Function    code
Default    value
Modify
P08.00
ACC time 2
See P00.11 and P00.12 for detailed   definition.
Goodrive300 series define four groups of   ACC/DEC time which can be selected by P5 group. The first group of ACC/DEC   time is the factory default one.
Setting range: 0.0–3600.0s
Depend on model
P08.01
DEC time 2
Depend on model
P08.02
ACC time 3
Depend on model
P08.03
DEC time 3
Depend on model
P08.04
ACC time 4
Depend on model
P08.05
DEC time 4
Depend on model
P08.06
Jogging frequency
This parameter is used to define the   reference frequency during jogging.
Setting range: 0.00 Hz–P00.03 (Max.   frequency)
5.00Hz
P08.07
Jogging ACC time
The   jogging ACC time means the time needed if the VFD runs from 0Hz to the Max.   Frequency.
The   jogging DEC time means the time needed if the VFD goes from the Max. frequency   (P00.03) to 0Hz.
Depend on model
P08.08
Jogging DEC time
Depend on model
P08.09
Jump frequency 1
When the set frequency is in the range of   jumping frequency, the VFD will run at the edge of the jumping frequency.
The VFD can avoid the mechanical resonance   point by setting the jumping frequency. The VFD can set three jumping   frequency. But this function will be invalid if all jumping points are 0.
Setting   range: 0.00Hz–P00.03 (Max. output frequency)
0.00Hz
P08.10
Jump frequency bandwidth 1
0.00Hz
P08.11
Jump frequency 2
0.00Hz
P08.12
Jump frequency bandwidth 2
0.00Hz
P08.13
Jump frequency 3
0.00Hz
P08.14
Jumping frequency range 3
0.00Hz
P08.15
Traverse range
This function   applies to the industries where traverse and convolution function are   required such as textile and chemical fiber.
The traverse   function means that the output frequency of the VFD is fluctuated with the   set frequency as its center. The route of the running frequency is   illustrated as below, of which the traverse is set by P08.15 and when P08.15   is set as 0, the traverse is 0 with no function.
Traverse range: The   traverse running is limited by upper and low frequency.
The traverse range corresponds   to the center frequency: traverse range AW=center frequency×traverse range P08.15.
Sudden   jumping frequency=traverse   range AW×sudden jumping frequency range P08.16. When run at the traverse   frequency, the value corresponds to the sudden jumping frequency.
The   raising time of the traverse frequency: The time from the lowest point to the   highest one.
The   declining time of the traverse frequency: The time from the highest point to   the lowest one.
Setting range of   P08.15: 0.0–100.0% (corresponding to the set frequency)
Setting range of   P08.16: 0.0–50.0% (corresponding to the traverse range)
Setting range of   P08.17: 0.1–3600.0s
Setting range of   P08.18: 0.1–3600.0s
0.0%
P08.16
Sudden jumping frequency range
0.0%
P08.17
Traverse boost time
5.0s
P08.18
Traverse declining time
5.0s
P08.19
Set length
The function codes of setting length, actual   length and unit pulse are mainly used to control the fixed length.
The length is counted by the pulse signal of HDI   terminals input and the HDI terminals are needed to set as the length   counting input.
Actual length=the length counting input pulse /unit pulse
When the actual length P08.20 exceeds the set   length P08.19, the multi-function digital output terminals will output ON.
Setting range of P08.19: 0–65535m
Setting range of P08.20: 0–65535m
Setting range of P08.21: 1–10000
Setting range of P08.22: 0.01–100.00cm
Setting range of P08.23: 0.001–10.000
Setting range of P08.24: 0.001–1.000
0m
P08.20
Actual length
0m
P08.21
Pulse per rotation
P08.22
Alxe perimeter
10.00
cm
P08.23
Length ratio
1.000
P08.24
Length correcting coefficient
1.000
P08.25
Set count value
The counter works based on the input pulse signals   of the HDI terminals.
When the count value reaches the specified number,   the multi-function output terminal sends the signal of "The speficied   count value is reached" and the counter continues to count; when the   count value reaches the set number, the multi-function output terminal sends   the signal of "The set count value is reached", and the counter   will be reset to zero and recount when the next pulse occurs.
The value of P08.26 cannot be greater than that of   P08.25.
The function is illustrated as below:
Setting range of P08.25: P08.26–65535
Setting range of P08.26: 0–P08.25
P08.26
Specified count value
P08.27
Set running time
Pre-set running time of the VFD. When the   accumulative running time achieves the set time, the multi-function digital   output terminals will output the signal of "running time arrival".
Setting range: 0–65535m
0m
P08.28
Automatic fault reset times
Automatic   fault reset times: set the automatic fault   reset times. If the reset time exceeds this set value, the VFD will stop to wait   maintenance.
Interval   time of automatic fault reset: the interval   between the time when the fault occurs and the time when the reset action   occurs.
Setting range of P08.28: 0–10
Setting range of P08.29: 0.1–3600.0s
P08.29
1.0s
P08.30
Frequency decreasing ratio of the dropping   control
The output frequency of the VFD changes as   the load. And it is mainly used to balance the power when several VFDs drive   one load.
Setting range: 0.00–50.00Hz
0.00Hz
P08.31
Motor shifting
Goodrive300 supports the shift between two motors.   This function is used to select the shifting channel.
