Goodrive35 series VFDs have 2 relay output terminals and 1 Y output terminal and 1 high speed pulse output terminal in the standard configuration. All functions of the digital input terminals are programmable by the function codes. Open collector pole input can be selected into high speed pulse input terminal or common switch input terminal by function code.
The below table is the option of the four function parameters and selecting the repeated output terminal function is allowed.
Set value
Function
Instructions
Invalid
The output terminal has no function.
Running
Output ON signal when the VFD is running and there   is frequency output.
Forward running
Output ON signal when the VFD is running forward   and there is frequency output.
3
Reverse running
Output ON signal when the VFD is running reverse   and there is frequency output.
4
Jogging
Output ON signal when the VFD is jogging and there   is frequency output.
5
VFD fault
Output ON signal when the VFD is in fault
6
FDT1
Please refer to P08.32 and P08.33 for detailed   information.
7
FDT2
Please refer to P08.34 and P08.35 for detailed   information.
8
Frequency arrival
Please refer to P08.36 for detailed information.
9
Zero-speed   running
Output ON signal when the output frequency and given   frequency of the VFD is 0 at the same time.
10
Upper-limit   frequency arrival
Output ON signal when the running frequency of the   VFD is the upper limit frequency.
11
Output ON signal when the running frequency of the   VFD is the lower limit frequency.
12
Ready to run
When the   main circuit and the control circuit are established and the protection   function of the VFD is not active. The VFD is in the running state and it   will output ON signal.
13
Pre-exciting
Output ON   signal when the VFD is in the pre-exciting state.
14
Overload   pre-alarm
Output ON signal if the VFD is beyond the   pre-alarm point. Refer to P11.08–P11.10 for the detailed instruction.
15
Underload   pre-alarm
Output ON   signal if the VFD is beyond the pre-alarm point. Refer to P11.11–P11.12 for   the detailed instruction.
16
Simple PLC stage completion
Output signal if the simple PLC stage is   completed.
17
 Simple PLC cycle completion
Output signal if the 1 simple PLC cycle is   completed.
23
Modbus   communication virtual terminal output
Output corresponding signal according to the   setting value of Modbus. Output ON signal if the setting value is 1   and output OFF signal if the setting value is 0.
24
POROFIBUS/CANopen   communication virtual terminal output
Output corresponding signal according to the   setting value of PROFIBUS/CANOPEN. Output ON signal if the setting value   is 1 and output OFF signal if the setting value is 0.
25
Ethernet communication   virtual terminal output
Output the   corresponding signal according to the Ethernet signal. Output ON when setting   as1 and output OFF when setting as 0.
26
Bus voltage   established
Output ON   according to the establishment of bus voltage
27–29
Reserved
30
Positioning   finished
Output ON when   the positioning is finished
31
Spindle returning   finished
Output ON when   the returning is finished
32
Spindle scaling   finished
Output ON when   the scaling is finished
33
Speed limiting
Output ON when the speed is the upper or lower limit
34
Low bus voltage
Output ON when   the value is below P8.27
35
Underload   stopping output
If enabling bit of P08.26 is valid, and it is in   underload state, ON signal will be output
36
Speed/position switching finished
When the speed is switched to position control,   output ON signal
Relative parameters list:
Function    code
Default    value
P06.00
HDO output
0: Open collector pole high speed pulse output
1: Open collector   pole output
P06.01
Y1 output
0: Invalid
1: In operation
2: Forward rotation operation
3: Reverse rotation operation
4: Jogging operation
5: VFD fault
6: Frequency degree test FDT1
7: Frequency degree test FDT2
8: Frequency arrival
9: Zero speed running
10: Upper limit frequency arrival
11: Lower limit frequency arrival
12: Ready for operation
13: In pre-exciting
14: Overload pre-alarm
15: Underload pre-alarm
16: Completion of simple PLC stage
17: Completion of simple PLC cycle
18–22: Reserved
23: Modbus communication virtual terminals   output
24: PROFIBUS/CANopen communication virtual   terminals output
25: Ethernet communication virtual   terminals output
26: Bus   voltage established
27: Reserved
28: Pulse   superposing
29: Reserved
30: Positioning   finished
31: Spindle   zeroing finished
32: Spindle   scaling finished
33: Speed   limiting
34: Bus   voltage too low
35: Bus undervoltage stop state output
36: Speed/position control switching   finished
37–40: Reserved
P06.02
HDO output
P06.03
Relay RO1 output
P06.04
Relay RO2 output
5
P06.05
Polarity of output terminals
0x00–0x0F
0x00
P06.06
Y1 switch-on delay time
0.000–50.000 s
0.000 s
P06.07
Y1 switch-off delay time
0.000–50.000 s
0.000 s
P06.08
HDO switch-on delay
0.000–50.000   s (valid only when P06.00=1)
0.000 s
P06.09
HDO switch-off delay
0.000 s
P06.10
RO1 switch-on delay
0.000–50.000 s
0.000 s
P06.11
RO1 switch-off delay
0.000–50.000 s
0.000 s
P06.12
RO2 switch-on delay
0.000–50.000 s
0.000 s
P06.13
RO2 switch-off delay
0.000–50.000 s
0.000 s
P07.40
Output terminal state at present fault
P17.13
Digital output terminals state