5.5.1 What this section contains
This section introduces the function modules inside the VFD.
² Ensure all the terminals are fixed and   tightened firmly.
² Ensure the motor   matches with the VFD power.
5.5.2 Common commissioning procedure
The common operation procedure is shown in the following (taking motor 1 as an example).
Note: If fault occurred, rule out the fault cause according to "fault tracking".
The running command channel can be set by terminal commands besides P00.01 and P00.02.
Current running   command channel
P00.01
Multi-function   terminal function (36)
Command switches   to keypad
Multi-function   terminal function (37)
Command switches   to terminal
Multi-function   terminal function (38)
Command switches   to communication
Keypad
Terminal
Communication
Terminal
Keypad
Communication
Communication
Keypad
Terminal
Note: "/" means this multi-function terminal is invalid under current reference channel.
Related parameter list:
Function code
Description
Default
P00.00
Speed control mode
0: Sensorless vector control (SVC) mode 0
1: Sensorless vector control (SVC) mode 1
2: Space voltage vector control mode
3: Closed-loop vector control mode
Note: To select 0, 1, or 3 as the control mode, enable the VFD to   perform motor parameter autotuning first.
P00.01
Channel of running commands
0: Keypad
1: Terminal
2: Communication
P00.02
Communication mode of running commands
0: Modbus/Modbus TCP
1: Profibus/CANopen/DeviceNet
2: Ethernet
3: EtherCAT/Profinet/EtherNetIP
4: Programmable expansion card
5: Wireless communication card
P00.15
Motor parameter autotuning
0: No operation
1: Rotary autotuning.
  Comprehensive motor parameter autotuning. It is recommended to use rotating   autotuning when high control accuracy is needed.
2: Static autotuning 1 (comprehensive   autotuning); static autotuning 1 is used in cases where the motor cannot be   disconnected from load.
3: Static autotuning 2 (partial autotuning); when the present   motor is motor 1, only P02.06, P02.07   and P02.08 are autotuned; when the present motor is   motor 2, only P12.06, P12.07 and P12.08 are autotuned.
4: Rotary   autotuning 2,   similar to rotary autotuning 1, but valid only to AMs
5: Static autotuning 3 (partial autotuning), valid only to AMs
P00.18
Function parameter restore
0: No operation
1: Restore default values
2: Clear fault records
Note:   After the selected operation is performed, the   function code is automatically restored to 0. Restoring the default values   may delete the user password. Exercise caution when using this function.
P02.00
Type of motor 1
0: Asynchronous motor (AM)
1: Synchronous motor (SM)
P02.01
Rated power of AM 1
0.1–3000.0kW
Model depended
P02.02
Rated frequency of AM 1
0.01Hz–P00.03 (Max. output frequency)
50.00Hz
P02.03
Rated speed of AM 1
1–60000rpm
Model depended
P02.04
Rated voltage of AM 1
0–1200V
Model depended
P02.05
Rated current of AM 1
0.8–6000.0A
Model depended
P02.15
Rated power of SM 1
0.1–3000.0kW
Model depended
P02.16
Rated frequency of SM 1
50.00Hz
P02.17
Number of pole pairs of SM 1
1–50
P02.18
Rated voltage of SM 1
0–1200V
Model depended
P02.19
Rated current of SM 1
0.8–6000.0A
Model depended
P05.01P05.06
Function selection of multifunction   digital input terminals (S1–S4, HDIA, HDIB)
36: Switch the running command channel to   keypad
37: Switch the running command channel to   terminal
38: Switch the running command channel to   communication
P07.01
Reserved
P07.02
QUICK/JOG   key
function selection
Range: 0x00–0x27
Ones place: Function of QUICK/JOG
0: No function
1: Jog
2: Reserved
3: Switch between forward and reverse   rotating
4: Clear the UP/DOWN setting
5: Coast to stop
6: Switch command channels in sequence
7: Reserved
Tens place: Reserved
0x01
5.5.3 Vector control
AMs feature high order, nonlinearity, strong coupling and multi-variables, which increase difficulty to control AMs during actual application. The vector control technology solves this situation as follows: measures and controls the stator current vector of the AM, and then decomposes the stator current vector into exciting current (current component that generates internal magnet field) and torque current (current component that generates torque) based on field orientation principle, and therefore controls the amplitude values and phase positions of the two components (namely, controls the stator current vector of the AM) to realize decoupled control on exciting current and torque current, thus achieving high-performance speed regulation of the AM.
