Function code
Detailed    instruction
of parameters
Default    value
Modify
P03.00
ASR proportional gain 1
The   parameters of P03.00–P03.05 are applicable only to the vector control mode.   When the frequency is lower than P03.02 (Low-point frequency for switching),   the ASR PI parameters are P03.00 and P03.01. When the frequency is higher   than P03.05 (High-point frequency for switching), the ASR PI parameters are P03.03   and P03.04. When the frequency is between P03.02 and P03.05, the PI   parameters are obtained based on the linear change of these two groups of   parameters, as shown in the following figure.
You can   adjust the dynamic response characteristics of the automatic speed regulator   (ASR) in vector control by setting the ASR proportional gain and integral   time. Both increasing the proportional gain and decreasing the integral time   can accelerate the dynamic response of the ASR. However, if the proportional   gain is too large or the integral time is too short, system oscillation or   overadjustment may be caused. If the proportional gain is too small, system   steady-state oscillation may be easily caused, and static speed error may   also occur.
The ASR   PI parameters are closely related to the inertia of the system. The default   PI parameters need to be modified based on the characteristics of loads to   meet requirements of various scenarios.
The setting range of   P03.00: 0.0–200.0
The setting range of   P03.01: 0.000–10.000s
The setting range of   P03.02: 0.00 Hz–P03.05
The setting range of   P03.03: 0.0–200.0
The setting range of   P03.04: 0.000–10.000s
The setting range of   P03.05: P03.02–P00.03 (max. output frequency)
20.0
P03.01
ASR
integral
time 1
0.200 s
P03.02
Low-point
frequency
for
switching
5.00 Hz
P03.03
ASR proportional gain 2
20.0
P03.04
ASR
integral
 time 2
0.200 s
P03.05
High-point
frequency
for switching
10.00 Hz
P03.06
ASR
output filter
0–8 (corresponds to   0–28/10 ms)
P03.07
Compen
sation
coefficient
 of
electromotion   slip
Slip   compensation coefficient is used to adjust the slip frequency of the vector   control and improve the speed control accuracy of the system. Adjusting the   parameter properly can control the speed steady-state error.
Setting range: 50%–200%
100%
P03.08
Compen
sation
coefficient
of brake
slip
100%
P03.09
ACR
proportional
coefficient
 P
1. These two parameters adjust the PI adjustment parameter of the automatic   current regulator (ACR). They directly affect the dynamic responding speed   and control accuracy of the system. In general, you do not need to modify   their default values.
2. Applied to SVC 0   (P00.00=0) and closed-loop vector control mode only (P00.00=3)
3. The value of this   function code will be updated automatically after parameter autotuning of synchronous   motor.
Setting range: 0–20000
1000
P03.10
ACR
integral
coefficient
 I
1000
P03.11
Torque
setting
method
This parameter is   used to enable the torque control mode, and set the torque.
0: Torque control is   invalid
1: Keypad setting   torque (P03.12)
2: Analog AI1   setting torque
3: Analog AI2   setting torque
4: Analog AI3   setting torque
5: Pulse frequency   HDI setting torque
6: Multi-step torque   setting
7: Modbus   communication setting torque
8: PROFIBUS\CANopen   communication setting torque
9: Ethernet   communication setting torque
10: Reserved
Note: Setting modes 2–10,   100% corresponds to three times of the rated current of the motor.
P03.12
Keypad
setting torque
Setting range: -300.0%–300.0%   (rated current of the motor)
10.0%
P03.13
Torque
reference
 filter
time
0.000–10.000s
0.100 s
P03.14
Upper
frequency
of forward
rotation
in vector
 control
0: Keypad (P03.16   sets P03.14, P03.17 sets P03.15)
1: AI1
2: AI2
3: AI3
4: Pulse   frequency HDI setting upper-limit frequency
5: Multi-step   setting upper-limit frequency
6: Modbus   communication setting upper-limit frequency
7: PROFIBUS/CANopen   communication setting upper-limit frequency
8: Ethernet   communication setting upper-limit frequency
Note: Setting   method 0–8, 100% corresponds to the maximum frequency
P03.15
Upper
frequency
of reverse
rotation
in vector
control
P03.16
Keypad
setting
for upper
frequency
of forward
  rotation
This   function is used to set the upper limit of the frequency. P03.16 determines   the setting when P03.14=1; P03.17 determines the setting when P03.15=1.
