Goodrive35 series VFDs have 8 programmable digital input terminals and 1 open circuit electrode output terminal in the standard configuration. All functions of the digital input terminals are programmable by the function codes. Open collector pole input can be selected into high speed pulse input terminal or common switch input terminal by function code. When selected into HDI, the user can select HDI high speed pulse input as frequency reference, counting input or length pulse input by setting.
This parameter is used to set the function corresponds to the digital multi-function terminals.
Note: Two different multi-function terminals cannot be set as one function.
Set value
Function
Instructions
No function
The VFD does not work even there is input signal.   It is necessary to set the terminal which cannot be used to non-function to   avoid misacting.
Forward running (FWD)
The forward or reverse rotation of the VFD can be   controlled by the external terminals.
Reverse running (REV)
3
3-wire running   control
The terminal can determine the running mode of the   VFD is 3-wire control mode. Refer to P05.13 for detailed instruction of   3-wire control mode.
4
Forward jogging
See P08.06, P08.07 and P08.08 for jogging   frequency, and jogging ACC/DEC time.
5
Reverse jogging
6
Coast to stop
The VFD closes off the output. The motor is not   controlled by the VFD during the stopping. This method is usually to be used   when the load inertia is big and it has no requirement to the stopping time.
It has the same meaning with the "coast to   stop" in P01.08 and usually used in remote control.
7
Fault reset
External fault reset. It has the same function   with the reset function of STOP/RST on the keypad.   This function can realize remote fault reset.
8
Operation pause
The VFD   decelerates to stop. But all running parameters are in the memory state. For   example, PLC parameters, traverse parameters and PID parameters. After the   signal disappears, the VFD will come back to the state before stopping.
9
External fault   input
When the external fault signal is sent to the VFD,   the VFD will report the fault and stop.
10
Frequency setting   up (UP)
This parameter is used to modify the increasing   and decreasing command during the external terminal given frequency.
Frequency increasing/decreasing setting clear terminal can cancel the   assistant channel frequency set by the internal UP/DOWN of the VFD to make   the given frequency restore to the frequency given by the main given   frequency channel.
12
Frequency setting   down (DOWN)
12
13
Switch between A   setting and B setting
This function can realize the shifting between the   frequency setting channels.
The 13th function can realize the   shifting between A frequency given channel and B frequency given channel.
The 14th function can realize the   shifting between A frequency given channel and the combination setting   channel set by P00.09. The 15th function can realize the shifting   between B frequency given channel and the combination setting channel set by   P00.09.
14
Switch between A   setting and combination setting
15
Switch between B   setting and combination setting
16
Multi-step speed   terminal 1
The 16 stage speeds can be set by the combination   of digital state of four terminals.
Note: Multi-step speed 1 is the LSB; multi-step   speed 4 is the MSB.
17
Multi-step speed   terminal 2
18
Multi-step speed   terminal 3
19
Multi-step speed   terminal 4
20
Multi-step speed   pause
Shield the multi-step speed selection terminal   function to keep the setting value at the current state.
21
ACC/DEC time   selection 1
Select 4 ACC/DEC time by the combination of the 2   terminals.
22
ACC/DEC time   selection 2
23
Simple PLC stop   reset
Restart simple PLC and clear memory state of PLC.
24
Simple PLC pause
Program pause during PLC implement. Run at the   current speed stage. After cancel the function, simple PLC continues to run.
25
PID control pause
Temporal PID invalid and the VFD will output at   the current frequency.
26
Limit of forward   run
The function is valid only for forward run.
27
Limit of reverse   run
The function is valid only for reverse run.
28
Counter reset
Counter clear
29
Torque control disabling
The VFD shifts from torque control mode to speed   control mode.
30
ACC/DEC disabling
Ensure the VFD will not be affected by the external   signals (except for the stopping command) and keep the current output   frequency.
31
Counter trigging
Enable the pulse counter.