The VFD uses the sensor-less vector control algorithm, which can be used to drive AMs and permanent-magnet SMs simultaneously. As the core algorithm of vector control is based on accurate motor parameter models, the accuracy of motor parameters affects vector control performance. It is recommended to enter accurate motor parameters and autotune motor parameters before executing vector control.
As the vector control algorithm is complicated, exercise caution before modifying vector control function parameters.
Function code
Description
Default
P00.00
Speed control mode
P00.15
0: No operation
1:   Rotary autotuning 1.
4: Rotary autotuning 2. Similar to rotary autotuning 1, but it is   valid only for AMs.
5: Static autotuning 3 (partial autotuning), valid only for AMs.
P02.00
Type of motor 1
P03.00
Speed-loop proportional gain 1
0–200.0
20.0
P03.01
Speed-loop integral time 1
0.000–10.000s
0.200s
P03.02
Low-point frequency for switching
0.00Hz–P03.05
5.00Hz
P03.03
Speed-loop proportional gain 2
0–200.0
20.0
P03.04
Speed-loop integral time 2
0.000–10.000s
0.200s
P03.05
High-point frequency for switching
P03.02P00.03 (Max.   output frequency)
10.00Hz
P03.06
Speed-loop output filter
0–8 (0–28/10ms)
P03.07
Electromotive slip compensation   coefficient of vector control
50%–200%
100%
P03.08
Braking slip compensation coefficient of   vector control
50%–200%
100%
P03.09
Current-loop proportional coefficient P
0–65535
1000
P03.10
Current-loop integral coefficient I
0–65535
1000
P03.11
Torque setting method
11: Keypad (P03.12)
2: AI1   (100% corresponding to three times the motor rated current)
3: AI2   (same as the above)
4: AI3   (same as the above)
5:   Pulse frequency HDIA (same as the above)
6:   Multi-step torque (same as the above)
7: Modbus/Modbus   TCP communication (same as the above)
8:   Profibus/CANopen/DeviceNet communication (same as the above)
9:   Ethernet communication (same as the above)
10: Pulse frequency HDIB (same as the above)
11: EtherCat/Profinet/EtherNetIP communication
12: Programmable expansion card
Note: For setting methods 2–12, 100% corresponds to three times   the motor rated current.
P03.12
Torque   set through keypad
-300.0%–300.0% (of the motor rated current)
50.0%
P03.13
Torque reference filter time
0.000–10.000s
0.010s
P03.14
Setting   source of forward rotation upper-limit frequency in torque control
0: Keypad (P03.16)
1: AI1 (100% corresponding to the max. frequency)
2: AI2 (same as the above)
3: AI3 (same as the above)
4: Pulse frequency HDIA (same as the above)
5: Multi-step setting (same as the above)
6: Modbus/Modbus   TCP communication (same as the above)
7: Profibus/CANopen/DeviceNet communication (same as the above)
8: Ethernet communication (same as the above)
9: Pulse frequency HDIB (same as the above)
10: EtherCat/Profinet/EtherNetIP communication
11: Programmable expansion card
12: Reserved
Note: For setting methods 1–11, 100% corresponds to the maximum   frequency.
P03.15
Setting   source of reverse rotation upper-limit frequency in torque control
0: Keypad   (set by P03.17)
1–11:   Same as those of P03.14
P03.16
Forward rotation upper-limit frequency set   through keypad in torque control
Setting range: 0.00 Hz–P00.03 (Max. output   frequency)
50.00Hz
P03.17
Reverse   rotation upper-limit frequency set through keypad in torque control
50.00Hz
P03.18
Setting   source of electromotive torque upper limit
0:   Keypad (P03.20)
1: AI1   (100% corresponding to three times the motor rated current)
5: Modbus/Modbus   TCP communication (same as the above)
6:   Profibus/CANopen/DeviceNet    communication (same as the above)
7:   Ethernet communication (same as the above)
8:   Pulse frequency HDIB (same as the above)
9:   EtherCAT/Profinet communication
10:   Programmable expansion card
11:   Reserved
Note: For setting methods 1–10, 100%   corresponds to three times the motor rated current.
