10.4.1 Command code: 03H, reading N words (continuously reading up to 16 words)
The command code 03H is used by the master to read data from the VFD. The quantity of data to be read depends on the "data quantity" in the command. A maximum of 16 pieces of data can be read. The addresses of the read parameters must be contiguous. Each piece of data occupies 2 bytes, that is, one word. The command format is presented using the hexadecimal system (a number followed by "H" indicates a hexadecimal value). One hexadecimal value occupies one byte.
The 03H command is used to read information including the parameters and operation state of the VFD.
For example, starting from the data address of 0004H, to read two contiguous pieces of data (that is, to read content from the data addresses 0004H and 0005H), the structure of the frame is described in the following table.
RTU master command (transmitted by the master to the VFD)
START
T1-T2-T3-T4 (transmission   time of 3.5 bytes)
ADDR (address)
01H
CMD (command   code)
03H
Most significant   byte (MSB) of the start address
00H
Least significant   byte (LSB) of the start address
04H
MSB of data   quantity
00H
LSB of data   quantity
02H
LSB of CRC
85H
MSB of CRC
CAH
END
The value in START and END is "T1-T2-T3-T4 (transmission time of 3.5 bytes)", indicating that the RS485 needs to stay idle for at least the transmission time of 3.5 bytes. An idle time is required to distinguish on message from another to ensure that the two messages are not regarded as one.
The value of ADDR is 01H, indicating that the command is transmitted to the VFD whose address is 01H. The ADDR information occupies one byte.
The value of CMD is 03H, indicating that the command is used to read data from the VFD. The CMD information occupies one byte.
"Start address" indicates that data reading is started from this address. It occupies two bytes, with the MSB on the left and LSB on the right.
"Data quantity" indicates the quantity of data to be read (unit: word).
The value of "Start address" is 0004H, and that of "Data quantity" is 0002H, indicating that data is to be read from the data addresses of 0004H and 0005H.
CRC check occupies two bytes, with the LSB on the left, and MSB on the right.
RTU slave response (transmitted by the VFD to the master)
START
ADDR
01H
CMD
03H
Number of bytes
04H
MSB of data in   0004H
13H
LSB of data in   0004H
88H
MSB of data in   0005H
00H
LSB of data in   0005H
00H
LSB of CRC
7EH
MSB of CRC
9DH
END
The definition of the response information is described as follows:
The value of ADDR is 01H, indicating that the message is transmitted by the VFD whose address is 01H. The ADDR information occupies one byte.
The value of CMD is 03H, indicating that the message is a response of the VFD to the 03H command of the master for reading data. The CMD information occupies one byte.
"Number of bytes" indicates the number of bytes between a byte (not included) and the CRC byte (not included). The value 04 indicates that there are four bytes of data between "Number of bytes" and "LSB of CRC", that is, "MSB of data in 0004H", "LSB of data in 0004H", "MSB of data in 0005H", and "LSB of data in 0005H".
A piece of data is two bytes, with the MSB on the left and LSB on the right. From the response, we can see that the data in 0004H is 1388H, and that in 0005H is 0000H.
10.4.2 Command code: 06H, writing a word
This command is used by the master to write data to the VFD. One command can be used to write only one piece of data. It is used to modify the parameters and operation mode of the VFD.
For example, to write 5000 (1388H) to 0004H of the VFD whose address is 02H, the structure of the frame is described in the following table.
START
ADDR
02H
CMD
06H
MSB of data   writing address
00H
LSB of data   writing address
04H
MSB of to-be-written data
13H
LSB of to-be-written data
88H
LSB of CRC
C5H
MSB of CRC
6EH
END
START
ADDR
02H
CMD
06H
00H
04H
13H
88H
LSB of CRC
C5H
MSB of CRC
6EH
END
Note: Section 10.2 and 10.3 mainly describe the command format, and the detailed application will be mentioned in 10.4.8 with examples.
10.4.3 Command code: 08H, diagnosis
Sub-function code description
Sub-function Code
Description
0000
Return data based on query requests
For example, to query about the circuit detection information about the VFD whose address is 01H, the query and return strings are the same, and the format is described in the following tables.
