Goodrive35 series VFDs have 2 analog output terminals (0–10 V or 0–20mA) and 1 high speed pulse output terminal. Analog output signal can be filtered and the maximum and minimum values can be adjusted. The analog output signals can be proportional to motor speed, output frequency, output current, motor torque, motor power, etc. 100% of the output current is relative to 2 times of the rated current of the VFD.
Output instructions:
Set    value
Function
Instructions
Running frequency
0–max. output   frequency
Set frequency
Ramp reference   frequency
3
Running speed
0–2 times   of the rated synchronous rotation speed of the motor
4
Output current (relative   to the VFD)
0–2 times   of rated current of the VFD
5
Output current (relative   to the motor)
6
Output voltage
0–1.5   times of the rated VFD voltage
7
Output power
0–2 times   of the rated power
8
Setting torque value
0–2 times   of rated current of the motor
9
Output torque
10
AI1
0–10 V/0–20   mA
11
AI2
0–10 V/0–20 mA
12
AI3
-10 V–10   V
13
HDI
0.00–50.00 kHz
14
Setting value 1 of Modbus communication
-1000–1000, 1000 corresponds to 100.0%
15
Setting value 2 of Modbus communication
16
Setting value 1 of PROFIBUS/CANopen communication
17
Setting value 2 of PROFIBUS/CANopen communication
-1000–1000, 100 corresponds to 100.0%
18
Setting value 1 of Ethernet communication
19
Setting value 2 of Ethernet communication
20–21
Reserved
22
Torque current (bipolar, 100% corresponds to 10 V)
0–2 times   of the rated current of the motor
23
Exciting current (100% corresponds to 10 V)
0–1 time   of the rated current of the motor
24
Setting frequency (bipolar)
25
Ramp reference frequency (bipolar)
26
Operation speed (bipolar)
27–30
Reserved
Relative parameters list:
Function    code
Default    value
P06.00
HDO   output
0: Open collector pole high speed pulse   output
1: Open collector pole output.
P06.14
AO1 output
0:   Running frequency
1: Set frequency
2: Ramps reference frequency
3: Running speed
4: Output current (relative to 2 times the   rated current of the VFD)
5: Output current   (relative to 2 times the rated current of the motor)
6: Output voltage (relative to 1.5 times   the rated voltage of the VFD)
7: Output power (relative to 2 times the rated power of the motor)
8: Set torque value (relative to 2 times   the rated torque of the motor)
9: Output torque (relative to 2 times the   rated torque of the motor)
10:   Analog AI1 input value
11:   Analog AI2 input value
12:   Analog AI3 input value
13: Input   value of high-speed pulse HDIA
14: Set   value 1 of Modbus communication
15: Set   value 2 of Modbus communication
16: Set value   1 of PROFIBUS\CANopen communication
17: Set   value 2 of PROFIBUS\CANopen communication
18: Set   value 1 of Ethernet communication
19: Set value 2 of Ethernet communication
20–21: Reserved
22: Torque current (bipolar, 100%   corresponds to 10 V)
23: Excitation current (100% corresponds to   10 V)
24: Setting frequency (bipolar)
25: Ramp reference frequency (bipolar)
26: Operation speed (bipolar)
27: Reserved
P06.15
AO2 output
P06.16
HDO high-speed pulse output
P06.17
Lower output limit of AO1
-300.0%–P06.19
0.0%
P06.18
Corresponding AO1 output of lower limit
0.00 V–10.00 V
0.00 V
P06.19
Upper output limit of AO1
P06.13–300.0%
100.0%
P06.20
Corresponding AO1 output of upper limit
0.00 V–10.00 V
10.00 V
P06.21
AO1 output filter time
0.000 s–10.000 s
0.000 s
P06.22
Lower output limit of AO2
-300.0%–P06.24
0.0%
P06.23
Corresponding AO2 output of lower limit
0.00 V–10.00 V
0.00 V
P06.24
Upper output limit of AO2
P06.18–300.0%
100.0%
P06.25
The corresponding AO2 output of upper limit
0.00 V–10.00 V
10.00 V
P06.26
AO2 output filter time
0.000 s–10.000 s
0.000 s
P06.27
Lower output limit of HDO
-300.0%–P06.29
0.0%
P06.28
Corresponding HDO output of lower limit
0.00–50.00 kHz
0.0 kHz
P06.29
Upper output limit of HDO
P06.23–300.0%
100.0%
P06.30
Corresponding HDO output of upper limit
0.00–50.00 kHz
50.00 kHz
P06.31
HDO output filter time
0.000 s–10.000 s
0.000 s