P03.19
Setting   source of braking torque upper limit
0: Keypad   (set by P03.21)
1–10:   Same as those for P03.18
P03.20
Electromotive   torque upper limit
set   through keypad
0.0–300.0% (of the motor rated current)
180.0%
P03.21
Braking   torque upper limit set through keypad
180.0%
P03.22
Weakening   coefficient in constant power zone
0.1–2.0
0.3
P03.23
Lowest   weakening point in constant power zone
10%–100%
20%
P03.24
Max.   voltage limit
0.0–120.0%
100.0%
P03.25
Pre-exciting   time
0.000–10.000s
0.300s
P03.32
Enabling   torque control
0: Disable
1: Enable
P03.33
Flux weakening integral gain
0–8000
1200
P03.35
Control   optimization setting
0–0x1111
Ones   place: Torque command selection
0:   Torque reference
1:   Torque current reference
0:   Reserved
1:   Reserved
Hundreds   place: indicates whether to enable speed-loop integral separation
0:   Disable
1:   Enable
Thousands   place: Reserved
0:   Reserved
1:   Reserved
Range:   0x0000–0x1111
0x0000
P03.36
Speed-loop   differential gain
0.00–10.00s
0.00s
P03.37
High-frequency   current-loop
In the   closed-loop vector control mode (P00.00=3), when the frequency is   lower than the current-loop high-frequency switching threshold (P03.39), the current-loop PI parameters are P03.09   and P03.10; and when the frequency is higher than the   current-loop high-frequency switching threshold (P03.39),   the current-loop PI parameters are P03.37 and P03.38.
Setting   range of P03.37: 0–20000
Setting   range of P03.38: 0–20000
Setting range of P03.39: 0.0–100.0% (of the   maximum frequency)
1000
P03.38
1000
P03.39
Current-loop   high-frequency switching threshold
100.0%
P17.32
Flux   linkage
0.0–200.0%
0.0%
5.5.4 Space voltage vector control mode
The VFD also provides the space voltage control function. The space voltage control mode can be used in cases where mediocre control precision is enough and in cases where the VFD needs to drive multiple motors.
The VFD provides multiple V/F curve modes to meet different requirements. You can select V/F curves or set V/F curves as required.
Suggestions:
l For the load featuring constant moment, such as conveyor belt which runs in straight line, as the whole running process requires constant moment, it is recommended to adopt the straight line V/F curve.
l For the load featuring decreasing moment, such as fan and water pumps, as there is a power (square or cube) relation between its actual torque and speed, it is recommended to adopt the V/F curve corresponding to the power of 1.3, 1.7 or 2.0.
The VFD also provides multi-point V/F curves. You can change the V/F curves output by the VFD by setting the voltage and frequency of the three points in the middle. A whole curve consists of five points starting from (0Hz, 0V) and ending at (motor fundamental frequency, motor rated voltage). During setting, follow the rule: 0 ≤ f1 ≤ f2 ≤ f3 ≤ Motor fundamental frequency, and, 0 ≤ V1 ≤ V2 ≤ V3 ≤ Motor rated voltage
The VFD provides dedicated function codes for the space voltage control mode. You can improve the space voltage control performance by means of setting.
      (1)     Torque boost
The torque boost function can effectively compensate for the low-speed torque performance in space voltage control. Automatic torque boost has been set by default, which enables the VFD to adjust the torque boost value based on actual load conditions.
l Torque boost takes effect only at the torque boost cut-off frequency.
l If torque boost is too large, the motor may encounter low-frequency vibration or overcurrent. If such a situation occurs, reduce the torque boost value.
      (2)     Energy-saving run
During actual running, the VFD can search for the max. efficiency point to keep running in the most efficient state to save energy.
l This function is generally used in light load or no-load cases.
l This function is no applicable to the cases where sudden load changes often occur.
(3)     V/F slip compensation gain
Space voltage vector control belongs to an open-loop mode. Sudden motor load changes cause motor speed fluctuation. In cases where strict speed requirements must be met, you can set the slip compensation gain to compensate for the speed change caused by load fluctuation through VFD internal output adjustment.