RTU master command
START
ADDR
01H
CMD
08H
MSB of the sub-function code
00H
LSB of the sub-function code
00H
MSB of data
12H
LSB of data
ABH
LSB of CRC CHK
ADH
MSB of CRC CHK
14H
END
RTU slave response
START
ADDR
01H
CMD
08H
00H
00H
MSB of data
12H
LSB of data
ABH
LSB of CRC CHK
ADH
MSB of CRC CHK
14H
END
10.4.4 Command code: 10H, continuous writing
The command code 10H is used by the master to write data to the VFD. The quantity of data to be written is determined by "Data quantity", and a maximum of 16 pieces of data can be written.
For example, to write 5000 (1388H) and 50 (0032H) respectively to 0004H and 0005H of the VFD whose slave address is 02H, the structure of the frame is described in the following table.
START
ADDR
02H
CMD
10H
00H
04H
00H
02H
Number of bytes
04H
MSB of data to be   written to 0004H
13H
LSB of data to be   written to 0004H
88H
MSB of data to be   written to 0005H
00H
LSB of data to be   written to 0005H
32H
LSB of CRC
C5H
MSB of CRC
6EH
END
START
ADDR
02H
CMD
10H
00H
04H
00H
02H
LSB of CRC
C5H
MSB of CRC
6EH
END
10.4.4 The definition of data address
This section describes the address definition of communication data. The addresses are used for controlling the running, obtaining the state information, and setting related function parameters of the VFD.
10.4.5.1 The rules of parameter address of the function codes
The address of a function code consists of two bytes, with the MSB on the left and LSB on the right. The MSB ranges from 00 to ffH, and the LSB also ranges from 00 to ffH. The MSB is the hexadecimal form of the group number before the dot mark, and LSB is that of the number behind the dot mark. Take P05.06 as an example, the group number is 05, that is, the MSB of the parameter address is the hexadecimal form of 05; and the number behind the dot mark is 06, that is, the LSB is the hexadecimal form of 06. Therefore, the function code address is 0506H in the hexadecimal form. For P10.01, the parameter address is 0A01H.
Function    code
Detailed    parameter description
Default    value
Modify
P10.00
Simple PLC
0: Stop after running once.
1: Run at the final value after running once.
2. Cycle running.
P10.01
Simple PLC memory   selection
0: Power loss without memory
1: Power loss with memory
The parameters in the P29 group are set by the manufacturer. They cannot be read or modified. Some parameters cannot be modified when the VFD is running; some cannot be modified regardless of the state of the VFD. Pay attention to the setting range, unit, and related description of a parameter when modifying it.
The service life of the Electrically Erasable Programmable Read-Only Memory (EEPROM) may be reduced if it is frequently used for storage. For users, some function codes do not need to be stored during communication. The application requirements can be met by modifying the value of the on-chip RAM, that is, modifying the MSB of the corresponding function code address from 0 to 1. For example, if P00.07 is not to be stored in the EEPROM, you need only to modify the value of the RAM, that is, set the address to 8007H. The address can be used only for writing data to the on-chip RAM, and it is invalid when used for reading data.
10.4.5.2 The address instruction of other function in Modbus
In addition to modifying the parameters of the VFD, the master can also control the VFD, such as start and stop it, and monitor the operation state of the VFD.
The following table describes other function parameters.
