4.4.1 Wiring diagram of basic control circuit

image.png

Figure 4–12 Wiring diagram of control circuit

Note: If wire-passing board outlet space is insufficient when all terminals on the control board are wired, cut the knock-out hole on the lower cover for wire outlet. If a dangerous situation occurs when the knock-out hole is cut for a purpose but not wire outlet, we will not bear any responsibility.

Terminal    name

Instruction

+10V

The VFD provides +10.5V power

AI1

1. Input range: AI1 voltage/current can choose 0–10/   0–20mA; AI2: -10V–+10V voltage;

2. Input impedance: 20kΩ during voltage input; 250Ω during   current input;

3. AI1 voltage or current input is set by P05.50;

4. Resolution   ratio: When 10V corresponds to 50Hz, the min. resolution ratio is 5mV;

5. 25°C,   When input above 5V or 10mA, the error is ±0.5%

AI2

GND

+10.5V reference zero potential

AO1

1. Output range: 0–10V voltage or 0–20mA current

2. Voltage or current output is set by toggle switch SW2;

3. 25°C, when input   above 5V or 10mA, the error is ±0.5%.

RO1A

RO1 relay output; RO1A is NO, RO1B is NC, RO1C is   common port

Contact capacity: 3A/AC250V, 1A/DC30V

RO1B

RO1C

RO2A

RO2 relay output; RO2A is NO, RO2B is NC, RO2C is common port

Contact capacity: 3A/AC250V, 1A/DC30V

RO2B

RO2C

HDO

1. Switch capacity: 50mA/30V;  

2. Range of output   frequency: 0–50kHz

3. Duty ratio: 50%

COM

Common port of +24V

CME

Common port of open collector output; short connected   to COM by default

Y1

1. Switch capacity: 50mA/30V;

2. Range of output frequency: 0–1kHz

485+

485 communication port, 485 differential signal port   and standard 485 communication interface should use twisted shielded pair;   the 120ohm terminal matching resistor of 485 communication is connected by   toggle switch SW3.

485-

PE

Grounding terminal

PW

Provide input digital working power from external to internal;

Voltage range: 12–30V

24V

The VFD provides user power; the max. output current is   200mA

COM

Common port of +24V

S1

Digital input 1

1. Internal impedance: 3.3kΩ

2. Accept   12–30V voltage input

3. This   terminal is bi-directional input terminal and supports NPN/PNP connection   modes

4. Max.   input frequency: 1kHz

5. All are   programmable digital input terminals, users can set the terminal function via   function codes

S2

Digital input 2

S3

Digital input 3

S4

Digital input 4

HDIA

Besides S1–S4 functions, it can also act as high frequency pulse input   channel

Max. input frequency: 50kHz;

Duty ratio: 30%–70%;

Supports the input of a quadrature encoder with 24V   power supply; equipped with speed-measurement function

HDIB

+24V—H1

STO input 1

1. Safe   torque off (STO) redundant input, connect to external NC contact, STO acts   when the contact opens, and the VFD stops output;

2. Safety input signal wires use shielded wire whose   length is within 25m;

3. H1 and H2 terminals are short connected to +24V by default;   it is required to remove the short-contact tag on the terminal before using   STO function.

+24V—H2

STO input 2

 

4.4.2 Input/output signal connection diagram

Set NPN /PNP mode and internal/external power via U-type short-contact tag. NPN internal mode is adopted by default.

image.png

Figure 4–13 Position of U-type short-contact tag

If input signal comes from NPN transistors, set the U-type short-contact tag between +24V and PW based on the power used according to the figure below.

image.png

Figure 4–14 NPN mode

If input signal comes from PNP transistor, set the U-type short-contact tag based on the power used according to the figure below.

image.png

Figure 4–15 PNP mode


上一章节 下一章节