The setting range of slip compensation gain is 0–200%, in which 100% corresponds to the rated slip frequency.
Note: Rated slip frequency = (Rated synchronous rotation speed of motor – Rated rotation speed of motor) x (Number of motor pole pairs)/60
(4)     Oscillation control
Motor oscillation often occurs in space voltage vector control in large-power driving applications. To solve this problem, the VFD provides two oscillation factor function codes. You can set the function codes based on the oscillation occurrence frequency.
Note: A greater value indicates better control effect. However, if the value is too large, the VFD output current may be too large.
(5)     AM IF control
Generally, the IF control mode is valid for AMs. It can be used for SMs only when the frequency is extremely low. Therefore, the IF control mode described in this manual is only involved with AMs. IF control is implemented by performing closed-loop control on the total output current of the VFD. The output voltage adapts to the current reference, and open-loop control is separately performed over the frequency of the voltage and current.
Customized V/F curve (V/F separation) function:
When selecting the customized V/F curve function, you can specify the setting channels and acceleration/deceleration time of voltage and frequency respectively, which form a real-time V/F curve in combination manner.
Note: This type of V/F curve separation can be applied in various variable-frequency power sources. However, exercise caution when setting parameters as improper settings may cause equipment damage.
Function code
Description
Default
P00.00
Speed control mode
P00.03
P00.04–400.00Hz
50.00Hz
P00.04
Upper limit of running frequency
P00.05P00.03
50.00Hz
P00.05
Lower limit of running frequency
0.00Hz–P00.04
0.00Hz
P00.11
ACC time 1
0.0–3600.0s
Model depended
P00.12
DEC time 1
0.0–3600.0s
Model depended
P02.00
Type of motor 1
P02.02
50.00Hz
P02.04
0–1200V
Model depended
P04.00
V/F curve setting of motor 1
0: Straight-line V/F curve
1: Multi-point V/F curve
2: Torque-down V/F curve (power of 1.3)
3: Torque-down V/F curve (power of 1.7)
4: Torque-down V/F curve (power of 2.0)
5: Customized V/F curve (V/F separation)
P04.01
Torque boost of motor 1
0.0%: (automatic); 0.1%–10.0%
0.0%
P04.02
Torque boost cut-off of motor 1
0.0%–50.0% (of the rated frequency of motor 1)
20.0%
P04.03
V/F frequency point 1 of motor 1
0.00Hz–P04.05
0.00Hz
P04.04
V/F voltage point 1 of motor 1
0.0%–110.0%
0.0%
P04.05
V/F frequency point 2 of motor 1
P04.03P04.07
0.00Hz
P04.06
V/F voltage point 2 of motor 1
0.0%–110.0%
0.0%
P04.07
V/F frequency point 3 of motor 1
P04.05P02.02 or P04.05P02.16
0.00Hz
P04.08
V/F voltage point 3 of motor 1
0.0%–110.0%
0.0%
P04.09
V/F slip compensation gain of motor 1
0.0–200.0%
100.0%
P04.10
Low-frequency oscillation control factor   of motor 1
0–100
10
P04.11
High-frequency oscillation control factor   of motor 1
0–100
10
P04.12
Oscillation control threshold of motor 1
0.00Hz–P00.03 (Max. output frequency)
30.00Hz
P04.13
V/F curve setting of motor 2
P04.14
Torque boost of motor 2
0.0%
P04.15
Torque boost cut-off of motor 2
0.0%–50.0%(of the rated frequency of motor 1)
20.0%
P04.16
V/F frequency point 1 of motor 2
0.00Hz–P04.18
0.00Hz
P04.17
V/F voltage point 1 of motor 2
0.0%–110.0%
0.0%
P04.18
V/F frequency point 2 of motor 2
P04.16P04.20
0.00Hz
P04.19
V/F voltage point 2 of motor 2
0.0%–110.0%
0.0%
P04.20
V/F frequency point 3 of motor 2
P04.18P02.02 or P04.18P02.16
0.00Hz
P04.21
V/F voltage point 3 of motor 2
0.0%–110.0%
0.0%
P04.22
V/F slip compensation gain of motor 2
0.0–200.0%
100.0%
P04.23
Low-frequency oscillation control factor   of motor 2
0–100
10
P04.24
High-frequency oscillation control factor   of motor 2
0–100
10
P04.25
Oscillation control threshold of motor 2
30.00Hz
P04.26
Energy-saving run
0: Disable
1: Automatic energy-saving run
P04.27
Voltage setting channel
0: Keypad; Output voltage is determined by P04.28
1: AI1
2: AI2
3: AI3
4: HDIA
5: Multi-step running
6: PID
10: HDIB
13: Reserved
P04.28
Voltage set through keypad
0.0%–100.0%(of the motor rated voltage)
100.0%
P04.29
Voltage increase time
0.0–3600.0s
5.0s
P04.30
Voltage decrease time
0.0–3600.0s
5.0s
P04.31
Max. output voltage
P04.32–100.0% (of the motor rated voltage)
100.0%
P04.32
Min. output voltage
0.0%–P04.31 (the motor rated voltage)
0.0%
P04.33
1.00–1.30
1.00
P04.34
Pull-in current 1 in SM V/F control
When the SM V/F   control mode is enabled, the function code is used to set the reactive   current of the motor when the output frequency is lower than the frequency   specified by P04.36.
