4.5.1 Protecting the VFD and input power cable in short-circuit situations
Protect the VFD and input power cable in short circuit situations and against thermal overload.
Arrange the protection according to the following guidelines.
Fig 4-25 Fuse configuration
Note: Select the fuse as the manual indicated. The fuse will protect the input power cable from damage in short-circuit situations. It will protect the surrounding devices when the internal of the VFD is short circuited.
4.5.2 Protecting the motor and motor cable in short-circuit situations
The VFD protects the motor and motor cable in a short-circuit situation when the motor cable is dimensioned according to the rated current of the VFD. No additional protection devices are needed.
If the VFD is connected to multiple motors, a   separate thermal overload switch or a circuit breaker must be used for   protecting each cable and motor. These devices may require a separate fuse to   cut off the short-circuit current.
4.5.3 Protecting the motor against thermal overload
According to regulations, the motor must be protected against thermal overload and the current must be switched off when overload is detected. The VFD includes a motor thermal protection function that protects the motor and closes the output to switch off the current when necessary.
4.5.4 Implementing a bypass connection
It is necessary to set power frequency and variable frequency conversion circuits for the assurance of continuous normal work of the VFD if faults occur in some significant situations.
In some special situations, for example, if it is only used in soft start, the VFD can be converted into power frequency running after starting and some corresponding bypass should be added.
Never connect the supply power to the VFD output   terminals U, V and W. Power line voltage applied to the output can result in   permanent damage to the VFD.
If frequent shifting is required, employ mechanically connected switches or contactors to ensure that the motor terminals are not connected to AC power line and VFD output terminals simultaneously.