The terminals are arranged as follows:
CME and COM are shorted through J3 before delivery, and J5 is the jumper for selecting the output type (voltage or current) of AO2.
AI3
AO2
GND
COM
CME
Y2
S5
RO3A
RO3B
RO3C
PW
+24V
S6
S7
S8
RO4A
RO4C
Indicator definition
Indicator No.
Definition
Function
LED1
State indicator
This indicator is on when the extension card is establishing a connection with the control board; it blinks periodically after the extension card is properly connected to the control board (the period is 1s, on for 0.5s, and off for the other 0.5s); and it is off when the extension card is disconnected from the control board.
LED4
Power indicator
This indicator is on after the IO extension card is powered on by the control board.
The EC-IO501-00 extension card can be used in scenarios where the I/O interfaces of a Goodrive350 IP54 high-ingress protection series VFD cannot meet the application requirements. It can provide 4 digital inputs, 1 digital output, 1 analog input, 1 analog output, and two relay outputs. It is user-friendly, providing relay outputs through European-type screw terminals and other inputs and outputs through spring terminals.
EC-IO501-00 terminal function description
Category
Label
Function description
Power
PW
External power supply
The working power of digital input is provided by an external power supply.
Voltage range: 12–30 V
The terminals PW and +24V are shorted before delivery.
Analog input/output
AI3—GND
Analog input 1
1. Input range: 0–10 V, 0–20 mA
2. Input impedance: 20 kΩ for voltage input; 250 Ω for current input
3. Set it to be voltage or current input through the corresponding function code.
4. Resolution: When 10 V corresponds to 50 Hz, the minimum resolution is 5 mV.
5. Deviation:±0.5%; input of 5 V or 10 mA or higher at the temperature of 25°C
AO2—GND
Analog output 1
1. Output range: 0–10 V, 0–20 mA
2. Whether it is voltage or current output is determined by J5.
3. Deviation ±0.5%; input of 5 V or 10 mA or higher at the temperature of 25°C
Digital input/output
S5—COM
Digital input 1
1. Internal impedance: 3.3 kΩ
2. Power input range: 12–30 V
3. Bidirectional input terminal
4. Max. input frequency: 1 kHz
S6—COM
Digital input 2
S7—COM
Digital input 3
S8—COM
Digital input 4
Y2—CME
Digital output
1. Switch capacity: 50mA/30 V
2. Output frequency range: 0–1 kHz
3. The terminals CME and COM are shorted through J3 before delivery.
Relay output
RO3A
NO contact of relay 3
1. Contact capacity: 3A/AC 250 V, 1 A/DC 30 V
2. Do not use them as high-frequency digital outputs.
RO3B
NC contact of relay 3
RO3C
Common contact of relay 3
RO4A
NO contact of relay 4
RO4C
Common contact of relay 4