Setting range:-100.0%–100.0% (of the motor rated current)
20.0%
P04.35
Pull-in current 2 in SM V/F control
When the SM V/F   control mode is enabled, the function code is used to set the reactive   current of the motor when the output frequency is higher than the frequency   specified by P04.36.
10.0%
P04.36
Frequency threshold for pull-in current   switching in SM V/F control
When the SM V/F   control mode is enabled, the function code is used to set the frequency   threshold for the switching between pull-in current 1 and pull-in current 2.
Setting range: 0.00Hz–P00.03 (Max. output frequency)
50.00Hz
P04.37
Reactive current closed-loop proportional   coefficient in SM V/F control
When the SM V/F control mode is enabled,   the function code is used to set the proportional coefficient of reactive   current closed-loop control.
Setting range: 0–3000
50
P04.38
Reactive current closed-loop integral   time in SM V/F control
When the SM V/F control mode is enabled,   the function code is used to set the integral coefficient of reactive current   closed-loop control.
30
P04.39
Reactive current closed-loop output limit   in SM V/F control
When the SM V/F control mode is enabled,   the function code is used to set the output limit of the reactive current   closed-loop control. A greater value indicates a higher reactive closed-loop   compensation voltage and higher output power of the motor. In general, you do   not need to modify the function code.
Setting range: 0–16000
8000
P04.40
Enabling IF mode of AM 1
0: Disable
1: Enable
P04.41
Current setting in IF mode for AM 1
When IF control is adopted for AM 1, the   function code is used to set the output current. The value is a percentage in   relative to the rated current of the motor.
Setting range: 0.0–200.0%
120.0%
P04.42
Proportional coefficient in IF mode for   AM 1
When IF control is adopted for AM 1, the   function code is used to set the proportional coefficient of the output   current closed-loop control.
Setting range: 0–5000
650
P04.43
Integral coefficient in IF mode for AM 1
When IF control is adopted for AM 1, the   function code is used to set the integral coefficient of the output current   closed-loop control.
350
P04.44
Frequency threshold for switching off IF   mode for AM 1
0.00–P04.50
10.00Hz
P04.45
Enabling IF mode for AM 2
0: Disable
1: Enable
P04.46
Current setting in IF mode for AM 2
When IF control is adopted for AM 2, the   function code is used to set the output current. The value is a percentage in   relative to the rated current of the motor.
120.0%
P04.47
Proportional coefficient in IF mode for   AM 2
When IF control is adopted for AM 2, the   function code is used to set the proportional coefficient of output current   closed-loop control. Setting range: 0–5000
650
P04.48
Integral coefficient in IF mode for AM 2
When IF control is adopted for AM 2, the   function code is used to set the integral coefficient of output current   closed-loop control. Setting range: 0–5000
350
P04.49
Frequency threshold for switching off IF   mode for AM 2
0.00–P04.51
10.00Hz
P04.50
End frequency point for switching off IF   mode for AM 1
P04.44–P00.03
25.00Hz
P04.51
End frequency point for switching off IF   mode for AM 2
P04.49 – P00.03
25.00Hz