LED ones: shifting channel
0: terminal shifting; digital terminal is 35
1: Modbus communication shifting
2: PROFIBUS/CANopen communication shifting
3: Ethernet communication shifting
4: Reserved
LED tens: shifting enabling in operation
0: Disabled
1: Enabled
0x00–0x14
P08.32
FDT1 electrical level detection value
When the output frequency exceeds the   corresponding frequency of FDT electrical level, the multi-function   digital output terminals will output the signal of "frequency level   detect FDT" until the output frequency decreases to a   value lower than (FDT electrical level—FDT retention detection value) the   corresponding frequency, the signal is invalid. Below is the ware form   diagram:
Setting range of P08.32: 0.00Hz–P00.03 (Max.   frequency)
Setting range of P08.33: 0.0–100.0% (FDT1   electrical level)
Setting range of P08.34: 0.00Hz–P00.03 (Max.   frequency)
Setting range of P08.35: 0.0–100.0% (FDT2   electrical level)
50.00
Hz
P08.33
FDT1 retention   detection value
5.0%
P08.34
FDT2 electrical level detection value
50.00
Hz
P08.35
FDT2 retention   detection value
5.0%
P08.36
Frequency arrival detection range
When the output frequency is among the positive or   negative detection range of the set frequency, the multi-function digital   output terminal will output the signal of "frequency arrival", see   the diagram below for detailed information:
Setting   range: 0.00Hz–P00.03 (Max. frequency)
0.00Hz
P08.37
Enable dynamic braking
This parameter is used to control the   enabling of the internal braking pipe inside the VFD.
0: Disable
1: Enable
Note: This   function is only applicable to the internal braking pipe.
P08.38
Dynamic braking threshold voltage
Set the initial bus voltage for dynamic braking.   This value can be adjusted to perform valid braking on a load. The factory setting   changes with the voltage class.
Setting range: 200.0–2000.0V
To prevent customers from setting a value that is   too large, the following setting ranges are recommended:
380V voltage:
700.0V
500V voltage:
900.0V
660V voltage:
1120.0V
P08.39
Cooling fan running mode
0: Normal mode
1: The fan keeps running after being powered on.
P08.40
PWM selection
0x00–0x21
LED ones: PWM mode selection
0: PWM mode 1, three-phase modulation and   two-modulation
1: PWM mode 2, three-phase modulation
LED tens: low-speed carrier frequency limit   mode
0: Low-speed carrier frequency limit mode   1, the carrier frequency will limit to 2k if it exceeds 2k at low speed
1: Low-speed carrier frequency limit mode   2, the carrier frequency will limit to 4k if it exceeds 4k at low speed
2: No limit
01
P08.41
Overmodulation
LED ones
0: Invalid
1: Valid
LED tens (for factory commissioning)
0: Light overcommission; in zone 1
1: Heavy overcommission; in zone 2
01
P08.42
Keypad data control
0x000–0x1223
LED ones:frequency enable selection
0: Both ∧/∨ keys and digital potentiometer adjustments are valid
1: Only ∧/∨ keys adjustment is valid
2: Only digital potentiometer adjustments is valid
3: Neither ∧/∨ keys nor   digital potentiometer adjustments are valid
LED tens: frequency control selection
0: Only valid   when P00.06=0 or P00.07=0
1: Valid   for all frequency setting manner
2: Invalid   for multi-step speed when multi-step speed has the priority
LED hundreds: action selection during   stopping
0: Setting is valid
1: Valid during running, cleared after stopping
2: Valid during running, cleared after   receiving the stop command
LED thousands: ∧/∨ keys and digital potentiometer integral function
0: The integral function is valid
1: The integral function is invalid
0x0000
P08.43
Integral ratio of   the keypad potentiometer
0.01–10.00s
0.10s
P08.44
UP/DOWN terminals   control
0x000–0x221
LED ones: frequency control selection
0: UP/DOWN terminals setting valid
1: UP/DOWN terminals setting valid
1: All frequency means are valid
2: When the multi-step are priority, it is   invalid to the multi-step
LED hundreds: action selection when stop
0: Setting valid
1: Valid in the running, clear after stop
2: Valid in the running, clear after   receiving the stop commands
0x000
P08.45
UP terminals frequency changing ratio
0.01–50.00Hz/s
0.50 Hz/s
P08.46
DOWN terminals frequency changing ratio
0.01–50.00 Hz/s
0.50 Hz/s
P08.47
Frequency setting at power loss
0x000–0x111
LED ones: Action selection when power off.
0: Save when power off
1: Clear when power off
LED tens: Action selection when Modbus set   frequency off
LED hundreds: The action selection when   other frequency set frequency off
0x000
P08.48
High bit of initial power consumption
This parameter is used to set the original   value of the power comsumotion.
The original value of the power comsumotion   =P08.48×1000+P08.49 (kWh)
Setting range of P08.48: 0–59999 kWh (k)
Setting range of P08.49: 0.0–999.9 kWh
0 kWh
P08.49
Low bit of initial power consumption
0.0 kWh
P08.50
Magnetic flux braking
This function code is used to enable   magnetic flux.
0: Invalid.
100–150: The bigger the coefficient, the   stronger the braking is.
This VFD is used to increase the magnetic   flux to decelerate the motor. The energy generated by the motor during   braking can be converter into heat energy by increasing the magnetic flux.
The VFD monitors the state of the motor   continuously even during the magnetic flux period. So the magnetic flux can   be used in the motor stop, as well as to change the rotation speed of the   motor. Its other advantages are:
Brake immediately after the stop command.   It does not need to wait the magnetic flux weaken.
Better cooling for motors. The current of   the stator other than the rotor increases during magnetic flux braking, while   the cooling of the stator is more effective than the rotor.
P08.51
Current adjustment coefficient on the input   side
This function code is used to adjust the   displayed current of the AC input side.
Setting range: 0.00–1.00
0.56