Function    code
Default    value
Modify
P11.00
Phase loss protection
0x00–0x11
LED ones:
0: Input phase loss   protection disable
1: Input phase loss   protection enable
LED tens:
0: Output phase loss   protection disable
1: Output phase loss   protection enable
11
P11.01
Frequency-decreasing at sudden power loss
0: Disable
1: Enable
P11.02
Frequency decreasing ratio at sudden power   loss
Setting range:   0.00Hz/s–P00.03 (Max. frequency)
After the   power loss of the grid, the bus voltage drops to the sudden   frequency-decreasing point, the VFD begin to decrease the running frequency   at P11.02, to make the VFD generate power again. The returning power can   maintain the bus voltage to ensure a rated running of the VFD until the recovery of power.
1. Adjust   the parameter properly to avoid the stopping caused by VFD protection during   the switching of the grid.
2. Disable input   phase loss protection to enable this function.
10.00
Hz/s
P11.03
Overvoltage stall protection
0:Disable
1: Enable
P11.04
Voltage   protection of overvoltage stall
120–150%(standard bus voltage)( 380V)
136%
120–150%(standard bus voltage)( 500V)
132%
120–150%(standard bus voltage)(660V)
120%
P11.05
Current limit action selection
The actual   increasing ratio of motor speed is lower than the ratio of output frequency   because of the big load during ACC running. It is necessary to take measures   to avoid overcurrent fault and the VFD trips.
Ones: current limit:
0: Invalid
1: Valid
Tens: overload alarm   of hardware current limit (for factory commissioning)
0: Valid
1: Invalid
01
P11.06
Automatic current limit
During the running   of the VFD, it will detect the output current and compare it with the limit   level defined in P11.06. If it exceeds the level, the VFD will run at stable   frequency in ACC running, or the VFD will derate to run during the constant   running. If it exceeds the level continuously, the output frequency will keep   on decreasing to the lower limit. If the output current is detected to be   lower than the limit level, the VFD will accelerate to run.
Setting range of P11.06: 50.0–200.0%
Setting range of   P11.07: 0.00–50.00Hz/s
160.0%
P11.07
Frequency-decreasing ratio during current   limit
10.00
Hz/s
P11.08
Overload pre-alarm of motor/VFD
The output current   of the VFD or the motor is above P11.09 and the lasting time is beyond   P11.10, overload pre-alarm will be output.
Setting range of   P11.08:
Enable and define   the overload pre-alarm of the VFD or the motor.
Setting range: 0x000–0x131
LED ones:
0: Overload   pre-alarm of the motor, corresponding to the rated current of the motor
1: Overload pre-alarm   of the VFD, corresponding to the rated current of the VFD
LED tens:
0: The VFD continues   to work after underload pre-alarm
1: The VFD continues   to work after underload pre-alarm and the VFD stops to run after overload   fault
2: The VFD continues   to work after overload pre-alarm and the VFD stops to run after underload   fault
LED hundreds :
0: Detection all the   time
1: Detection in   constant running
Setting range of   P11.09: P11.11–200%
Setting range of   P11.10: 0.1–3600.0s
0x000
P11.09
Overload pre-alarm detection
150%
P11.10
Overload pre-alarm detection time
1.0s
P11.11
Underload pre-alarm detection
If the VFD current   or the output current is lower than P11.11, and its lasting time is beyond   P11.12, the VFD will output underload pre-alarm.
Setting range of   P11.11: 0–P11.09
Setting range of   P11.12: 0.1–3600.0s
50%
P11.12
Underload pre-alarm detection time
1.0s
P11.13
Output terminal action during fault
Select the action of   fault output terminals on undervoltage and fault reset.
0x00–0x11
LED ones:
0: Action under   fault undervoltage
1: No action under   fault undervoltage
LED tens:
0: Action during the   automatic reset
1: No action during   the automatic reset
0x00
P11.14
Speed deviation detection
0.0–50.0%
Set the speed   deviation detection time.
10.0%
P11.15
Speed deviation detection time
This parameter is   used to see the speed deviation detection time.
Setting   range of P11.15: 0.0–10.0s
0.5s
P11.16
Automatic   frequency-decreasing at voltage drop
0: Invalid
1: Valid; ensure rated output torque when voltge   drop
