Function code
Detailed    instruction
of parameters
Default    value
Modify
P01.00
Start
mode
0: Start-up   directly: start from the starting frequency P01.01
1: Start-up   after DC brake: start the motor from the starting frequency after DC brake (set   the parameter P01.03 and P01.04). It is suitable in the cases where reverse   rotation may occur to the low inertia load during starting.
2: Start-up after   speed tracing: start the rotating motor smoothly after tracking the rotation   speed and direction automatically. It is suitable in the cases where reverse   rotation may occur to the big inertia load during starting.
Note: The VFDs   above 4 kW have the function.
P01.01
Starting frequency
of direct
start
Starting frequency   of direct start-up means the original frequency during the VFD starting. See P01.02   for detailed information.
Setting range: 0.00–50.00   Hz
0.00 Hz
P01.02
Retention
time of
starting frequency
Set a proper starting frequency to increase the   torque of the VFD during starting. During the retention time of the starting   frequency, the output frequency of the VFD is the starting frequency. And   then, the VFD will run from the starting frequency to the set frequency. If   the set frequency is lower than the starting frequency, the VFD will stop   running and keep in the stand-by state. The starting frequency is not limited   in the lower limit frequency.
Setting range: 0.0–50.0s
0.0 s
P01.03
The brake current
before
starting
The VFD will carry out DC brake at the brake   current set before starting and it will speed up after the DC brake time. If   the DC brake time is set to 0, the DC brake is invalid.
The stronger the brake current, the bigger the brake   power. The DC brake current before starting means the percentage of the rated   current of the VFD.
The setting range of   P01.03: 0.0–100.0%
The setting range of   P01.04: 0.0–30.0s
0.0%
P01.04
The brake
time
before
starting
0.0 s
P01.05
ACC/DEC selection
The changing mode of   the frequency during start-up and running.
0: Linear type. The   output frequency increases or decreases linearly.
1: S curve. The   output frequency increases or decreases according to the S curve.
S curve is generally   used in cases where smooth startup/stop is required eg elevator, conveyor   belt, etc.
P01.06
ACC time
of the
starting
step of
S curve
The curve rate   of S curve is determined by the acceleration range and acceleration/deceleration   time.
0.1 s
P01.07
DEC time
 of the
ending
step of
S curve
0.1 s
P01.08
Stop
mode
0: Decelerate to   stop: after the stop command becomes valid, the VFD decelerates to decrease   the output frequency during the set time. When the frequency decreases to P01.15,   the VFD stops.
1: Coast to stop: after   the stop command becomes valid, the VFD ceases the output immediately. And   the load coasts to stop at the mechanical inertia.
P01.09
Starting frequency
 of DC
brake
The   starting frequency of stop brake: The VFD will carry on stop DC brake when   the frequency is arrived during the procedure of decelerating to stop.
Demagnetizing   time: Before the stop DC brake, the VFD will close output and begin to carry   on the DC brake after the waiting time. This function is used to avoid the   overcurrent fault caused by DC brake when the speed is too high.
Stop DC   brake current: the DC brake added. The stronger the current, the bigger the   DC brake effect.
The brake   time of stop brake: the retention time of DC brake. If the time is 0, the DC   brake is invalid. The VFD will stop at the set deceleration time.
Setting range of P01.09:   0.00 Hz–P00.03 (max. output frequency)
Setting range of P01.10:   0.00–30.00s
Setting range of P01.11:   0.0–100.0%
Setting range of P01.12:   0.0–50.0s
0.00 Hz
P01.10
Demagne
tizing time
0.00 s
P01.11
DC brake current
0.0%
P01.12
DC
brake
time
0.0 s
P01.13
Dead
time of
FWD
/REV
rotation
During the procedure of switching for/rev   rotation, set the threshold by P01.14,   which is as the table below:
Setting range: 0.0–3600.0s
0.0 s
P01.14
Shifting between FWD
/REV
rotation
Set the threshold   point of the VFD:
0: Switch after zero   frequency
1: Switch after the starting   frequency
P01.15
Stopping speed
0.00–100.00 Hz
0.20 Hz
P01.16
Detection
 of
stopping speed
0: Detect according   to speed setting (no stopping delay)
1: Detect according   to speed feedback (only valid for vector control)
P01.17
Detection time of
the
feedback speed
If set P01.16   to 1, the feedback frequency is less than or equal to P01.15 and detect in   the set time of P01.17, the VFD will stop; otherwise the VFD will stop after   the set time of P01.17.
Setting   range: 0.0–100.0s (only valid when P01.16=1)
0.5 s
P01.18
Terminal running protection when powering   on
When the running   commands are controlled by the terminal, the system will detect the state of   the running terminal during powering on.
0: The terminal   running command is invalid when powering on. Even the running command is   detected to be valid during powering on, the VFD won’t run and the system   keeps in the protection state until the running command is canceled and   enabled again.
1: The terminal   running command is valid when powering on. If the running command is detected   to be valid during powering on, the system will start the VFD automatically   after the initialization.
Note: this   function should be selected with cautions, or serious result may follow.
P01.19
Action if running frequency< lower limit   frequency (valid >0)
This   function code determines the running state of the VFD when the set frequency   is lower than the lower-limit one.
0: Run at   the lower-limit frequency
1: Stop
2: Hibernation
3: Run at   zero frequency
The VFD   will coast to stop when the set frequency is lower than the lower-limit one.   If the set frequency is above the lower limit one again and it lasts for the   time set by P01.20, the VFD will come back to the running state automatically.
P01.20
Hibernation restore
delay time
This function code   determines the hibernation delay time. When the running frequency of the VFD   is lower than the lower limit one, the VFD will pause to stand by.
When the set   frequency is above the lower limit one again and it lasts for the time set by   P01.20, the VFD will run automatically.
Setting range: 0.0–3600.0s   (valid when P01.19=2)
0.0 s
P01.21
Restart
after
power off
This function can enable the VFD start or not   after the power off and then power on.
0: Disable
1: Enable, if the   starting need is met, the VFD will run automatically after waiting for the   time defined by P01.22.
P01.22
The waiting time of restart after power off
The function determines the waiting time before   the automatic running of the VFD when powering off and then powering on.
Setting range: 0.0–3600.0   s (valid when P01.21=1)
1.0 s
P01.23
Start delay time
The function determines the brake release after the running command is   given, and the VFD is in a stand-by state and wait for the delay time set by P01.23
Setting range: 0.00–60.00   s
0.00 s
P01.24
Delay time
 of the stop speed
Setting range: 0.0–60.0   s
0.0 s
P01.25
DEC time of E-stop
DEC time of E-stop (terminal function is set to 56).
2.00 s