Setting range: 0.00   Hz–P00.03 (max. output frequency)
50.00 Hz
P03.17
Keypad
setting
for upper
 frequency
of reverse
   rotation
50.00 Hz
P03.18
Upper
electromo
tion
torque
source
This function   code is used to select the electromotion and brake torque upper-limit setting   source selection.
0: Keypad   setting upper-limit frequency (P03.20 sets P03.18, P03.21 sets P03.19)
1: AI1
2: AI2
3: AI3
4: HDI
5: Modbus   communication
6:   PROFIBUS/CANopen communication
7: Ethernet   communication
Note: setting mode 1–7,100%   corresponds to three times of the motor current.
P03.19
Upper
brake
torque
source
P03.20
Keypad
setting of
 electromo
tion
torque
The function   code is used to set the limit of the torque.
Setting   range: 0.0–300.0% (motor rated current)
180.0%
P03.21
Keypad
setting
 of brake
 torque
180.0%
P03.22
Weakening
coefficient
 in constant
power
zone
The usage of AM in   weakening control.
Function code P03.22   and P03.23 are effective at constant power. The motor will enter into the   weakening state when the motor runs at rated speed. Change the weakening   curve by modifying the weakening control coefficient. The bigger the   weakening control coefficient is, the steeper the weak curve is.
The setting range of   P03.22: 0.10–2.00
The setting range of   P03.23: 5%–50%
1.00
P03.23
Lowest
weakening
point in
constant
power
zone
20%
P03.24
Max
voltage
 limit
P03.24 set the max voltage   of the VFD, which is dependent on the site situation.
The setting range: 0.0–120.0%
100.0%
P03.25
Pre-exciting time
Preactivate the motor   when the VFD starts up. Build up a magnetic field inside the VFD to improve   the torque performance during the starting process.
The setting time: 0.000–10.000s
0.000 s
P03.26
Weak proportional gain
The response characteristic of the flux weakening controller   is relative to P03.26 and P03.27. It can be adjusted properly.
Setting range: 0–8000
1200
P03.27
Integral
gain of
 the flux
 weakening
1200
P03.28
Control
mode of
 flux
weakening
0x000–0x112
Ones: Control mode selection
0: Mode 0;
1: Mode   1;
2: Mode   2
Tens: Inductance compensation selection
0: Compensate
1: Not compensate
Hundreds: High-speed control mode
0: Mode 0
1: Mode 1
0x000
P03.29
Torque
control
mode
0x0000–0x7111
Ones: Torque command selection
0: Torque reference
1: Torque current reference
Tens: Torque compensation direction at 0 speed
0: Positive
1: Negative
Hundreds: ASR integral separation   setting
0: Disabled
1: Enabled
Thousands: Torque control word setting
Bit0: Torque command filtering   mode
0: Inertia filter
1: Linear ACC/DEC filtering
Bit1–2: ACC/DEC time for rotating   speed upper limit
0: No ACC/DEC time
1: ACC/DEC time 1
2: ACC/DEC time 2
3: ACC/DEC time 3
0x0001
P03.30
Low-speed friction   torque
P03.30 is   the compensation value of low-speed (<1.0 Hz) friction torque.
P03.31 is   the compensation value of high-speed (>P03.32) friction torque. The   friction torque between low and high speed is the liner scale of P03.30 and P03.31.
Note: Torque compensation   is valid only in the torque control mode (P03.11≠0).
Setting range of P03.30:   0.0–50.0% (rated torque of the motor)
Setting range of P03.31:   0.0–50.0% (rated torque of the motor)
Setting range of P03.32:   1.00 Hz–400.00 Hz
0.0%
P03.31
High-speed friction   torque
0.0%
P03.32
Correspond
ing
 frequency
of high-
speed
friction
torque
50.00 Hz