Goodrive35 series VFDs support two kinds of control mode: torque control and rotation speed control. The core of rotation speed is that the whole control focuses on the stable speed and ensures the setting speed is the same as the actual running speed. The Max Load should be in the range of the torque limit. The core of torque control is that the whole control focus on the stable torque and ensures the setting torque is the same as the actual output torque. At the same time, the output frequency is among the upper limit or the lower limit.
Function    code
Default value
P00.00
Speed control mode
0: Sensorless vector control mode 1
1: Sensorless vector control mode 2
2: SVPWM   control
3: Closed-loop   vector control mode
P03.11
Torque setting method
0: Torque control is   invalid
1: Keypad setting   torque (P03.11)
2: Analog AI1   setting torque (100% corresponds to three times of the rated current of the   motor)
3: Analog AI2   setting torque (the same as above)
4: Analog AI3   setting torque (the same as above)
5: Pulse frequency   HDI setting torque (the same as above)
6: Multi-step torque   setting (the same as above)
7: Modbus   communication setting torque (the same as above)
8: PROFIBUS/CANopen   communication setting torque (the same as above)
9: Ethernet   communication setting torque (the same as above)
10: Reserved
P03.12
-300.0%–300.0% (rated current of the motor)
10.0%
P03.13
Torque reference filter time
0.000–10.000 s
0.100s
P03.14
Upper frequency of forward rotation in   vector control
0: Keypad   (P03.16)
1: AI1   (100% corresponds to max. frequency)
2: AI2   (the same as above)
3: AI3   (the same as above)
4: Pulse   frequency HDI (the same as above)
5:   Multi-step (the same as above)
6: Modbus   communication (the same as above)
7:   PROFIBUS/CANopen communication (the same as above)
8:   Ethernet communication (the same as above)
P03.15
Upper frequency of reverse rotation in   vector control
0: Keypad   (P03.17)
P03.16
Keypad setting for upper frequency of   forward rotation
0.00 Hz–P00.03 (max. output frequency)
50.00 Hz
P03.17
Keypad setting for upper frequency of   reverse rotation
50.00 Hz
P03.18
Upper electromotion torque source
0: Keypad   setting upper-limit frequency (P03.20)
1: AI1 (100%   corresponds to three times of the rated current of the motor)
4: HDI (the   same as above)
5: Modbus   communication (the same as above)
6:   PROFIBUS/CANopen communication (the same as above)
7:   Ethernet communication (the same as above)
P03.19
Upper brake torque source
0: Keypad   setting upper-limit frequency (P03.21)
P03.20
Keypad setting of electromotion torque
0.0–300.0% (rated current of   the motor)
180.0%
P03.21
Keypad setting of brake torque
180.0%
P17.09
Output torque
-250.0–250.0%
0.0%
P17.15
Torque reference
-300.0–300.0% (rated current of the motor)
0.0%