
0.0%
5.5.16 Running at wobbling frequency
Wobbling frequency is mainly applied in cases where transverse movement and winding functions are needed like textile and chemical fiber industries. The typical working process is shown as below.
Function code
Description
Default
P00.03
P00.03–400.00Hz
50.00Hz
P00.06
Setting channel of A frequency command
0:   Keypad
1: AI1
2: AI2
3: AI3
5:   Simple PLC program
6:   Multi-step speed running
7: PID   control
8:   Modbus/Modbus TCP communication
9: PROFIBUS/CANopen/DeviceNet   communication
10:   Ethernet communication
11:   High-speed pulse HDIB
12:   Pulse train AB
13:   EtherCat/Profinet/EtherNetIP communication
14:   Programmable expansion card
P00.11
ACC   time 1
0.0–3600.0s
Model depended
P00.12
DEC   time 1
0.0–3600.0s
Model depended
P05.01P05.06
26: Wobbling frequency pause (stop at current frequency)
27: Wobbling frequency reset (revert to center frequency)
P08.15
Amplitude of wobbling frequency
0.0–100.0% (relative   to set frequency)
0.0%
P08.16
Amplitude of jump frequency
0.0–50.0% (relative   to amplitude of wobbling frequency)
0.0%
P08.17
Wobbling frequency rise time
0.1–3600.0s
5.0s
P08.18
Wobbling frequency fall time
0.1–3600.0s
5.0s
5.5.17 Local encoder input
The VFD supports pulse count function by inputting the count pulse from HDI high-speed pulse port. When the actual count value is no less than the set value, digital output terminal will output count-value-reached pulse signal, and the corresponding count value will be zeroed out.
Function code
Description
Default
P05.00
HDI input type
0x00–0x11
0x00
P05.38
HDIA high-speed pulse input function
0: Set input via frequency
1: Reserved
2: Input via encoder, used in combination with HDIB
P05.44
HDIB high-speed pulse input function selection
1: Reserved
2: Input via encoder, used in combination with HDIA
P18.00
Actual frequency of encoder
-999.9–3276.7Hz
0.0Hz
P20.15
Speed measurement mode
0: PG card
1: Local; realized   by HDIA and HDIB; supports incremental 24V encoder only
5.5.18 Commissioning procedures for closed-loop control, position control and spindle positioning
1. Commissioning procedures for closed-loop vector control of asynchronous motor
Step 1: Restore to default value via keypad
Step 2: Set P00.03, P00.04 and P02 group motor nameplate parameters
Step 3: Motor parameter autotuning
Carry out rotary parameter autotuning or static parameter autotuning via keypad, if the motor can be disconnected from load, then it is users can carry out rotary parameter autotuning; otherwise, carry out static parameter autotuning, the parameter obtained from autotuning will be saved in P02 motor parameter group automatically.
Step 4: Verify whether the encoder is installed and set properly
a) Confirm the encoder direction and parameter setup
Set P20.01 (encoder pulse-per-revolution), set P00.00=2 and P00.10=20Hz, and run the VFD, at this point, the motor rotates at 20Hz, observe whether the speed measurement value of P18.00 is correct, if the value is negative, it indicates the encoder direction is reversed, under such situation, set P20.02 to 1; if the speed measurement value deviates greatly, it indicates P20.01 is set improperly. Observe whether P18.02 (encoder Z pulse count value) fluctuates, if yes, it indicates the encoder suffers interference or P20.01 is set improperly, requiring users to check the wiring and the shielding layer.
b) Determine Z pulse direction
Set P00.10=20Hz, and set P00.13 (running direction) to forward and reverse direction respectively to observe whether the difference value of P18.02 is less than 5, if the difference value remains to be larger than 5 after setting Z pulse reversal function of P20.02, power off and exchange phase A and phase B of the encoder, and then observe the difference between the value of P18.02 during forward and reverse rotation. Z pulse direction only affects the forward/reverse positioning precision of the spindle positioning carried out with Z pulse.
Step 5: Closed-loop vector pilot-run
Set P00.00=3, and carry out closed-loop vector control, adjust P00.10 and speed loop and current loop PI parameter in P03 group to make it run stably in the whole range.
Step 6: Flux-weakening control
Set flux-weakening regulator gain P03.26=0–8000, and observe the flux-weakening control effect. P03.22P03.24 can be adjusted as needed.
2. Commissioning procedures for closed-loop vector control of synchronous motor
Step 1: Set P00.18=1, restore to default value
Step 2: Set P00.00=3 (FVC), set P00.03, P00.04, and motor nameplate parameters in P02 group.
Step 3: Set P20.01 encoder parameter.
When the encoder is resolver-type encoder, set the encoder pulse count value to (resolver pole pair number × 1024), e.g., if pole pair number is 4, set P20.01 to 4096.