Function
Address
Data description
R/W
Communication-based control command
2000H
0001H: Forward   running
R/W
0002H: Reverse running
0003H: Forward jogging
0004H: Reverse jogging
0005H: Stop
0006H: Coast to stop (emergency stop)
0007H: Fault reset
0008H: Jogging to stop
Communication-based value setting
2001H
Communication-based frequency setting (0–Fmax, unit: 0.01 Hz)
R/W
2002H
PID setting, range (0–1000, 1000 corresponding to   100.0%)
2003H
PID feedback, range (0–1000, 1000 corresponding to   100.0%)
R/W
2004H
Torque setting (-3000–+3000, 1000 corresponding to 100.0%   of the rated current of the motor)
R/W
2005H
Setting of the upper limit of the forward running   frequency (0–Fmax, unit: 0.01 Hz)
R/W
2006H
Setting of the upper limit of the reverse running   frequency (0–Fmax, unit: 0.01 Hz)
R/W
2007H
Upper limit of the electromotion torque (0–3000,   1000 corresponding to 100.0% of the rated current of the VFD)
R/W
2008H
Upper limit of the brake torque (0–3000, 1000   corresponding to 100.0% of the rated current of the motor)
R/W
2009H
Special control command word:
Bit0–1: =00: Motor 1   =01: Motor 2
        =10: Motor 3   =11: Motor 4
Bit2: =1 Torque control disabled =0:   Torque control cannot be disabled
Bit3: =1 Power consumption reset to   0
=0: Power consumption not reset
Bit4: =1 Pre-excitation  =0: Pre-excitation disabled
Bit5: =1 DC brake  =0: DC brake disabled
R/W
200AH
Virtual   input terminal command, range: 0x000–0x1FF
R/W
200BH
Virtual   output terminal command, range: 0x00–0x0F
R/W
200CH
Voltage setting (used when V/F separation is   implemented)
(0–1000, 1000 corresponding to 100.0% of the rated   voltage of the motor)
R/W
200DH
AO output setting 1 (-1000–+1000, 1000 corresponding to 100.0%)
R/W
200EH
AO output setting 2 (-1000–+1000, 1000 corresponding to 100.0%)
R/W
VFD state word 1
2100H
R
0003H: Stopped
0004H: Faulty
0005H: POFF
0006H:   Pre-excited
VFD state word 2
2101H
Bit0:  =0: Not ready to   run =1: Ready to run
Bi1–2: =00: Motor 1   =01: Motor 2
Bit3:   =0: Asynchronous   machine  =1: Synchronous   machine
Bit4: =0: No overload alarm =1: Overload   alarm
Bit5–Bit6: =00: Keypad-based control   =01: Terminal-based control
=10: Communication-based   control
R
VFD fault code
2102H
See the description of fault types.
R
VFD   identification code
2103H
GD35-----0x0109
R
Running   frequency
3000H
0–Fmax (unit: 0.01Hz)
Compatible with CHF100A and CHV100 communication   addresses
R
Set frequency
3001H
R
Bus voltage
3002H
0.0–2000.0 V (unit: 0.1V)
R
Output voltage
3003H
0–1200V (unit: 1V)
R
Output current
3004H
0.0–3000.0A (unit: 0.1A)
R
Rotating speed
3005H
0–65535 (unit: 1RPM)
R
Output power
3006H
-300.0–+300.0% (unit: 0.1%)
R
Output torque
3007H
-250.0–+250.0% (unit: 0.1%)
R
Closed-loop setting
3008H
-100.0–+100.0% (unit: 0.1%)
R
Closed-loop   feedback
3009H
R
Input state
300AH
000–1FF
R
Output state
300BH
000–1FF
R
Analog input 1
300CH
0.00–10.00V (unit: 0.01V)
R
Analog input 2
300DH
R
Analog input 3
300EH
-10.00–10.00V (unit: 0.01V)
R
Analog input 4
300FH
R
Read input of high-speed pulse 1
3010H
0.00–50.00kHz (unit: 0.01Hz)
R
Read input of high-speed pulse 2
3011H
R
Read current step of multi-step speed
3012H
0–15
R
External length
3013H
0–65535
R
External count   value
3014H
0–65535
R
Torque setting
3015H
R
Identification   code
3016H
R
Fault code
5000H
R
The Read/Write (R/W) characteristics indicate whether a function can be read and written. For example, "Communication-based control command" can be written, and therefore the command code 6H is used to control the VFD. The R characteristic indicates that a function can only be read, and W indicates that a function can only be written.
Note: Some parameters in the preceding table are valid only after they are enabled. Take the running and stop operations as examples, you need to set "Running command channel" (P00.01) to "Communication", and set "Communication running command channel" (P00.02) to the Modbus communication channel. For another example, when modifying "PID setting", you need to set "PID reference source" (P09.00) to Modbus communication.
The following table describes the encoding rules of device codes (corresponding to the identification code 2103H of the VFD).
MSB of the code
Meaning
LSB of the code
Meaning
01
GD
0x08
GD35 vector VFD
0x09
GD35-H1 vector VFD
0x0a
GD300 vector VFD
10.4.6 Fieldbus ratio values
In practical applications, communication data is represented in the hexadecimal form, but hexadecimal values cannot represent decimals. For example, 50.12 Hz cannot be represented in the hexadecimal form. In such cases, we can multiply 50.12 by 100 to obtain an integer 5012, and then 50.12 can be represented as 1394H (5012 in the decimal form) in the hexadecimal form.
In the process of multiplying a non-integer by a multiple to obtain an integer, the multiple is referred to as a fieldbus scale.
