Function code
Default    value
Modify
P04.00
Motor 1
V/F
curve
setting
These function codes define the V/F curve of Goodrive35   motor 1 to meet the need of different loads.
0: Straight line V/F curve; applying to the   constant torque load
1: Multi-dots V/F curve
2: 1.3th power low torque V/F curve
3: 1.7th power low torque V/F curve
4: 2.0th power low torque V/F curve
Curves 2–4 apply to the torque loads such as fans   and water pumps. Users can adjust according to the features of the loads to   achieve a best energy-consuming effect.
5: Customized V/F (V/F separation); on this mode,   V and F can be separated from f and f can be adjusted through the frequency   given channel set by P00.06 or the voltage given channel set by P04.27 to   change the feature of the curve.
Note: Vb in the below picture is the motor rated   voltage and fb is the motor rated frequency.
P04.01
Torque
 boost
of motor
Torque boost to the output voltage for the   features of low frequency torque. P04.01 is for the Max Output voltage   Vb.
P04.02 defines the percentage of closing frequency   of manual torque to fb.
Torque boost should be selected according to the   load. The bigger the load is, the bigger the boost is. Too big torque boost   is inappropriate because the motor will run with over-magnetic, and the   current of the VFD will increase to raise the temperature of the VFD and   decrease the efficiency.
When the torque boost is set to 0.0%, the VFD is   automatic torque boost.
Torque boost threshold: under the threshold, the   torque boost is valid, but over the threshold, the torque boost is invalid.
The setting range of P04.01: 0.0%: (automatic)   0.1%–10.0%
The setting range of P04.02: 0.0%–50.0%
0.0%
P04.02
Torque
boost
close of
motor 1
20.0%
P04.03
V/F
frequency
 1 of
motor 1
When P04.00 =1, the user can set V//F curve   through P04.03–P04.08.
V/F is   generally set according to the load of the motor.
Note: V1< V2< V3,f1<f2<f3. Too   high low frequency voltage will heat the motor excessively or cause damage.   The VFD may stall when overcurrent or overcurrent protection.
The setting range of P04.03: 0.00 Hz–P04.05
The setting range of P04.04: 0.0%–110.0%
The setting range of P04.05: P04.03–P04.07
The setting range of P04.06: 0.0%–110.0% (the rated voltage of motor 1)
The setting range of P04.07: P04.05–P02.02 (the rated frequency of   motor 1) or P04.05–P02.16 (the rated frequency of motor 1)
The setting range of P04.08: 0.0%–110.0% (the rated voltage of motor 1)
0.00 Hz
P04.04
V/F
voltage
 1 of
motor 1
0.0%
P04.05
V/F
frequency
 2 of
motor 1
0.00 Hz
P04.06
V/F
voltage 2
 of motor
0.0%
P04.07
V/F
frequency
 3 of
motor 1
0.00 Hz
P04.08
V/F
voltage
 3 of
motor 1
0.0%
P04.09
V/F slip
compensa
tion
gain of
motor 1
This function code is used to compensate the   change of the rotation speed caused by load during compensation SVPWM control   to improve the rigidity of the motor. It can be set to the rated slip   frequency of the motor which is counted as below:
△f=fb-n*p/60
Of which, fb is the rated frequency of   the motor, its function code is P02.02; n is the rated rotating speed of the   motor and its function code is P02.03; p is the pole pair of the motor.   100.0% corresponds to the rated slip frequency△f.
Setting range: 0.0–200.0%
100.0%
P04.10
Vibration
control
factor
at low
 frequency
 of motor 1
In SVPWM control mode, current fluctuation may   occur to the motor at some frequency, especially the motor with big power.   The motor cannot run stably or overcurrent may occur. These phenomena can be   canceled by adjusting this parameter.
The setting range of P04.10: 0–100
The setting range of P04.11: 0–100
The setting range of P04.12: 0.00 Hz–P00.03   (max. output frequency)
10
P04.11
Vibration
control
factor
at high
frequency
 of motor 1
10
P04.12
Vibration
control
threshold
of motor 1
30.00 Hz
P04.13
Motor
2 V/F
curve
This group of parameters defines the V/F setting   means of Goodrive35 motor 2 to meet various requirements of different loads.   See P04.00–P04.12 for the detailed function code   instruction.
Note: P04 group includes two sets of V/F parameters of   the motor which cannot display simultaneously. Only the selected V/F   parameter can be shown. The motor selection can be defined by terminals   function "the shift between motor 1 and motor 2"
P04.14
Torque
boost
of motor 2
0.0%
P04.15
Torque
boost
close of
 motor 2
20.0%
P04.16
V/F
frequency
 1 of
motor 2
0.00 Hz
P04.17
V/F
voltage
 1 of
motor 2
0.0%
P04.18
V/F
frequency
 2 of
motor 2
0.00 Hz
P04.19
V/F
voltage
 2 of
motor 2
0.0%
P04.20
V/F
frequency
 3 of
motor 2
0.00 Hz
P04.21
V/F
voltage
 3 of
motor 2
0.0%
P04.22
V/F
slip
compensa
tion
gain of
motor 2
100.0%
P04.23
Vibration
control
 factor
 at low
 frequency
 of motor
In SVPWM control   mode, current fluctuation may occur to the motor on some frequency,   especially the motor with big power. The motor cannot run stably or   overcurrent may occur. These phenomena can be canceled by adjusting this   parameter.
The setting range of P04.23: 0–100
The setting range of P04.24: 0–100
The setting range of P04.25: 0.00 Hz–P00.03   (max. output frequency)
10
P04.24
Vibration
control
 factor
at high
 frequency
 of motor
10
P04.25
Vibration
control
 threshold
of motor
30.00 Hz
P04.26
Energy-saving operation
0: No operation
1: Automatic energy-saving operation (reserved)
Motors will automatically adjust the output   voltage to save energy when light loads.
P04.27
Voltage setting
Select the output setting channel at V/F curve   separation.
0: Keypad: the output voltage is determined   by P04.28.
1: AI1 ;
2: AI2;
3: AI3;
4: HDI;
5: Multi-step speed;
6: PID;
7: Modbus communication;
8: PROFIBUS/CANopen communication;
9: Ethernet communication;
10: Reserved
Note: 100% corresponds to   the rated motor voltage.
P04.28
Keypad setting voltage
The function code is the voltage displaying when   the voltage is set through keypad.
The setting range: 0.0%–100.0%
100.0%
P04.29
Voltage increasing time
Voltage   increasing time is the time when the VFD accelerates from the output minimum   voltage to the output maximum voltage.
Voltage   decreasing time is the time when the VFD decelerates from the output maximum   voltage to the output minimum voltage.
The setting range: 0.0–3600.0s
5.0 s
P04.30
5.0 s
P04.31
Maximum output voltage
Set the upper and low limit of the output voltage.
The setting range of P04.31: P04.32–100.0%   (the rated voltage of the motor)
The setting range of P04.32: 0.0%–P04.31
100.0%
P04.32
Minimum output voltage
0.0%