Step 4: Ensure the encoder is installed and set correctly
When motor stops, observe whether P18.21 (resolver angle) fluctuates, if it fluctuates sharply, check the wiring and grounding. Rotates the motor slowly, observe whether P18.21 changes accordingly. If yes, it indicates motor is connected correctly; if the value of P18.02 keeps constant at a non-zero value after rotating for multiple circles, it indicates encoder Z signal is correct.
Step 5: Autotuning of initial position of magnetic pole
Set P20.11=2 or 3 (3: rotary autotuning; 2: static autotuning), press RUN key to run the VFD.
a) Rotary autotuning (P20.11 = 3)
Detect the position of current magnetic pole when autotuning starts, and then accelerates to 10Hz, autotuning corresponding magnetic pole position of encoder Z pulse, and decelerate to stop.
During running, if ENC1O or ENC1D fault occurred, set P20.02=1 and carry out autotuning again.
After autotuning is done, the angle obtained from autotuning will be saved in P20.09 and P20.10 automatically.
b) Static autotuning
In cases where the load can be disconnected, it is recommended to adopt rotary autotuning (P20.11=3) as it has high angle precision. If the load cannot be disconnected, users can adopt static autotuning (P20.11=2). The magnetic pole position obtained from autotuning will be saved in P20.09 and P20.10.
Step 6: Closed-loop vector pilot-run
Adjust P00.10 and speed loop and current loop PI parameter in P03 group to make it run stably in the whole range. If oscillation occurred, reduce the value of P03.00, P03.03, P03.09 and P03.10. If current oscillation noise occurred during low speed, adjust P20.05.
Note: It is necessary to re-determine P20.02 (encoder direction) and carry out magnetic pole position autotuning again if the wiring of motor or encoder is changed.
3. Commissioning procedures for pulse string control
Pulse input is operated based on closed-loop vector control; speed detection is needed in the subsequent spindle positioning, zeroing operation and division operation.
Step 1: Restore to default value by keypad
Step 2: Set P00.03, P00.04 and motor nameplate parameters in P02 group
Step 3: Motor parameter autotuning: rotary parameter autotuning or static parameter autotuning
Step 4: Verity the installation and settings of encoder. Set P00.00=3 and P00.10=20Hz to run the system, and check the control effect and performance of the system.
Step 5: Set P21.00=0001 to set positioning mode to position control, namely pulse-string control. There are four kinds of pulse command modes, which can be set by P21.01 (pulse command mode).
Under position control mode, you can check high-order bit and low-order bit of position reference and feedback, P18.02 (count value of Z pulse), P18.00 (actual frequency of encoder), P18.17 (pulse command frequency) and P18.19 (position regulator output) via P18, through which users can figure out the relation between P18.08 (position of position reference point) and P18.02, pulse command frequency P18.17, feedforward P18.18 and position regulator output P18.19.
Step 6: The position regulator has two gains, namelyP21.02 and P21.03, and they can be switched by speed command, torque command and terminals.
Step 7: When P21.08 (output limit of position controller) is set to 0, the position control will be invalid, and at this point, the pulse string acts as frequency source, P21.13 (position feedforward gain) should be set to 100%, and the speed acceleration/deceleration time is determined by the acceleration /deceleration time of pulse string, the pulse string acceleration/deceleration time of the system can be adjusted. If the pulse string acts as the frequency source in speed control, users can also set P21.00 to 0000, and set the frequency source reference P00.06 or P00.07 to 12 (set by pulse string AB), at this point, the acceleration/deceleration time is determined by the acceleration/deceleration time of the VFD, meanwhile, the parameters of pulse string AB is still set by P21 group. In speed mode, the filter time of pulse string AB is determined by P21.29.
Step 8: The input frequency of pulse string is the same with the feedback frequency of encoder pulse, the relation between them can be changed by altering P21.11 (numerator of position command ratio) and P21.12 (denominator of position command ratio)
Step 9: When running command or servo enabling is valid (by setting P21.00 or terminal function 63), it will enter pulse string servo running mode.
4. Commissioning procedures for spindle positioning
Spindle orientation is to realize orientation functions like zeroing and division based on closed-loop vector control
Step 1–4: These four steps are the same with the first four steps of the commissioning procedures for closed-loop vector control, which aim to fulfill the control requirements of closed-loop vector control, thus realizing spindle positioning function in either position control or speed control mode.
Step 5: Set P22.00.bit0=1 to enable spindle positioning, set P22.00.bit1 to select spindle zero input. If the system adopts encoder for speed measurement, set P22.00.bit1 to 0 to select Z pulse input; if the system adopts photoelectric switch for speed measurement, set P22.00.bit1 to 1 to select photoelectric switch as zero input; set P22.00.bit2 to select zero search mode, set P22.00.bit3 to enable or disable zero calibration, and select zero calibration mode by setting P22.00.bit7.
