You can perform various operations on the VFD by using the keypad, including entering/exiting menus, parameter selection, list modification and parameter addition.
5.4.1 Enter/exit menu
Regarding the monitoring menu, the operation relation between enter and exit is shown below.
Regarding the system menu, the operation relation between enter and exit is shown below.
The keypad menu setup is shown in the following.
Level 1
Level 2
Level 3
Level 4
Common parameter setup
P00.10: Set   frequency via keypad
P00.00: Speed   control mode
Pxx.xx : Common   parameter setup xx
Quick setup for function code
Pxx.xx
Parameter setup
Basic parameter group setup
P00: Basic function group
P00.xx
P07: HMI group
P07.xx
P08: Enhance function group
P08.xx
P11: Protection parameter group
P11.xx
P14: Serial communication function group
P14.xx
P99: Factory function group
P99.xx
Motor parameter group setup
P02: Motor 1 parameter group
P02.xx
P12: Motor 2 parameter group
P12.xx
P20: Motor 1 encoder group
P20.xx
P24: Motor 2 encoder group
P24.xx
Control parameter group setup
P01: Start/stop control group
P01.xx
P03: Motor 1 vector control group
P03.xx
P04: V/F control group
P04.xx
P09: PID control group
P09.xx
P10: Simple PLC and multi-step speed control group
P10.xx
P13: Synchronous motor control parameter group
P13.xx
P21: Position control group
P21.xx
P22: Spindle positioning group
P22.xx
P23: Motor 2 vector control group
P23.xx
Terminal function group setup
P05: Input   terminal group
P05.xx
P06: Output   terminal group
P06.xx
P98: AIAO calibration function group
P98.xx
Optional card function group setup
P15: Communication expansion card 1 function group
P15.xx
P16: Communication expansion card 2 function group
P16.xx
P25: Expansion   I/O card input function group
P25.xx
P26: Expansion I/O card output function group
P26.xx
P27: PLC function group
P27.xx
P28: Master/slave function group
P28.xx
Default function group setup
P90: Customized function group 1
P90.xx
P91: Customized function group 2
P91.xx
P92: Customized function group 3
P92.xx
P93: Customized function group 4
P93.xx
State monitoring/fault record
State monitoring
P07: HMI group
P07.xx
P17: State-check function group
P17.xx
P18: Closed-loop   vector state check function group
P18.xx
P19: Expansion card state check function group
P19.xx
Fault record
P07.27: Type of   present fault
P07.28: Type of   the last fault
P07.29: Type of   the last but one fault
P07.30: Type of   the last but two fault
P07.31: Type of   the last but three fault
P07.32: Type of   the last but four fault
Fault state
P07.33: Running frequency of present fault
P07.34: Ramps   frequency of present fault
P07.xx: xx state   of the last but xx fault
Clear fault history
Sure to clear   fault history?
Modified parameter
Pxx.xx has   modified parameter 1
Pxx.xx has   modified parameter 2
Pxx.xx has   modified parameter xx
Motor parameter autotuning
Complete parameter   rotary autotuning
Complete   parameter static autotuning
Partial parameter   static autotuning
Parameter backup/restore default value
Operate the storage area 1: BACKUP01
Upload local   function parameter to keypad
Download complete   keypad function parameter
Download key   function parameters which are not in motor group
Download keypad   function parameters which are in motor group
Operate the storage area 2: BACKUP012
Operate the storage area 3: BACKUP03
Restore function parameter to default value
Ensure to restore   function parameters to default value?
System setup
Language   selection
Time/date
Backlight   brightness regulation
Backlight time   adjustment
Power-on guiding   enable
Power-on guiding   settings
Keyboard burning   selection
Fault time enable
Control board   burning selection
5.4.2 List edit
The monitoring items displayed in the parameter list of stop state can be added by users as needed (through the menu of the function code in state check group), and the list can also be edited by users e.g. "shift up", "shift down" and "delete from the list". The edit function is shown in the interface below.
Press image.png key to enter edit interface, select the operation needed, and press image.png key,  image.png key or image.png key to confirm the edit operation and return to the previous menu (parameter list), the returned list is the list edited. If image.png key or image.png key is pressed in edit interface wihouth selecting
edit operation, it will return to the previous menu (parameter list remain unchanged).
Note: For the parameter objects in the list header, shift-up operation will be invalid, and the same principle can be applied to the parameter objects in the list footer; after deleting a certain parameter, the parameter objects under it will be shifted up automatically.
The monitoring items displayed in the parameter list of running state can be added by users as needed (through the menu of the function code in state check group), and the list can also be edited by users e.g. "shift up", "shift down" and "delete from the list". The edit function is shown in the interface below.
The parameter list of common parameter setup can be added, deleted or adjusted by users as needed, including delete, shift-up and shift-down; the addition function can be set in a certain function code of a function group. The edit function is shown in the figure below.
5.4.3 Add parameters to the parameter list displayed in stop/running state
In the fourth-level menu of "State monitoring", the parameters in the list can be added to the "parameter displayed in stop state" list or "parameter displayed in running state" list as shown below.