32
Length reset
Length counter clear
33
Frequency   increasing/decreasing setting temporal clear
When the terminal closes, the frequency set by UP/DOWN   can be cleared. All set frequency will be restored into the given frequency   by the frequency command channel and the frequency will come back to the   value after the frequency increasing or decreasing.
34
DC brake
The VFD   will begin DC brake after valid command.
35
Switch between   motor1 and motor2
Motor-shifting can be controlled after terminal is   valid.
36
Switch commands   to keypad
After the function terminal become valid, the   running command channel will be shifted into keypad running command channel   and the running command channel will come back to the original state if the   function terminal is invalid.
37
Switch commands   to terminals
After the function terminal become valid, the   running command channel will be shifted into terminal running command channel   and the running command channel will come back to the original state if the   function terminal is invalid.
38
Switch commands   to communication
After the function terminal become valid, the   running command channel will be shifted into communication running command   channel and the running command channel will come back to the original state   if the function terminal is invalid.
39
Pre-excitation   commands
Perform pre-exciting if the terminal is valid   until the terminal is invalid.
40
Power consumption   clear
The power   consumption will be cleared   after the command is valid.
41
Power consumption   retention
If the   command is valid, the current running of the VFD will not affect its power consumption.
42
Keypad setting of   the torque upper limit
The upper   limit is set by the keypad if the command is valid.
43
Position   reference input (only S8 valid)
If S8 is   set to 43, the external reference can be detected.
44
Spindle direction   prohibit
The   function is disabled if the command is valid.
45
Spindle returning /Local position returning
The   function is enabled if the command is valid.
46
Zero position selection 1
46 and 47   can select 4 returning positions and correspond to the returning position of P22.
47
Zero position selection 2
48
Spindle scaling   selection 1
7 scaling   selections are available through 48, 49, and 50 and correspond to the scaling   position of P22.
49
Spindle scaling   selection 2
50
Spindle scaling   selection 3
51
Switching   terminal of position control and speed control
Position control and speed control can be switched   to achieve the pulse string reference control.
52
Pulse input   disabled
Pulse input is disabled if the command is   valid.
53
Position   deviation clear
Position deviation can be cleared if the   command is valid.
54
Position proportional gain switch
Position   proportional gain can be switched.
55
Digital position cycle positioning enabled
When   command is valid, repeated positioning in the digital position mode is   available.
56
E-stop
When command   valid, the motor will stop within the time designated by P1.25.
57
Motor   overtemperature fault input
The motor   will stop when fault occurs.
58
Rigid tapping   enable
The mode   is enabled if the terminal is valid
59
Switch to SVPWM   control
If the   terminal is valid in stopping mode, it will switch to V/F control
60
Switch to FVC   control
If the   terminal is valid in stopping mode, it will switch to FVC control
61
PID pole   switching
The   terminal is used with P09.03 to switch the output pole
62
Undervoltage   stopping input
The terminal and the enabling bit is valid, the VFD   will stop at the time set by P08.05
63
Servo enabling
Under the position mode, Servo enable signal is valid,   the VFD will run into the servo mode, if there is no servo enable signal, the   VFD needs to receive the forward or reverse run command to perform the servo   operation mode.