Step 6: Spindle zeroing operation
a) Select the positioning direction by setting P22.00.bit4.
b) There are four zero positions in P22 group, users can choose one out of four zeroing positions by setting zeroing input terminal selection (46, 47) in P05 group. When executing zeroing function, the motor will stop accurately at corresponding zeroing position according to the set positioning direction, which can be viewed via P18.10.
c) The positioning length of spindle zeroing is determined by the deceleration time of accurate-stop and the speed of accurate-stop.
Step 7: Spindle division operation
There are seven scale-division positions in P22 group, users can choose one out of seven scale-division positions by setting scale-division input terminal selection (48, 49, 50) in P05 group. Enable corresponding scale-division terminal after the motor stops accurately, and the motor will check the scale-division position state and switch to corresponding position incrementally, at this point, users can check P18.09.
Step 8: Priority level of speed control, position control and zeroing
The priority level of speed running is higher than that of the scale division, when the system runs in scale-division mode, if spindle orientation is prohibited, the motor will turn to speed mode or position mode.
The priority level of zeroing is higher than that of the scale division.
Scale-division command is valid when the scale-division terminal is from 000 state to non-000 state, e.g., in 000–011, the spindle executes scale division 3. The transition time during terminal switchover needs to be less than 10ms; otherwise, wrong scale division command may be executed.
Step 9: Hold positioning
The position loop gain during positioning is P21.03; while the position loop gain in positioning-completion-hold state is P21.02. In order to keep sufficient position-hold force and ensure no system oscillation occurred, adjust P03.00, P03.01, P20.05, and P21.02.
Step 10: Positioning command selection (bit6 of P22.00)
Electric level signal: Positioning command (zeroing and scale division) can be executed only when there is running command or the servo is enabled.
Step 11: Spindle reference point selection (bit0 of P22.00)
Encoder Z pulse positioning supports the following spindle positioning modes:
a) The encoder is installed on the motor shaft, the motor shaft and spindle is 1:1 rigid connection;
b) The encoder is installed on the motor shaft, the motor shaft and spindle is 1:1 belt connection;
At this point, the belt may slip during high-speed running and cause inaccurate positioning, it is recommended to install proximity switch on the spindle.
c) The encoder is installed on the spindle, and the motor shaft is connected to the spindle with belt, the drive ratio is not necessarily 1:1.
At this point, set P20.06 (speed ratio of the mounting shaft between motor and encoder), and set P22.14 (spindle drive ratio) to 1. As the encoder is not installed on the motor, the control performance of closed-loop vector will be affected.
Proximity switch positioning supports the following spindle positioning modes:
a) The encoder is installed on the motor shaft, the drive ratio between motor shaft and spindle is not necessarily 1:1;
At this point, it is required to set P22.14 (spindle drive ratio).
5. Commissioning procedures for digital positioning
The diagram for digital positioning is shown below.
Step 1–4: These four steps are the same with the first four steps of the commissioning procedures for closed-loop vector control, which aim to fulfill the control requirements of closed-loop vector control.
Step 5: Set P21.00=0011 to enable digital positioning. Set P21.17, P21.11 and P21.12 (set positioning displacement) according to actual needs; set P21.18 and P21.19 (set positioning speed); set P21.20 and P21.21 (set acceleration/deceleration time of positioning).
Step 6: Single positioning operation
Set P21.16.bit1=0, and the motor will carry out single positioning action and stay in the positioning position according to the setup in step 5.
Step 7: Cyclic positioning operation
Set P21.16.bit1=1 to enable cyclic positioning. The cyclic positioning is divided into continuous mode and repetitive mode; users can also carry out cyclic positioning through terminal function (no. 55, enable digital positioning cycle)
6. Commissioning procedures for positioning of photoelectric switch
Photoelectric switch positioning is to realize positioning function based on closed-loop vector control.
Step 5: Set P21.00=0021 to enable photoelectric switch positioning, the photoelectric switch signal can be connected to S8 terminal only, and set P05.08=43, meanwhile, set P21.17, P21.11 and P21.12 (set positioning displacement) based on actual needs; set P21.21 (deceleration time of positioning), however, when present running speed is too fast or the set positioning displacement is too small, the deceleration time of positioning will be invalid, and it will enter direct deceleration positioning mode.
Step 6: Cyclic positioning
After positioning is done, the motor will stay in current position. Users can set cyclic positioning through input terminal function selection (55: enable cyclic digital positioning) in P05 group; when the terminal receives cyclic positioning enable signal (pulse signal), the motor will continue running in the set speed as per the speed mode and re-enter positioning state after encountering photoelectric switch.
(7) Hold positioning