Press image.png key to enter parameter addition interface, select the operation needed, and press image.png key,  image.pngkey or image.png key to confirm the addition operation. If this parameter is not included in
the "parameter displayed in stop state" list or "parameter displayed in running state" list, the parameter added will be at the end of the list; if the parameter is already in the "parameter displayed in stop state" list or "parameter displayed in running state" list, the addition operation will be invalid. If
 image.png key or image.png key is pressed without selecting addition peration in "Addition" interface, it will
return to monitoring parameter list menu.
Part of the monitoring parameters in P07 HMI group can be added to the "parameter displayed in stop state" list or "parameter displayed in running state" list; All the parameters in P17, P18 and P19 group can be added to the "parameter displayed in stop state" list or "parameter displayed in running state" list.
Up to 16 monitoring parameters can be added to the "parameter displayed in stop state" list; and up to 32 monitoring parameters can be added to the "parameter displayed in running state" list.
5.4.4 Add parameter to common parameter setup list
In fourth-level menu of "parameter setup" menu, the parameter in the list can be added to the "common parameter setup" list as shown below.
Add image.png key to enter addition interface, and press image.png key, image.png key or image.png key to confirm the addition operation. If this parameter is not included in the original "common parameter setup" list, the newly-added parameter will be at the end of the list; if this parameter is already in the "common parameter setup" list, the addition operation will be invalid. If image.png key or image.png key is pressed without selecting addition operation, it will return to parameter setup list menu.
All the function code groups under parameter setup sub-menu can be added to "common parameter setup" list. Up to 64 function codes can be added to the "common parameter setup" list.
5.4.5 Parameter selection edit interface
In parameter selection edit interface, the "authority" on the top right indicates whether this parameter is editable or not.
"" indicates the set value of this parameter can be modified under current state.
"×" indicates the set value of this parameter cannot be modified under current state.
"Current value" indicates the value of current option.
"Default value" indicates the default value of this parameter.
5.4.6 Parameter setup edit interface
In parameter selection edit interface, the "authority" on the top right indicates whether this parameter can be modified or not.
"Current value" indicates the value saved last time.
5.4.7 State monitoring interface
5.4.8 Motor parameter autotuning
After selecting motor autotuning type, enter motor parameter autotuning interface, and press RUN key to start motor parameter autotuning. After autotuning is done, a prompt will pop out indicating autotuning is succeeded, and then it will return to the main interface of stop. During autotuning, users can press STOP/RST key to terminate autotuning; if any fault occur during autotuning, the keypad will pop out a fault interface.
Figure 5.19 Parameter autotuning finished
5.4.9 Parameter backup
5.4.10 System setup
5.4.11 Power-on guiding settings
The keyboard supports the power-on guiding function, mainly for the first power-on situation, guiding the user to enter the setting menu, and gradually implementing basic functions such as basic parameter setting, direction judgment, mode setting and autotuning. The power-on guiding enable menu guides the user to enable power-on to boot each time. Power-on guiding setup menu guides the user to set step by step according to the functions.
The power-on guide is shown as below.
Level    1
Level    2
Level    3
Level    4
Language
0: Simplified Chinese
0: Power-on each time
Whether to enter the power-on guiding settings?
0:Yes
Whether to test the motor rotation   direction?
Yes
1:English
1: Only once
1:No
No
P00.06
Setting   channel of A frequency command
0:   Keypad
Press the JOG button first. It is   currently forward, Is it consistent with the expectations?
Yes
1: AI1
No
2: AI2
P02.00 Type of motor   1
0: AM
3: AI3
1: SM
4:   High-speed pulse HDIA
P02.01 Rated power of   AM 1
5:   Simple PLC program
P02.02 Rated frequency   of AM 1
6: Multi-step   speed running
P02.03 Rated speed of   AM 1
7: PID   control
P02.04 Rated voltage   of AM 1
8:   Modbus/
  Modbus TCP communication
P02.05 Rated current of AM 1
9:   Profibus/CANopen/DeviceNet communication
P02.15 Rated power of SM 1
10:   Ethernet communication
P02.16 Rated frequency of SM 1
11:   High-speed pulse HDIB
P02.17 Number of pole pairs of SM 1
12:   Pulse train AB
P02.18 Rated voltage of SM 1
13:   EtherCat/Profinet/EtherNetIP communication
P02.19 Rated current of SM 1
14: PLC card
Whether to conduct autotuning?
Yes
15: Reserved
No
P00.01
Running command   channel
0: Keypad
Motor   parameter autotuning interface
1: Terminal
2:   Communication command
P00.02
Communication running command channel
0: Modbus/
1:   PROFIBUS / CANopen /Devicenet communication
2: Ethernet Communication
3: EtherCat   /Profinet/EtherNetIP communication
4: PLC programmable card
5: Wireless communication card
P08.37
Enable energy-
  consumption brake
0: Disable
1: Enable
P00.00
Speed   control mode
0:   Sensorless vector control (SVC) mode 0
1:   Sensorless vector control (SVC) mode 1
2: VF control
3:   Closed-loop vector control mode
P01.08
Stop mode
0: Decelerate   to stop
1: Coast to stop
P00.11
ACC time 1
P00.12
DEC time 1