The fieldbus scale depends on the number of decimals in the value specified in "Detailed parameter description" or "Default value". If there are n decimals in the value, the fieldbus scale m is the nth-power of 10. Take the following table as an example, m is 10.
Function    code
Default    value
Modify
P01.20
Hibernation restore delay time
0.0–3600.0s (valid   when P01.19 is   2)
0.0s
P01.21
Restart after power off
0: Restart   is disabled
1: Restart   is enabled
The value specified in "Detailed parameter description" or "Default value" contains one decimal, so the fieldbus scale is 10. If the value received by the upper computer is 50, the value of "Wake-up-from-sleep delay" of the VFD is 5.0 (5.0=50/10).
To set the "Wake-up-from-sleep delay" to 5.0s through Modbus communication, you need first to multiply 5.0 by 10 according to the scale to obtain an integer 50, that is, 32H in the hexadecimal form, and then transmit the following write command:
After receiving the command, the VFD converts 50 into 5.0 based on the fieldbus scale, and then sets "Wake-up-from-sleep delay" to 5.0s.
For another example, after the upper computer transmits the "Wake-up-from-sleep delay" parameter read command, the master receives the following response from the VFD:
The parameter data is 0032H, that is, 50, so 5.0 is obtained based on the fieldbus scale (50/10=5.0). In this case, the master identifies that the "Wake-up-from-sleep delay" is 5.0s.
10.4.7 Fault message response
Operation errors may occur in communication-based control. For example, some parameters can only be read, but a write command is transmitted. In this case, the VFD returns an error message response.
Error message responses are transmitted by the VFD to the master. The following table describes the codes and definitions of the error message responses.
Code
Definition
01H
Invalid command
The command code received by the upper computer is   not allowed to be executed. The possible causes are as follows:
• The function code is applicable only on new devices and is not implemented   on this device.
• The slave is in the faulty state when processing   this request.
02H
Invalid data address
For the VFD, the data address in the request of   the upper computer is not allowed. In particular, the combination of the   register address and the number of the to-be-transmitted bytes is invalid.
03H
Invalid data bit
The received data domain contains a value that is   not allowed. The value indicates the error of the remaining structure in the   combined request.
Note: It does not mean that the data item submitted for   storage in the register includes a value unexpected by the program.
04H
Operation failure
The parameter is set to an invalid value in the   write operation. For example, a function input terminal cannot be set   repeatedly.
05H
Password error
The password entered in the password verification   address is different from that set in P07.00.
06H
Data frame error
The length of the data frame transmitted by the   upper computer is incorrect, or in the RTU format, the value of the CRC check   bit is inconsistent with the CRC value calculated by the lower computer
07H
Parameter read-only
The parameter to be modified in the write   operation of the upper computer is a read-only parameter.
08H
Parameter cannot be modified in running
The parameter to be modified in the write   operation of the upper computer cannot be modified during the running of the VFD.
09H
Password protection
A user password is set, and the upper computer   does not provide the password to unlock the system when performing a read or   write operation. The error of "system locked" is reported.
When returning a response, the device uses a function code domain and fault address to indicate whether it is a normal response (no error) or exception response (some errors occur). In a normal response, the device returns the corresponding function code and data address or sub-function code. In an exception response, the device returns a code that is equal to a normal code, but the first bit is logic 1.
For example, if the master device transmits a request message to a slave device for reading a group of function code address data, the code is generated as follows:
0 0 0 0 0 0 1 1 (03H in the hexadecimal form)
For a normal response, the same code is returned. For an exception response, the following code is returned:
1 0 0 0 0 0 1 1 (83H in the hexadecimal form)
In addition to the modification of the code, the slave returns a byte of exception code that describes the cause of the exception. After receiving the exception response, the typical processing of the master device is to transmit the request message again or modify the command based on the fault information.
For example, to set the "Running command channel" (P00.01, the parameter address is 0001H) of the VFD whose address is 01H to 03, the command is as follows:
But the setting range of the "Running command channel" is 0 to 2. The value 3 exceeds the setting range. In this case, the VFD returns an error message response as shown in the following:
The exception response code 86H (generated based on the MSB "1" of the write command 06H) indicates that it is an exception response to the write command (06H). The error code is 04H. From the preceding table, we can see that it indicates the error "Operation failure", which means "The parameter is set to an invalid value in the write operation".
