4.4.1 Wiring diagram of basic control circuit
Figure 4‑20 Wiring of control circuit
Terminalname
Description
+10V
Local   power supply +10 V
AI1
1. Input   range: AI1/AI2 voltage and current can be chosen: 0–10 V/0–20mA; AI1 can be   shifted by J3 while AI2 can be shifted by J4; AI3: -10 V–+10 V
2. Input   impedance: voltage input: 20kΩ; current input: 500Ω
3.   Resolution: the minimum one is 5m V when 10 V corresponds to 50 Hz
4.   Deviation ±1%, 25°C
AI2
AI3
GND
+10 V   reference null potential
AO1
1. Output   range: 0–10 V or -20–20mA; The voltage or the current output is depended on   the jumper. AO1 is switched by J1 and AO2 is switched by J2
2.   Deviation±1%, 25°C
AO2
Terminalname
Description
RO1A
RO1 relay output; RO1A is NO, RO1B is NC,   RO1C is common port
Contact capacity: 3A/AC250V, 1A/DC30V
RO1B
RO1C
RO2A
RO2 relay output; RO2A is NO, RO2B is NC, RO2C is   common port
RO2B
RO2C
Terminalname
Description
HDO
1. Switch   capacity: 200mA/30V;
2. Range   of output frequency: 0–50kHz
COM
Common   port of +24V
CME
Common   port of open collector output
Y
2. Range   of output frequency: 0–1kHz
485+
For 485   communication port, 485 differential signal port and standard 485   communication interfaces, use twisted pairs or shielded cables.
485-
Terminalname
Description
PE
Grounding   terminal
PW
Provide   input digital working power from external to internal;
Voltage   range: 12–30V
24V
The VFD provides user power; the maximum output current   is 200mA
COM
Common port of +24V
S1
Digital input 1
1. Internal   impedance: 3.3kΩ
2. Accept   12–30V voltage input
3. This   terminal is bi-directional input terminal and supports NPN/PNP connection   modes
4. Max.   input frequency: 1kHz
5. All   are programmable digital input terminals, and users can set the terminal   function via function codes
S2
Digital input 2
S3
Digital input 3
S4
Digital input 4
S5
Digital input 5
S6
Digital input 6
S7
Digital input 7
S8
Digital input 8
HDI
Besides   S1–S8 functions, it can also act as high frequency pulse input channel
Max.   input frequency: 50kHz
4.4.2 C1 terminal (EC-PG301-24) instruction and the wiring diagram
4.4.2.1 Terminal arrangement
4.4.2.2 Terminal instruction
Terminal name
Instruction
+24 V
Encoder   power supply.
It can provide   power supply of 24 V, 200 mA.
A+, A-, B+, B-, Z+, Z-
Support   encoder signal differential, push-pull, and open collector input.
COM1
Power   supply ground of the encoder
Note: Refer to section 4.4.1 for detailed information of AO1, AO2, AI1, AI2, 485 and other terminals.
4.4.2.3 Wiring diagram
4.4.3 D1 terminal (EC-PG304-05) instruction and the wiring diagram
4.4.3.1 Terminal arrangement
4.4.3.2 Terminal instruction
Terminal    name
Instruction
EXC+EXC-
Exciting   signal of 10k Hz, and max. output current of 100 mA.
SIN+, SIN- , COS+   and COS-
Encoder   differential signal input.
A+, A-, B+, B-
Pulse reference signal, default as 5 V input.   External current-limiting resistor is needed when the input voltage is above   10 V.
AO+, AO-, BO+, BO-, ZO+, ZO-
Frequency-divided output of encoder signals, 5 V   differential signals
Frequency dividing ratio: 1:1
4.4.3.3 Wiring diagram
4.4.4 H1 terminal (EC-PG305-12) instruction and the wiring diagram
4.4.4.1 Terminal arrangement
4.4.4.2 Terminal instruction
Terminal    name
Instruction
PWR
Power   supply, provide 5 V/12 V, 200mA power supply
A1+, A1-, B1+, B1-, Z1+, Z1-
Encoder   differential, open collector, and push-pull signal input
A2+, A2-, B2+, B2-,
Support encoder differential, open collector, and   push-pull pulse reference signal. Pulse reference signal, default as 5 V   input. External current-limiting resistor is needed when the input voltage is   above 10 V
AO+, AO-, BO+, BO-,   ZO+ and ZO-
Frequency-divided output of encoder pulse signals, 5   V differential signals
COM
4.4.4.3 Wiring diagram
4.4.5 H2 terminal (EC-PG305-05) instruction and the wiring diagram
4.4.5.1 Terminal arrangement
4.4.5.2 Interfaces instruction
DB15 (CNC)
CNC system interface signal
DB15 (ENCODER)
Encoder interface signal
AO+
+5 V
AO-
A1+
3
BO+
3
B1+
4
BO-
4
Z1+
5
ZO+
5
U+
6
ZO-
6
U-
7
CME
7
V+
8
COM
8
V-
9
S7
9
GND
10
S8
10
A1-
11
A2+
11
B1-
12
A2-
12
Z1-
13
B2+
13
W+
14
B2-
14
W-
15
COM
15
4.4.5.3 Terminal instruction
Terminal name (CNC)
Instruction
A2+, A2-,   B2+, B2-
5 V differential pulse + direction reference signal,   Support 400 kHz at maximum
CME, COM
Alarm output (If use this function, it is necessary   to short-connect Y terminal to +24 V terminal, and remove the tag between CME   and COM terminal)
Terminal   name (ENCODER)
Instruction
S7
Common digital input
+5 V, GND
Encoder power supply, support 5 V±5%, 200mA power
The encoder differential input signal, support 400   kHz at maximum
U+, U-, V+,   V-, W+, W-
Difference angle input signal input of UVW encoders   (not for incremental encoders)
4.4.5.4 The wiring diagram
4.4.6 S1 terminal (EC-PG302-05) instruction
4.4.6.1 Sin/cos terminal layout
4.4.6.2 DB15 interface instruction
DB15 (upper    layer)
Pulse    reference and output interface signal
DB15 (Lower    layer)
Sin/cos    encoder interface signal
AO+
B-
AO-
Null
3
BO+
3
R+
4
BO-
4
R-
5
ZO+
5
A+
6
ZO-
6
A-
7
7
0 V
8
8
B+
9
9
5 V
10
10
C-
11
A2+
11
C+
12
A2-
12
D+
13
B2+
13
D-
14
B2-
14
Null
15
15
Null
4.4.6.3 DB15 pin function instruction
Name of   upper layer terminal (pulse reference interface)
Instruction
A2+, A2-,   B2+, B2-,
5 V   differential quadrature pulse reference signal, support 400 kHz at maximum
Name of lower   layer terminal (sin/cos encoder interface)
Instruction
+5 V, 0 V
Encoder power, can provide 5 V±5%, 200mA.
A+, A-,   B+, B-, C+,   C-, D+, D-, R+, R-
Sin/cos encoder signal input, support SINA/SINB/SINC/SIND 0.8–1.2 Vpp, SINR 0.2–0.85 Vpp, 200 kHz at   maximum
4.4.7 Input/output signal connection diagram
Use U-type tag to set the NPN/PNP mode and internal/external power sources. The default setting is NPN internal mode.
Figure 4‑21 U-shaped contact tag
If the signal is from NPN transistor, please set the U-shaped contact tag between +24 V and PW as below according to the used power supply.
Figure 4‑22 NPN modes
If the signal is from PNP transistor, please set the U-shaped contact tag as below according to the used power supply.
Figure 4‑23 PNP modes