63
Reserved
Relative parameters list:
Function    code
Default    value
P05.00
HDI input selection
0: High   pulse input
1: Digital input
P05.01
S1 terminals function
0: No function
1: Forward rotation operation
2: Reverse rotation operation
3: 3-wire control operation
4: Forward jogging
5: Reverse jogging
6: Coast to stop
7: Fault reset
8: Operation pause
9: External fault input
10: Increasing frequency setting (UP)
11: Decreasing frequency setting (DOWN)
12: Frequency setting clear
13: Shift between A setting and B setting
14: Shift between combination setting and A   setting
15: Shift between combination setting and B   setting
16: Multi-step speed terminal 1
17: Multi-step speed terminal 2
18: Multi-step speed terminal 3
19: Multi- step speed terminal 4
20: Multi- step speed pause
21: ACC/DEC time 1
22: ACC/DEC time 2
23: Simple PLC stop reset
24: Simple PLC pause
25: PID control pause
26: Limit of forward running
27: Limit of reverse running
28: Electronic gear selection
29: Torque control disabling
30: ACC/DEC disabling
31: Pulse ascending
32: Pulse descending
33: Cancel the frequency change setting   temporarily
34: DC brake
35: Shift the motor 1 into motor 2
36: Shift the command to the keypad
37: Shift the command to the terminals
38: Shift the command to the communication
39: Pre-magnetized command
40: Consumption power clear
41: Consumption power holding
42: Keypad setting of the torque upper limit
43: Position reference input (only S8 valid)
44: Spindle direction prohibit
45:   Spindle returning/local position returning
46: Zero   position selection 1
47: Zero   position selection 2
48: Spindle scaling selection 1
49: Spindle scaling selection 2
50: Spindle scaling selection 3/pulse   superposition enabling
51: Switching terminal of position control and   speed control
52: Pulse input disabled
53: Position deviation clear
54:   Position proportional gain switch
55:   Digital position cycle positioning enabled
56: E-stop
57: Motor overtemperature fault input
58: Rigid tapping enable
59: Switch to SVPWM control
60: Switch to FVC control
61: PID pole switching
62: Undervoltage stopping input
63: Servo enabling
P05.02
S2 terminals function
4
P05.03
S3 terminals function
7
P05.04
S4 terminals function
P05.05
S5 terminals function
P05.06
S6 terminals function
P05.07
S7 terminals function
P05.08
S8 terminals function
P05.09
HDI terminal function
P05.10
Polarity selection of the input terminals
0x000–0x1FF
0x000
P05.11
ON-OFF filter time
0.000–1.000 s
0.010 s
P05.12
Virtual terminals setting
0x000–0x1FF (0: Disabled, 1: Enabled)
BIT0: S1 virtual terminal
BIT1: S2 virtual terminal
BIT2: S3 virtual terminal
BIT3: S4 virtual terminal
BIT4: S5 virtual terminal
BIT5: S6 virtual terminal
BIT6: S7 virtual terminal
BIT7: S8 virtual terminal
BIT8: HDI virtual terminal
Note: After a virtual terminal is enabled, the state of the terminal can   only be modified through communication, and the communication address is   0x200A.
P05.13
Terminals control running mode
0: 2-wire control   1
1: 2-wire control   2
2: 3-wire control   1
3: 3-wire control   2
P05.14
Switch-on delay of S1
0.000–50.000   s
0.000 s
P05.15
Switch-off delay of S1
0.000–50.000   s
0.000 s
P05.16
Switch-on delay of S2
0.000–50.000   s
0.000 s
P05.17
Switch-off delay of S2
0.000–50.000   s
0.000 s
P05.18
Switch-on delay of S3
0.000–50.000   s
0.000 s
P05.19
Switch-off delay of S3
0.000–50.000   s
0.000 s
P05.20
Switch-on delay of S4
0.000–50.000   s
0.000 s
P05.21
Switch-off delay of S4
0.000–50.000   s
0.000 s
P05.22
Switch-on delay of S5
0.000–50.000   s
0.000 s
P05.23
Switch-off delay of S5
0.000–50.000   s
0.000 s
P05.24
Switch-on delay of S6
0.000–50.000   s
0.000 s
P05.25
Switch-off delay of S6
0.000–50.000   s
0.000 s
P05.26
Switch-on delay of S7
0.000–50.000   s
0.000 s
P05.27
Switch-off delay of S7
0.000–50.000   s
0.000 s
P05.28
Switch-on delay of S8
0.000–50.000   s
0.000 s
P05.29
Switch-off delay of S8
0.000–50.000   s
0.000 s
P05.30
Switch-on delay of HDI
0.000–50.000   s
0.000 s
P05.31
Switch-off delay of HDI
0.000–50.000   s
0.000 s
P07.39
Present fault input terminal state
P17.12
ON/OFF input terminals state
0000–01FF