10.4.8 Example of writing and reading
For details about the formats of the read and write commands, see sections 10.4.1 and 10.4.2.
10.4.8.1 Example of reading command 03H
Example 1: Read state word 1 of the VFD whose address is 01H. From the table of other function parameters, we can see that the parameter address of state word 1 of the VFD is 2100H.
The read command transmitted to the VFD is as follows:
Assume that the following response is returned:
The data content returned by the VFD is 0003H, which indicates that the VFD is in the stopped state.
Example 2: View information about the VFD whose address is 03H, including "Type of current fault" (P07.27) to "Type of last but four fault" (P07.32) of which the parameter addresses are 071BH to 0720H (contiguous 6 parameter addresses starting from 071BH).
The command transmitted to the VFD is as follows:
From the returned data, we can see that all the fault types are 0023H, that is, 35 in the decimal form, which means the maladjustment fault (STo).
10.4.8.2 Example of writing command 06H
Example 1: Set the VFD whose address is 03H to be forward running. Refer to the table of other function parameters, the address of "Communication-based control command" is 2000H, and 0001H indicates forward running, as shown in the following figure.
Function
Address
Data description
R/W
2000H
R/W
0005H: Stop
0007H: Fault reset
The command transmitted by the master is as follows:
If the operation is successful, the following response is returned (same as the command transmitted by the master):
Example 2: Set the "Max. output frequency" of the VFD whose address is 03H to 100 Hz.
Function code
Default value
Modify
P00.03
Setting range: P00.04–400.00 Hz
50.00Hz
From the number of decimals, we can see that the fieldbus scale of the "Max. output frequency" (P00.03) is 100. Multiply 100 Hz by 100. The value 10000 is obtained, and it is 2710H in the hexadecimal form.
Note: In the preceding command description, spaces are added to a command just for explanatory purposes. In practical applications, no space is required in the commands.
10.4.8.3 Example of continuous writing command10H
Example 1: make the VFD whose address is 01H run forward at 10 Hz. Refer to the instruction of 2000H and 0001. Set the address of "communication setting frequency" is 2001H and 10 Hz corresponds to 03E8H. See the table below.
Example 1: Set the VFD whose address is 01H to be forward running at the frequency of 10 Hz. Refer to the table of other function parameters, the address of "Communication-based control command" is 2000H, 0001H indicates forward running, and the address of "Communication-based value setting" is 2001H, as shown in the following figure. 10 Hz is 03E8H in the hexadecimal form.
Function instruction
Address definition
Data meaning instruction
R/W characteristics
2000H
R/W
0005H: Stop
0007H: Fault reset
2001H
R/W
2002H
In the actual operation, set P00.01 to 2 and P00.06 to 8.
If the operation is successful, the following response is returned:
Example 2: Set "Acceleration time" of the VFD whose address is 01H to 10s, and "Deceleration time" to 20s.
Function code
Default value
Modify
P00.11
ACC time 1
Setting range of P00.11 and P00.12:
0.0–3600.0 s
Depend on model
P00.12
DEC time 1
Depend on model
The address of P00.11 is 000B, ACC time of 10s is 0064H in the hexadecimal form, and the DEC time of 20s is 00C8H in the hexadecimal form.
10.4.8.4 Modbus communication debugging instance
A PC is used as the host, an RS232-RS485 converter is used for signal conversion, and the PC serial port used by the converter is COM1 (a RS232 port). The upper computer commissioning software is the serial port commissioning assistant Commix, which can be downloaded from the Internet. Download a version that can automatically execute the CRC check function. The following figure shows the interface of Commix.
First, select COM1 for "serial port" and the baud rate should be set to the same value with P14.01. The data bit, check bit and stop bit must be consistent with the setup in P14.02. As RTU mode is used here, "HEX" should be selected. Check image.pngto make the software add CRC automatically, and select CRC16 (MODBUSRTU) with the starting byte being 1. Once enabled, CRC check will be added automatically, which removes the need to fill in CRC manually.
The commissioning command to set the VFD whose address is 03H to be forward running is as follows:
1.  Set the address (P14.00) of the VFD to 03.
2.  Set "Channel of running commands" (P00.01) to "Communication", and set "Communication channel of running commands" (P00.02) to the Modbus communication channel.
3.  Click Send. If the line configuration and settings are correct, a response transmitted by the VFD is received as follows: