image.png

The terminals are arranged as follows:

SW1 is the start/stop switch of the programmable expansion card. CN1 contains terminals PE, 485-, 485+, GND, AI1, and AO1, and a selection jumper resides on the next. "AI" and "AV" are the current type input selection and voltage type input selection of AI1, and they can be selected through J2. "AIO" and "AVO" are the current type output selection and voltage type output selection of AO1, and they can be selected through J5. "120" indicates 120Ω terminal resistor, and it can connect to J1. By default, J1 connects to NC, J2 to AV, and J5 to AVO.

image.png

Indicator definition:

Indicator

Name

Function

LED1

Power indicator (Green)

This indicator is   on when the expansion card is powered on.

LED3

Communication   indicator (Green)

This indicator is   on when the expansion card is establishing a connection with the control   board; it blinks periodically after the expansion card is properly connected   to the control board (the period is 1s, on for 0.5s, and off for the other   0.5s); and it is off when the expansion card is disconnected from the control   board.

LED4

Error indicator   (Red)

This indicator blinks   when an error occurs (the blinking period is 1s, on for 0.5s, and off for the   other 0.5s). You can query the error types on the upper computer Auto   Station.

This indicator is   off when there is no error.

LED5

Power indicator

This indicator is   on when the expansion card is powered on.

LED6

RUN indicator (Green)

This indicator is on when the PLC program is running; it is off when   the PLC program stops.

The EC-PC502-00 programmable expansion card can replace some micro PLC applications. It adopts the global mainstream development environment PLC, supporting the instruction language (IL), ladder diagram (LD), and sequential function chart (SFC). It provides a user program storage space of 16K steps and data storage space of 8K words, and supports saving data of 1K words at power failure, which facilitate customers' secondary development and meets the customization requirements.

The EC-PC502-00 programmable expansion card provides 6 digital inputs, 2 relay outputs, 1 analog input, 1 analog output, and 1 RS485 communication channel (for master/slave switchover). It is user-friendly, providing relay outputs through European-type screw terminals and other inputs and outputs through spring terminals.

EC-PC502-00 terminal function description:

Category

Sign

Name

Function

Power

PW

External power

The working power of digital input is provided by   an external power supply.

Voltage range: 12–24 V

The terminals PW and +24V are shorted before   delivery.

24V

Internal power

Internal output power: 100mA

Digital   input/output

PS1—COM

Digital input 1

1. Internal impedance: 4 kΩ

2. Allowable voltage input: 12–30 V

3. Bidirectional terminal

4. Max. input frequency: 1 kHz

5. Supporting both source type input and sink   type input, but the input type must be the same

PS2—COM

Digital input 2

PS3—COM

Digital input 3

PS4—COM

Digital input 4

PS5—COM

Digital input 5

PS6—COM

Digital input 6

PY1—CME

Digital output 1

1. Switch capacity: 200 mA/30 V

2. Output frequency range: 0–1 kHz

3. The terminals CME and COM are shorted through   J1 before delivery.

PY2—CME

Digital output 2

Analog   input/output

AI1

Analog input 1

1. Input range: 0~10V   or 0~20mA

2. Input   resistance: 20kΩ for voltage input, and 250kΩ for current input

3. Whether the   input is the voltage or current type is set through the jumper.

4. Resolution:   When 10V corresponds to 50Hz, the min. resolution is 5mV.

5. Deviation ±1%,   25°C, full measuring range

AO1

Analog output 1

1. Output range:   0~10V voltage or 0~20mA current

2. Whether the   output is the voltage or current type is set through the jumper.

3. Deviation ±1%,   25°C, full measuring range

Relay output

PRO1A

NO contact of   relay 1

1. Contact capacity: 3A/AC 250 V, 1 A/DC 30 V

2. Do not use them as high-frequency digital   outputs.

PRO1B

NC contact of   relay 1

PRO1C

Common contact of   relay 1

PRO2A

NO contact of   relay 2

PRO2C

Common contact of   relay 2

For details about the operation of programmable expansion cards, see the Goodrive350 Series VFD Auto Station Programmable Expansion Card Operation Manual.